Asked on: Thursday, October 2, 2025 at 11:31 pm EDT
Answered on: Thursday, October 2, 2025 at 11:35 pm EDT
Question: vd = 2 x `12.9 x 11.5 x 580 = 172086 = 6.5 voltscmil 26240I need to run the circuit for a 1.5hp water well. The control box says that the pump will use 11.5 amps @ 240 volts. The total length is 580ft. The well company ran #10 wire down the well to the pump. I show that #6 should be used for the well due to voltage drop. Would it be code compliant to run #6 up to the well head, then use their #10 that runs from the well head to the well pump?
Okay, let's break down this situation, considering code compliance and safety.
Understanding the Problem
You've identified a significant voltage drop issue with the existing wiring for your well pump. You correctly calculated (or found) that #10 wire over 580ft at 11.5 amps will result in a voltage drop exceeding what's generally acceptable (your 6.5V drop on a 6.5V target is on the right track, but we'll calculate precisely). Your calculation confirms that using #6 wire for the entire run would be more appropriate to minimize voltage drop.
Key Considerations1. Voltage Drop Calculation
The calculation you've started is good. Let's refine it a bit for 240V systems and more clarity:
Acceptable Voltage Drop
A common rule of thumb is to keep voltage drop under 3% for branch circuits and 5% for feeders. On a 240V system, that's a maximum of: 3%: 240V 0.03 = 7.2V 5%: 240V 0.05 = 12V
Formula
There are various formulas, but a common one for voltage drop in a single-phase circuit is:
Where: VD = Voltage Drop (in volts) K = Material constant (12.9 for copper) I = Current (in amps) = 11.5A D = One-way Distance (in feet) = 580ft CM = Circular Mils of the wire VD = (2 K I D) / CM
#10 Wire Calculation
CM of #10 AWG copper wire = 10380 VD = (2 12.9 11.5 580) / 10380 = 16.07V (approximately)This is a significant voltage drop! You're losing 16.07 volts over the run, which is 6.69% voltage drop. This exceeds both the 3% and 5% thresholds.
#6 Wire Calculation
CM of #6 AWG copper wire = 26240 VD = (2 12.9 11.5 580) / 26240 = 6.35V (approximately) This is about 2.65% voltage drop. Acceptable.
2.
Code Compliance (NEC - National Electrical Code)
NEC 310.16
This section, and its accompanying tables, dictate the ampacity (current carrying capacity) of conductors. You MUST ensure the wire size is adequate for the load. For #10 copper conductors with THHN insulation in conduit, the typical ampacity is 30 amps. Therefore, #10 is good for the 11.5 amp current the pump is drawing. The voltage drop is the issue.
NEC 300.3(B)
Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, cable, or cord, unless otherwise permitted in 300.3(B)(1) through (B)(4).
NEC 250
Grounding is critical. Verify your grounding system is adequate and properly connected.
Local Codes
Always check with your local electrical inspector for any local amendments or requirements that might supersede the NEC.3.
Safety
Undersized wiring can overheat, causing insulation damage, fires, and premature equipment failure. Voltage drop reduces the motor's efficiency and lifespan.
Answer to Your QuestionNo, it is not generally code compliant to run #6 wire up to the wellhead and then splice it to the existing #10 wire for the final run to the pump. Here's why: Weakest Link
The #10 wire becomes the "weakest link" in the circuit. While the #6 can handle the current and minimize voltage drop up to the splice, the #10 will still be subject to the excessive voltage drop, and could overheat if a fault occurs. It doesn't solve the fundamental problem.
NEC 110.3(B)
Equipment must be installed per its listing and labeling. The pump manufacturer likely specifies wiring requirements.
Series Circuit Issue
Effectively, you'd be creating a series circuit where a large portion of the voltage drop still occurs on the undersized #10 wire.
Recommended Solution
The correct and safest solution is to replace the entire run of wire from the control box to the pump with #6 wire. This ensures: Adequate ampacity for the load. Acceptable voltage drop over the entire distance. Code compliance. Proper operation and longevity of your well pump.
Additional Recommendations Consult a Qualified Electrician
Well pump wiring can be tricky, and it's best to have a licensed electrician do the work. They can properly size the wire, ensure code compliance, and make safe connections.
Consider Submersible Splices
If you absolutely must make a splice inside the well casing (which is generally discouraged), use only submersible splices specifically designed for that purpose. These are watertight and designed to withstand the harsh environment.
Inspect the Existing Wiring
Have the electrician inspect the existing #10 wire for any signs of damage or degradation. If it's old or damaged, it should be replaced regardless.
Use the Correct Wire Type
Use the appropriate type of wire for the application (e.g., THWN or UF for wet locations).
In summary: While your initial idea might seem like a shortcut, it's not a safe or code-compliant solution. Running #6 wire for the entire distance is the best way to ensure proper operation and safety. Flag for review