Question: I have a furniture feed requiring four phases and two neutralsI have four existing 12/2 at a central location that I was hoping to box and reuse use for the furniture feeds.Because the branch circuit will be MC cable....is there an issue using two 12/2 feeding the two circuits that would be sharing a neutral...the shared neutral would be in two different cables. If I was using Romex and a plastic box I wouldn't worry but because I'm using MC cable I'm wondering if that is code compliant
Okay, let's break down the situation and address the code compliance concerns when using MC cable with shared neutrals (multi-wire branch circuits).
Understanding the Issue: Shared Neutrals and MC Cable
The core issue is inductance in the steel or aluminum sheath of the MC cable. When you have unbalanced current flowing in the phase conductors and a shared neutral, that current imbalance can induce a voltage in the metal sheath of the MC cable. This isn't a problem with non-metallic sheathed cable (Romex) because it's... well, non-metallic.
Code Compliance: NEC Requirements
The relevant section of the National Electrical Code (NEC) that applies here is 300.3(B) Conductors of the Same Circuit. It states:>(B) Conductors of the Same Circuit. All conductors of the same circuit and, where used, the grounded conductor and all equipment grounding conductors and bonding conductors shall be contained within the same raceway, auxiliary gutter, cable tray, cablebus assembly, cable armor, or cable sheath.Why This Matters to You Impedance and Induced Voltages
If you run the phase conductors of two different circuits in separate MC cables, even if they share a neutral in a box, the current in each MC cable won't be perfectly balanced. This unbalanced current creates an electromagnetic field around each cable. The steel or aluminum sheath of the MC cable acts as a single-turn transformer winding, and the unbalanced current induces a voltage in the sheath. While it's usually small, it can create circulating currents, heat, and, in extreme cases, potentially nuisance tripping.
Harmonics
Non-linear loads (common in electronics) produce harmonic currents. The neutral current in a multi-wire branch circuit can exceed the current in the individual phase conductors if those harmonics are present. This exacerbates the problems with inductance and induced voltages.
The Problem with Your Proposed Setup
Using two 12/2 MC cables, one for each phase conductor and separately carrying the shared neutral, technically violates 300.3(B) because all conductors of the same circuit are not contained within the same cable sheath.
Acceptable Solutions (Assuming You Need MC Cable)
Here's how you can make this code-compliant and safe:1. MC Cable with Shared Neutral
The correct way to do this is with a single
4-conductor MC cable (12/4). The 12/4 cable provides two hots, a neutral, and a ground wire all within the same sheath. The hot and neutral conductors for each circuit are bundled together, which minimizes inductance and voltage drop in the sheathing. You would connect the red and black to the hots, the white to the neutral, and the bare to ground.2. Conduit with THHN/THWN Conductors
If you're open to using conduit instead of MC cable, you could run conduit and pull individual THHN/THWN wires. Run all the conductors (two hots, one neutral, and one ground) for both circuits within the same conduit.
Why This Is Important
While the induced voltages and circulating currents might be small, over time they can cause: Increased Energy Consumption
Circulating currents generate heat, wasting energy.
Nuisance Tripping
The increased heat can trigger the breaker.
Overheating of Cable Sheath
Potentially leading to damage to the cable.
Electromagnetic Interference (EMI)
The electromagnetic fields can interfere with nearby electronic equipment.
In Summary
Don't use two separate 12/2 MC cables to create a shared-neutral circuit. It violates NEC 300.3(B) and can lead to various problems. Use a single multi-conductor (4-conductor) MC cable, or run conduit with individual wires. If you choose to run conduit and pull individual wires, make sure the conduit is appropriately sized for the number and gauge of conductors you're using. Flag for review