Topic: MC Cable Support

User: Alwayslearningelec, Location: NJ

Asked on: Friday, October 3, 2025 at 7:59 am EDT
Answered on: Friday, October 3, 2025 at 7:59 am EDT

Question: I thought MC cable did not need to be supported every 6' within stud.

You are correct. MC cable, according to the NEC, does not necessarily need to be supported every 6 feet within a stud bay.Here's the breakdown of the support requirements for MC cable, based on the National Electrical Code (NEC): General Rule (NEC 330.30(A))

MC cable must be supported and secured at intervals not exceeding 6 feet.


Exception 1 (NEC 330.30(A))

Where the cable is fished between access points, support is not required. (Think existing walls where you can't easily nail or screw supports).

Exception 2 (NEC 330.30(A))

Where the cable is not subject to physical damage and is 8 feet or less from the last point of support to a luminaire or other electrical equipment.


Exception 3 (NEC 330.30(D))

MC cable is permitted to be unsupported where the cable complies with Article 300.11(C)(1).

Therefore, MC cable can be run through stud cavities (stud bays) without needing to be supported every 6 feet within each stud cavity IF you meet the general rule and exceptions.
Key Considerations



Physical Damage

The NEC always emphasizes protecting wiring from physical damage. If the MC cable is in a location where it's likely to be damaged (e.g., rubbing against sharp edges, subject to impact), you'll want to provide more support than the minimum requirement.


300.11(C)(1) Dedicated Support

MC cable can be used as a means of support for Class 2 Circuit cables, communication cables, etc., if it is identified for this use.

In summary, you're right to question the idea that MC cable always needs support every 6 feet within stud bays. The NEC allows for some flexibility, especially when fishing the cable or when it's not subject to physical damage.
Disclaimer: This information is for general guidance only. Always consult the current edition of the NEC and local electrical codes for specific requirements in your area. When in doubt, err on the side of providing more support and securement. Flag for review