User: Pinnie, Location: Ohio
Asked on: Friday, October 3, 2025 at 9:00 am EDT
Answered on: Friday, October 3, 2025 at 9:01 am EDT
Question: Struggling with this code rule. You have to use the greater of either the (100% non-continuous+ 125% continuous load) or (the ampacity after applying 310.15).(1) is the load ampacity being raised due to conditions(2) is wire ampacity being raised or lowered due to conditionsSay you have a 27 amp continuous load(1) = 34ampsGot it(2) 10awg is 35 at 75C but then you run into 240.4(d). So go up to 8awg.It seems (2) is determined based on (1), which is what I always thought anyway. Where does the “greater of the two” come in?
You're right to be questioning this and clarifying the application of these rules! It's a common point of confusion. Let's break it down
The Rule: "Greater Of" - What It Actually Means
The rule you're referring to is about determining the minimum required ampacity of the conductors. It's not necessarily about raising or lowering the load ampacity in itself. The "greater of" applies when comparing two different methods for calculating that minimum conductor ampacity. It's about which method dictates a larger minimum ampacity, thus determining the wire size you need.
Two Methods Compared Method 1: 100% Non-Continuous Load + 125% Continuous Load This is your first calculation and establishes the minimum required ampacity based on the nature of the loads. In your example, this has already resulted in a minimum of 34 Amps. Method 2: Ampacity after applying 310.15 (Temperature Correction and Adjustment Factors) This method starts with the conductor ampacity rating in the ampacity tables (like Table 310.16) but then adjusts that ampacity based on conditions like ambient temperature and the number of current-carrying conductors in a raceway or cable. This is where you could potentially derate (reduce) the conductor's ampacity.
Your Example – And Where the Confusion Arises
You've correctly calculated the following: Continuous Load = 27 Amps 125% of Continuous Load = 27 1.25 = 33.75 Amps (rounded up to 34 Amps)Now let's look at the conductor sizing and the "greater of" rule1. Apply Method 1
The 125% continuous load rule dictates that the conductors must have a minimum ampacity of 34 amps.2.
Potential Conductor Sizes
#10 AWG
You correctly identify that #10 AWG has a 30A ampacity (at 60C) according to 240.4(D) and 35 amps (at 75C). However, using 240.4(D) the ampacity would have to be less than 30. This means, even under ideal conditions, a #10 AWG conductor cannot be used.
#8 AWG
#8 AWG has a 40A ampacity. However, if it is in a high-temperature environment or bundled with many other current-carrying conductors, its ampacity could be derated BELOW 34 amps.3.
Apply Method 2
This is where you consider temperature correction and conductor bundling. If the #8 AWG is exposed to high temperatures, the table 310.15(b) says the rating will need to be reduced.For example, If the temperature is a constant 100F then you'll be at 82% (40amps .82 = 32.8Amps). In this instance, you'd want to go to the next size up to a #6awg.
4.
The "Greater Of" Comparison
Method 1 (125% Continuous Load)
Requires a minimum ampacity of 34 Amps.
Method 2 (310.15 Adjusted Ampacity)
In this example, requires a minimum ampacity of 33 Amps. (40amps .82 = 32.8Amps). Since this is lower, then Method 1 takes precedence.
Conclusion
Because 34 amps is greater than 32.8amps, the NEC requires that you continue to move to the next available wire size. In this case, it will be a #6 AWG.
Key Takeaways and Clarifications Order of Operations
Don't confuse applying the 125% continuous load rule with already having "raised" the load. The 125% rule is part of determining the minimum required conductor ampacity.
Derating Affects Conductor Ampacity
Temperature correction and adjustment factors (310.15) lower the conductor's allowable ampacity from its table value.
240.4(d)
This is a key rule for smaller conductor sizes. It limits the overcurrent protection device to a lower value than the conductor's theoretical ampacity in Table 310.16 unless you meet specific exceptions.
Focus on Conductor Ampacity
The comparison is about the minimum ampacity required for the conductor, not about directly modifying the load itself.
In Summary: You calculate the required ampacity based on the 125% continuous load rule. Then, you choose a conductor size that, even after derating for temperature and conductor bundling, has an ampacity at least as high as the value you calculated using the 125% rule. If derating brings the initial conductor choice's ampacity below the required minimum (from the 125% rule), you have to go up to the next larger conductor size.Hopefully, this clarifies the process! Flag for review