Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC 430.24 or NEC 215.2(A)(1)

User: johnharkin97, Location: Bristol

Asked on: Friday, October 3, 2025 at 9:43 am EDT
Answered on: Friday, October 3, 2025 at 9:44 am EDT

Question: Hello all,I am designing a piece of equipment with multiple motors and other loads. How do I know whether to follow NEC 430.24 or NEC 215.2(A)(1) when it comes to sizing my feeders?

You're asking a very common and important question in electrical design. Here's a breakdown to help you choose between NEC 430.24 and NEC 215.2(A)(1) for feeder sizing, focusing on the key differences and how to apply them

Understanding the Sections
NEC 430.24: Several Motors or a Motor(s) and Other Loads This section is specifically for sizing feeders (and branch circuits, but we're focused on feeders here) that supply multiple motors or a motor(s) combined with other types of loads. The "other loads" are things like lighting, receptacles, heating elements, etc. Important

430.24
must be applied to any feeder supplying more than one motor.

NEC 215.2(A)(1): Minimum Size Feeder Conductor
This section covers the general requirements for sizing feeder conductors. It focuses on calculating the continuous and non-continuous loads and ensuring the feeder is adequately sized to handle them. It is more generic.

The Decision: When to Use Which

The primary key is to determine if you are supplying multiple motors.

If you have a feeder supplying more than one motor then NEC 430.24 must be used. If there is only a single motor on a given feeder than it falls outside the scope of 430.24. NEC 430.24 takes precedence when you have multiple motors connected to the feeder. It is a more detailed and specific calculation tailored to motor loads. You need to follow the steps outlined in 430.24, considering the largest motor, other motors, and any additional non-motor loads. NEC 215.2(A)(1) is used in these situations



Single motor only

If the feeder supplies only a single motor.


Only non-motor loads

If the feeder supplies only non-motor loads.

As a cross-check or
in addition to 430.24

You
might use 215.2(A)(1) after you've done the calculations under 430.24 to verify that your feeder size is still adequate based on the total calculated load, especially when the non-motor loads are a significant portion of the total load.

Steps to Follow


Here's a structured approach:1. Identify the Loads

List all the loads connected to the feeder. Categorize them as:
Motors (list the nameplate FLA - Full Load Amps - of each motor) Continuous Non-Motor Loads (loads expected to operate for 3 hours or more at a time) Non-Continuous Non-Motor Loads2.

Is there more than one motor?
Yes

NEC 430.24 is your primary guide. Proceed to step 3.

No

NEC 215.2(A)(1) should be used. Size the feeder per that section considering the single motor and/or non-motor loads.3.

Apply NEC 430.24



Determine the largest motor

Identify the motor with the highest Full Load Amps (FLA) from its nameplate.


Calculate motor load

Multiply the largest motor's FLA by 125% (NEC 430.24 states this is how to treat the largest motor's load)

Add the FLA of all
other motors

Include 100% of the FLA of all other motors connected to the feeder.


Calculate Continuous Non-Motor Loads

Multiply the sum of the continuous non-motor loads by 125% per NEC 215.2(A)(1).

Add all non-continuous non-motor loads

No multiplier here.


Total calculated load (using 430.24)

Sum the results from the above steps. This is your initial feeder ampacity requirement.4.

Voltage Drop

Always consider voltage drop. NEC informational note No. 4 in 215.2(A)(1) points this out. Longer feeder runs, especially with motors starting and stopping, can cause significant voltage drop, which negatively impacts motor performance. Calculate voltage drop based on your initial feeder size and adjust the feeder size upward if necessary to keep voltage drop within acceptable limits (typically 3% for the feeder and 5% total to the farthest motor).
5.


Conductor Ampacity

Select a conductor with an ampacity at least equal to the calculated load from step 3, and adjusted for voltage drop.6.

Overcurrent Protection

Size the feeder overcurrent protection (circuit breaker or fuses) according to the ampacity of the conductor you selected. Also, double-check motor branch circuit protection requirements as they are separate and have their own rules (NEC Article 430 Part III).7.

Verify if needed

As a prudent step, you can also calculate the total load using NEC 215.2(A)(1) as a check, to ensure the feeder size selected using 430.24 is still adequate when considering the continuous and non-continuous loads from all sources. This is especially useful when the non-motor loads are a significant portion of the total load.

Example

Let's say you have a feeder supplying: Motor 1: 20 FLA Motor 2: 10 FLA Motor 3: 5 FLA Continuous Lighting Load: 10 Amps Non-Continuous Receptacle Load: 5 Amps1.

Largest Motor

Motor 1 (20 FLA)2.

Motor 1 Load

20 FLA
1.25 = 25 Amps3.

Other Motors Load

10 FLA + 5 FLA = 15 Amps4.

Continuous Lighting Load

10 amps 1.25 = 12.5 amps5.

Receptacle Load

5 Amps6.

Total Load (430.24)

25 + 15 + 12.5 + 5 = 57.5 AmpsNow you would select a conductor with an ampacity of at least 57.5 Amps, consider voltage drop, and then choose an appropriate overcurrent protective device.

Key Considerations & Cautions



Nameplate Data

Always use the motor's nameplate FLA for calculations, not horsepower conversions. FLA is the actual current the motor is designed to draw at its rated load.

Service Factor

If a motor has a service factor greater than 1.15, or a temperature rise greater than specified in NEC 430.32(A)(1), a different percentage may be used when calculating the motor's overload protection (but not for the feeder calculation itself).


Continuous vs. Non-Continuous

Accurately determining which loads are continuous is critical. If in doubt, treat a load as continuous.

Spare Capacity

It's good practice to add some spare capacity to your feeder. Equipment may be added in the future, or the actual loads may be higher than initially estimated. Adding 10-20% additional capacity is a common practice.


Coordination

Ensure proper coordination between the feeder overcurrent protective device and the motor branch circuit protective devices to prevent nuisance tripping.

Local Codes

Always check with your local authority having jurisdiction (AHJ) for any specific local code requirements that may affect feeder sizing.


Professional Assistance:
If you're not comfortable with these calculations, or if you have a complex system, consult with a qualified electrical engineer.By following these steps and carefully considering the specific requirements of NEC 430.24 and NEC 215.2(A)(1), you can correctly size your feeders for motor loads and other loads, ensuring safety and reliable operation of your equipment. Remember, accuracy and attention to detail are paramount when working with electrical systems. Flag for review

Previous Question Next Question