Question: If a panelboard is existing to remain but all the branch circuits are to be demo'ed and you are to safe off and disconnect with removals by others you would still remove conduit/wire out of the panel obviously, correct? To what point?

Yes, you are correct. Even though the panelboard is remaining, if all the branch circuits are being demolished and removed by others, you would still need to disconnect and remove the wiring and conduit associated with those circuits from the panelboard. Here's the breakdown to what point you'd remove everything

Your Scope (Safe Off, Disconnect, and Removals by Others):
De-energize and Lockout/Tagout (LOTO)

The VERY FIRST and MOST IMPORTANT step. Verify the circuits are de-energized
at the source and properly LOTO the breakers/fuses feeding those circuits. This is critical for safety.

Double check with a meter!
Disconnect Wiring at the Panelboard

Disconnect all circuit conductors (hot, neutral, ground) from the panelboard's terminals (breakers, neutral bus, ground bus). Be methodical and label each wire as you disconnect it. Documenting this with photos is also a good practice.

Remove Wiring from the Panelboard

Remove the disconnected conductors from the panelboard enclosure. The goal is to leave the panelboard empty of all branch circuit wiring.


Remove Conduit Back to a Manageable Point

This is where the "to what point?" question comes in. You need to remove the conduit back to a point where it's safe and doesn't pose a hazard. Here are some options, listed in order of preference:

Ideal

Remove the conduit back to its point of origin, if feasible. This might be another panel, a junction box, or the source of the wiring. This leaves the demolition crew with nothing to deal with.


Practical, but still very good

Remove the conduit back to the point where it exits the room, or the building. This will still allow the demolition crew to safely remove the rest of the conduit without worrying about encountering live wires.

Acceptable (But less ideal)

Remove the conduit back to a point
immediately outside the panelboard enclosure. This should be the absolute minimum. Carefully cut the conduit (using a proper conduit cutter, not a sawzall or grinder that could create sparks and damage the panel) close to the enclosure, leaving a stub protruding out.

Cap or tape off the conduit end securely
with electrical tape to prevent debris or foreign objects from entering the conduit and potentially affecting the remaining wiring in the panelboard. Bonding

Ensure the remaining panelboard enclosure is still properly bonded to ground according to code. If you've disturbed any bonding conductors during the process, re-establish them.

Labeling

Clearly label the panelboard to indicate that the branch circuits have been removed and that
only the panelboard remains. Also, label any stubs of conduit with a warning: "Conduit Stub - No Wiring Inside. Demolition Required."

Coordinate with Demolition Crew

Communicate clearly with the demolition crew. Explain what you've done, show them the capped conduit stubs, and confirm that they understand their responsibility for removing the rest of the conduit.

Why all the detail?
Safety

This is paramount. You need to ensure that the circuits are completely de-energized and cannot be accidentally re-energized.


Clarity of Scope

It's essential to clearly define the scope of work and avoid any ambiguity.

Avoidance of Future Problems

Leaving dangling wires or improperly capped conduits can create hazards for other trades working on the site.


Compliance with Codes

All work must be done in accordance with the National Electrical Code (NEC) and any local codes.

Important Considerations



Asbestos

If the building is older, be aware of the potential for asbestos in conduit or wire insulation. If asbestos is suspected, have it tested and abated by qualified professionals before any work is done.


Permits

Check with the local authorities to determine if any permits are required for this work.*

Qualified Electrician:
This work should only be performed by a qualified and licensed electrician.By following these steps, you can safely and effectively disconnect and remove the branch circuits from the panelboard, leaving it ready for the demolition crew to complete the removal of the conduit. Remember to prioritize safety and communication throughout the process. Flag for review