Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 600 amp service install

User: Therealcrt, Location: Kansas City

Asked on: Friday, October 3, 2025 at 11:22 am EDT
Answered on: Friday, October 3, 2025 at 11:22 am EDT

Question: Gonna be doing a new 600 amp service install at a warehouse,service feeders from transformer to A CT cabinet from my CT cabinet to the tenants. Space. I’m gonna be pulling aluminum so I figured 500 is good for 310 at 75°C so I’ll be running parallel 500 each set in a 3 inch conduit three phase 480 VI just have a few questions. When are the use of bonding bushings required do I need to use them in my CT cabinet if the voltage is 277 or greater to ground whether or not I use a whole punch or a concentric/eccentric knockout since it’s at the service.Also, I believe I’m gonna be using window current transformers I’ve done them before and I always remember that the white dot that’s painted on there faces the primary side, but I’ve seen various rules as far as I have to remove the mounting bracket on the back is that specific to the AHJ or is that common and also is there a manual that comes with those CT’s that state that I must do that?

Okay, let's break down your 600A service installation and address your questions about bonding bushings and current transformers (CTs).

General Considerations Good Choice on Aluminum

Using aluminum conductors for services of this size is common and cost-effective. 500 kcmil aluminum conductors are generally adequate for 310A at 75°C ampacity, and paralleling them is the standard approach.


3" Conduit

Verify that the conduit fill with (6) 500 kcmil aluminum conductors (two sets of three-phase conductors) is within the NEC limits. I think it will be, but double-check with Chapter 9, Table 1 of the NEC, or a conduit fill calculator.

Bonding Bushings


This is a critical safety issue, so let's be precise: The Rule

NEC 250.92(B)(2), outlines when bonding bushings (or other methods) are required on service raceways. Here's the breakdown as it likely applies to your situation:


Metal Raceways

Any metal raceway (including your conduit and CT cabinet) containing service conductors must be bonded to the service grounding electrode system (service neutral) where the raceway enters the enclosure.

Knockouts

The type of knockout
does matter. If you're using concentric or eccentric knockouts that are not "listed for grounding" OR you punch a hole significantly larger than the fitting/connector, you must use a bonding jumper to connect the raceway/conduit to the CT cabinet's grounding bus. Bonding bushings are one common way to achieve this. If you use properly sized, clean, and tight locknuts to land on properly sized knockouts, and the enclosure is listed, then a bonding bushing might not be needed, BUT I WOULD JUST USE THE BONDING BUSHING ANYWAY!

Voltage 277 to Ground

The 277V-to-ground aspect of your 480V system does trigger additional bonding requirements. Since your service is fed from the transformer, the NEC 250.92(B)(2) is in place.

Essentially

Since you are running service conductors in a metallic raceway into a metallic enclosure, and your voltage is 277 to ground or greater, you need to verify that the raceway is bonded back to the service neutral conductor in a way that will comply with 250.92(B)(2).


Why Bonding Bushings?
They provide a low-impedance path for fault current back to the source (transformer) so that overcurrent protective devices (fuses or breakers) will quickly trip in the event of a ground fault. This is critical for safety. Bottom Line

Err on the side of caution. Installing bonding bushings or appropriately sized ground bushings and bonding jumpers on all metallic raceway entries into your CT cabinet is a best practice, even if the code seems ambiguous in a specific instance. The cost is minimal compared to the safety benefits.

Current Transformers (CTs)
Polarity Dot

You are correct. The white polarity dot (or sometimes a raised mark) on the CT always faces the source (primary side). This ensures proper current and phase relationship for metering and protective relaying.

Mounting Bracket Removal



Common Practice, but Verify

Removing the mounting bracket on the back of the CT is often required or recommended by the manufacturer. The reason is to ensure proper insulation and to prevent a potential path for circulating currents (especially in high-voltage applications) that could affect CT accuracy.

Manufacturer's Instructions are KEY

Always read the installation manual that comes with your specific CTs. That manual will clearly state whether bracket removal is required. This is where the definitive answer lies.

AHJ Influence

Some local jurisdictions (AHJs) may have specific interpretations or rules about CT installation. It's always prudent to check with your local electrical inspector to confirm their requirements.

General Recommendation

If the CT manual
recommends removing the bracket (even if it doesn't explicitly say "must"), I would remove it. It's a simple step that reduces the chance of problems.

Action Items


Double-Check Conduit Fill

Ensure your 3" conduit is adequately sized for your conductors.2.

Bonding

Plan for bonding bushings (or properly sized ground bushings and grounding jumpers) on all metallic raceway entries into your CT cabinet.3.

CT Manual

Find the installation manual for your
specific current transformers before* you start the physical installation. Follow the manufacturer's instructions regarding bracket removal.4.

Consult AHJ

When in doubt, talk to your local electrical inspector. A quick conversation can save you time and money in the long run.

Disclaimer:
I am an AI chatbot and cannot provide definitive electrical code interpretations. Always consult the latest edition of the National Electrical Code (NEC) and local amendments, and consult with a qualified electrical engineer or licensed electrician for project-specific advice. This information is for educational purposes only. Flag for review

Previous Question Next Question