Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Disconnect In Sight

User: Alwayslearningelec, Location: NJ

Asked on: Friday, October 3, 2025 at 2:12 pm EDT
Answered on: Friday, October 3, 2025 at 2:12 pm EDT

Question: The panels in the pic are feeding equipment in pic. If the panel(breaker feeding equip) is within sight of the equipment it's feeding is a disconnect required?What code section is this? Thanks.

Okay, let's break down the disconnect requirements when the panel is within sight of the equipment it feeds.

General Rule: A Disconnect is Typically Required

Even if the panel (breaker) is within sight of the equipment it feeds, a separate disconnect switch (or breaker) is generally required at or near the equipment. The primary reason is for safety during maintenance and repair. It allows the person working on the equipment to positively verify that the power is off and locked out/tagged out right at the equipment location.

NEC 430.102 Location(A) Controller. An individual disconnecting means shall be provided for a controller and shall disconnect the controller. The disconnecting means shall be located within sight from the controller location and conform to 430.102(B) or (C), as applicable.(B) Motor. An individual disconnecting means shall be provided for each motor. The disconnecting means shall be located within sight from the motor location and the driven machinery location.

Exception No. 1

The disconnecting means for a motor shall not be required under either condition (1) or condition (2), provided the controller disconnecting means required in 430.102(A) is capable of being locked in the open position.

(1)
Where such a motor is vital to operation of the facility and therefore is required to operate continuously(2) Where such a motor is under the exclusive control of a qualified personKey Considerations and Exceptions



Lockout/Tagout

The main reason for a local disconnect is to allow for safe lockout/tagout procedures. If the panel breaker can be locked out in the
open (off) position, and this meets all safety requirements, some exceptions may apply. However, this is rarely the case, especially for equipment that requires frequent maintenance.

Line of Sight Requirement

The "within sight" rule (generally interpreted as being visible and no more than 50 feet away) exists to ensure that the person operating the disconnect can see the equipment being de-energized.

Summary


While "within sight" of the panel is a factor, it does not automatically eliminate the need for a local disconnect.

Disclaimer: I am an AI chatbot and cannot provide electrical code interpretations that should be used in place of a licensed electrician. It is critical that you consult with a qualified electrician to ensure your installation meets all applicable codes and safety standards. Flag for review

Previous Question Next Question