Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Residential

User: hhsting, Location: Glen bunie, md, us

Asked on: Friday, October 3, 2025 at 3:12 pm EDT
Answered on: Friday, October 3, 2025 at 3:12 pm EDT

Question: If I have feeder feeding single family dwelling feeding 200A panel and the feeder is sized #2/0 awg then can I have 200A breaker feeding that feeder or I would need 175A breaker feeding that feeder?

You can use a 200A breaker to protect a #2/0 AWG copper feeder to a dwelling unit's 200A panel, assuming the conditions outlined below are met.Here's why and what you need to consider: Ampacity of #2/0 Copper

According to NEC Table 310.16 (for conductors rated 60°C, 75°C, or 90°C and not more than three current-carrying conductors in a raceway, cable, or directly buried), the ampacity of #2/0 AWG copper is as follows:
75°C rated conductor: 175 Amps 90°C rated conductor: 195 Amps

Dwelling Unit Feeder Calculation & 310.15(B)(7)

For dwelling unit feeders, the NEC permits using specific reduced ampacity rules as defined in 310.15(B)(7). This section allows for a reduction in the required ampacity of the feeder conductors to the dwelling unit's service or feeder.Here's what 310.15(B)(7) basically allows (summarized): For a 100A through 400A service or feeder to a dwelling unit, the feeder conductors can be sized based on a percentage of the service or feeder rating. For a 200A service/feeder, the minimum calculated feeder conductor size is permitted to be based on 83% of the service or feeder rating. 200 0.83 = 166 AIf 2/0 AWG conductors are rated for 175A at 75°C, then this size is sufficient for your 200A load. The breaker can be rated to 200A in this case.

Important Considerations



Conductor Termination Temperature Rating

Pay close attention to the termination temperature ratings of the circuit breakers and the panelboard to which the #2/0 AWG conductors are connected. These devices are often rated for 75°C. Even if the conductor itself is rated for 90°C, you may be limited by the termination temperature rating. This will determine the applicable ampacity you can use from NEC Table 310.16.


Other Loads

This calculation assumes it's only for the main dwelling unit feeder. If there are other significant loads (e.g., electric vehicle chargers, large workshops) connected to this same feeder, they must be factored into the total load calculation.

Local Amendments

Always check with your local electrical inspector. Some jurisdictions have amendments to the NEC that might affect how dwelling unit feeders are sized.

In summary

You can likely use a 200A breaker with #2/0 AWG copper for a dwelling unit feeder due to the allowances in NEC 310.15(B)(7).*

HOWEVER

You

must
perform a full load calculation for the dwelling unit to ensure that the #2/0 AWG conductors, using the ampacity based on the termination temperature ratings, are sufficient to carry the calculated load. You should also confirm there are no specific local amendments or requirements that might supersede the NEC. When in doubt, consult with a qualified electrician or your local electrical inspector. Flag for review

Previous Question Next Question