User: Therealcrt, Location: Kansas City
Asked on: Friday, October 3, 2025 at 6:16 pm EDT
Answered on: Friday, October 3, 2025 at 6:17 pm EDT
Question: I’ve helped install CT cabinets before but always just landed the primary side and the secondary side under all the lugs, then mounted the window CT around the buss’s but that was it. I didn’t do anything with the meter enclosure so what else is there after that? Do I have to run wires from those CT’s to the meter enclosure it’s a 3 phase 480v 600amp. There are usually little screws or terminals on the CT’s if I remember but after looking at finish installs on some online I see wires coming off those.
You're right, you're missing the crucial step of connecting the CT secondaries to the meter enclosure! Here's a breakdown of what needs to happen after you've landed the primary and secondary side of the CT cabinet, and what to do with those wires you saw coming off the CTs
The Purpose of CTs and Metering
CTs (Current Transformers)
CTs step down the high current of your 600A service to a much lower, manageable current (typically 0-5 amps). This is essential because meters can't directly handle such high current.
Meters
Meters measure this reduced current and convert it into a reading of power (kW) and energy consumption (kWh).
Wiring from CTs to the Meter Enclosure1. CT Secondary Wiring
This is the key. You must run wires from the secondary terminals of each CT (those little screws or terminals you mentioned) to the corresponding input terminals in the meter enclosure.
Polarity Matters
CTs have polarity markings (usually labeled "S1" and "S2" or with polarity dots). The wires must be connected with the correct polarity to the meter for accurate readings. Pay close attention to the meter's wiring diagram. Typically, S1 goes to the positive or "source" terminal on the meter, and S2 goes to the negative or "load" terminal.
Dedicated Wiring
Use dedicated, twisted-pair wiring for each CT secondary circuit. This helps minimize noise and interference. Shielded cable is often recommended.
Wire Gauge
The wire gauge depends on the distance between the CTs and the meter enclosure and the CT burden. Consult the meter and CT specifications. Often, 16 AWG to 12 AWG is sufficient.
Conduit
Run the CT secondary wiring in a separate, grounded metal conduit from the CT cabinet to the meter enclosure. This provides physical protection and reduces electrical noise. Do not run these wires with high voltage or control wiring.
Shorting Blocks (Important Safety)
Before disconnecting any CT wiring (even for testing), you MUST install shorting blocks on the CT secondary terminals.
NEVER leave a CT secondary open-circuited while the primary conductor is energized. This can generate extremely high voltage and can damage the CT and pose a severe shock hazard. Install these shorting blocks in the CT cabinet, and short all phases if possible.2. Voltage Inputs (Potential Transformers or Direct Connection)
Potential Transformers (PTs or VTs)
In some installations, especially at higher voltages, you'll also use Potential Transformers (PTs) or Voltage Transformers (VTs) to step down the 480V line voltage to a level the meter can handle (usually 120V). If PTs are used, you will run wires from the PT secondaries to the meter's voltage input terminals.
Direct Voltage Connection
In other cases, especially for smaller services, the meter may be rated to directly accept the 480V input. In this case, you will run wires from the service entrance (fused) to the meter's voltage input terminals.
Fusing
Ensure appropriate fusing is in place for the voltage inputs to the meter, whether using PTs or direct connection.3.
Neutral Connection
The meter will also require a neutral connection. Connect the neutral from the service entrance to the meter's neutral terminal.4.
Grounding
The meter enclosure must be properly grounded to the building's grounding system.
Wiring Diagram and Documentation Crucial Step
Always refer to the meter's wiring diagram. This diagram is essential for understanding the correct connections for both the CT secondaries and the voltage inputs. Different meters have different terminal designations and wiring configurations.
As-Built Drawings
Create or update as-built drawings that clearly show the CT and meter wiring. This is vital for future maintenance and troubleshooting.
Commissioning and Testing1. Verify Wiring
Double-check all wiring connections to ensure they are correct and secure.2.
CT Polarity Verification
Before energizing the system, verify the CT polarity using a CT polarity tester. This ensures the meter will read correctly.3.
Meter Configuration
Configure the meter with the correct CT ratio (e.g., 600:5 for a CT that reduces 600 amps to 5 amps) and any other necessary settings.4.
Testing and Calibration
After energizing the system, test the meter's accuracy against a known load. Calibrate the meter if necessary.
Safety Considerations De-energize
Whenever possible, de-energize the service before working on any wiring.
Lockout/Tagout
Follow proper lockout/tagout procedures to ensure the service cannot be accidentally energized while you are working on it.
Qualified Personnel
Only qualified electricians with experience in CT and metering installations should perform this work.
Shorting Blocks
As mentioned above, shorting blocks are critical for CT safety.
Never disconnect a CT secondary while the primary conductor is energized without using shorting blocks.
In Summary
After installing the CTs around the bus bars and landing the connections to the CT cabinet, you must:1. Run dedicated, twisted-pair wiring from the CT secondary terminals to the corresponding terminals in the meter enclosure, observing proper polarity.
2. Connect the voltage inputs to the meter, either from PT secondaries or directly from the service entrance (with appropriate fusing).3. Connect the neutral to the meter.
4. Ground the meter enclosure.5. Follow the meter's wiring diagram meticulously.
6. Thoroughly test and calibrate the system.This is a complex process, and proper training and understanding are essential for safety and accurate metering. If you are unsure about any step, consult with a qualified electrician or metering specialist. Good luck! Flag for review