Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Bonding Bushing Required?

User: hellofl, Location: FL

Asked on: Saturday, October 4, 2025 at 11:23 am EDT
Answered on: Saturday, October 4, 2025 at 11:24 am EDT

Question: I have metal conduit which is for the feeder from a fused disconnect enclosure (less than 250V). The service wire comes in through non-metal.I have seen different interpretations if locknuts would be sufficient for the feeder side. Which is the correct interpretation?

Okay, let's break down the requirements for grounding metal conduit used as a feeder from a fused disconnect enclosure, especially when the service entrance is non-metallic. This is a common scenario, and understanding the nuances is crucial for safety and code compliance.

The Core Issue: Grounding and Bonding

The critical question is how the metal conduit is used for grounding. Specifically, is it being used as the Equipment Grounding Conductor (EGC)? If it is, the connections need to be very robust and designed for grounding.

Understanding the NEC (National Electrical Code)

The NEC is the prevailing code in the US (check your local jurisdiction for any amendments). Here's a breakdown of relevant sections: NEC 250.4(A)(3) Grounding of Electrical Equipment. Non-current-carrying conductive materials enclosing electrical conductors or equipment, or forming part of such equipment, shall be connected together and to the electrical supply source in a manner that establishes an effective ground-fault current path. NEC 250.92(A): Services. States that if the service entrance conductors are run in a metal raceway (which yours aren't), then the metal raceway must be bonded per 250.92(B) NEC 250.92(B): Method of Bonding at the Service The gist of this is that it requires the metal raceway (conduit) be bonded using methods like bonding bushings, bonding locknuts, and grounding-type locknuts. But, if you are using non-metallic raceway, you're not directly affected. NEC 250.96: Bonding Other Enclosures. States that Metal raceways, cable trays, cable armor, cable sheaths, enclosures, frames, fittings, and other metal non-current-carrying parts that are to serve as grounding conductors, with or without the use of supplementary equipment grounding conductors, shall be effectively bonded where necessary to ensure electrical continuity and the capacity to conduct safely any fault current likely to be imposed on them. NEC 250.97: Equipment Bonding Jumpers. Internal bonding jumpers used on equipment are permitted to be installed in a raceway external to the equipment.

Applying it to Your Situation

Here's a breakdown of the common interpretations and the most likely correct approach:1. If the Metal Conduit is the Sole Equipment Grounding Conductor (EGC)

This is the most restrictive case and the one that often leads to the "locknuts are not enough" interpretation.

Locknuts alone are generally not considered sufficient for bonding the metal conduit for grounding purposes.
Locknuts can loosen over time or not provide a reliable connection. You need a method specifically designed for grounding/bonding. Acceptable methods for this scenario would typically include



Grounding Bushings

These have a setscrew that bites into the metal enclosure and a lug for connecting a grounding conductor (wire).

Grounding Locknuts

These are similar to standard locknuts, but have a tooth or teeth designed to penetrate the enclosure surface for better electrical contact, as well as a lug for connecting a grounding conductor.


Bonding Jumpers

Using a wire-type bonding jumper that is run to the grounding bar or other grounding point.

Threaded Conduit

If the conduit is threaded directly into a threaded hub on the enclosure (properly tightened), this
can be an acceptable grounding method if the enclosure is listed for that purpose.2.

If
You are Running a Separate Equipment Grounding Conductor (EGC) Inside the Conduit

This is a less restrictive but often better approach. You run a properly sized insulated grounding wire inside the conduit along with the feeder conductors.

In this case, the metal conduit is primarily for physical protection of the wires, and the
wire is the primary EGC.
Locknuts might be acceptable for mechanically securing the conduit, but it's still best practice to use grounding bushings or grounding locknuts, especially where the conduit enters the disconnect enclosure. This ensures better electrical continuity and helps prevent the conduit from becoming energized in the event of a fault. Most jurisdictions favor using grounding locknuts or grounding bushings even with a separate EGC.3. Non-Metallic Service Entrance Impact

The fact that your service entrance is non-metallic emphasizes the importance of properly grounding the feeder conduit. Because you don't have a continuous metallic path from the service entrance to the disconnect, you need to be extra diligent in establishing a reliable ground path for the feeder. This ground path ensures that a fault in the feeder circuit will trip the breaker/fuse, preventing dangerous voltage on the metal conduit.

Best Practices & Recommendations
1. Always include a properly sized Equipment Grounding Conductor (EGC) inside the conduit. This provides a dedicated, low-impedance path for fault current. Size the EGC according to NEC 250.122.
2. Use grounding bushings or grounding locknuts at both ends of the conduit run,
especially at the disconnect enclosure.3. Tighten all connections securely.4. Inspect the installation to ensure proper grounding before energizing the circuit.5. Consult your local electrical inspector. They have the final say on what's acceptable in your specific jurisdiction. They can clarify any local amendments to the NEC.

Why Grounding Matters



Safety

A properly grounded system protects people from electrical shock by providing a low-impedance path for fault current to flow, causing the overcurrent protection device (breaker or fuse) to trip quickly.

Equipment Protection

Grounding helps protect equipment from damage due to voltage surges and other electrical disturbances.


Code Compliance

Following the NEC and local codes ensures a safe and reliable electrical installation.

In Summary:


While locknuts might be technically permissible in some cases (with a separate EGC), using grounding bushings or grounding locknuts with a separate EGC is the recommended and safest practice, especially when the service entrance is non-metallic. It ensures a reliable and robust ground fault current path, protecting people and equipment. When in doubt, include the EGC, and use grounding locknuts/bushings for extra safety. Always consult your local electrical inspector for clarification and approval. Flag for review

Previous Question Next Question