Topic: Service bonding

User: pedro1200, Location: Ny

Asked on: Saturday, October 4, 2025 at 12:16 pm EDT
Answered on: Saturday, October 4, 2025 at 12:16 pm EDT

Question: In the nec 250.92b it states where theres knockouts you need to put a bonding jumper (ssbj) to clear any possible fault. If you have nonmetallic conduit the bonding jumper is not required. What if you have a metallic conduit with no eccentric knockouts is the bonding jumper required

You are correct in referencing NEC 250.92(B). Let's break down when a bonding jumper is required for service raceways (metallic conduit):NEC 250.92(B) generally requires bonding jumpers to ensure the electrical continuity of the grounding path around any flexible metal conduit, flexible metallic tubing, or other fittings if those are used as the service raceway.Here's the breakdown for your specific scenario: Metallic Conduit with NO Eccentric or Concentric Knockouts

If you have rigid metal conduit (RMC), intermediate metal conduit (IMC), or electrical metallic tubing (EMT) and it's
installed without concentric or eccentric knockouts, and you are directly connecting this raceway to enclosures listed for grounding without supplemental bonding jumpers the NEC does not require a supplemental bonding jumper around the connection. This is because the connection is already deemed electrically continuous.

Why the Concern with Knockouts?
Concentric and eccentric knockouts are designed to be broken out to accommodate different conduit sizes. The removal of these knockouts can leave gaps, paint, or other non-conductive barriers between the conduit and the enclosure. This creates a potentially unreliable ground fault path. The bonding jumper bridges this potentially unreliable connection, providing a low-impedance path for fault current. Important Considerations



Listed Fittings

The enclosure and fittings used must be listed for grounding. This means they've been tested and approved to provide a reliable ground path. This is often indicated by markings on the fitting.

Tight Connections

Ensure that all connections are made up
tightly. Loose connections increase impedance and reduce the effectiveness of the grounding path.

Service vs. Feeder/Branch Circuit

Remember this section deals specifically with service raceways. Grounding requirements for feeders and branch circuits can be different.

Local Amendments

Always check with your local authority having jurisdiction (AHJ) as they may have additional requirements or amendments to the NEC. Some jurisdictions are more strict than others.

In summary, if you have metallic conduit (RMC, IMC, or EMT) serving as the service raceway, and it's properly installed without eccentric or concentric knockouts, using listed fittings, and making tight connections, then a bonding jumper is not required around the conduit connection according to the NEC. If knockouts are involved, a bonding jumper is required
Consult a qualified electrician for any work that involves electricity.* Flag for review