Topic: Residential 400A CT service Questions

User: T. See, Location: NY

Asked on: Saturday, October 4, 2025 at 6:35 pm EDT
Answered on: Saturday, October 4, 2025 at 6:36 pm EDT

Question: I'm installing a 400 A CT service for one of my better customers this week and I've never done one before. The utility here provides the cabinet, CT's, and meter. I got them yesterday. The change over is scheduled for this Thursday and has been on the books for two plus months. This service comes to a private pole where the existing 200A meter is located. The plan is to reuse the existing feeders going to the house and we've run new 2" PVC to the detached garage and pulled 4/0, 4/0, 2/0 URD to a new 200A panel.I met with a planner from the utility (he's the one that suggested the CT service) two months ago who signed off on my plan. He's been unavailable since then.Going over the paperwork provided with the equipment, they require that the service neutral and CT cabinet be bonded to ground in the CT cabinet. Does this ground then become the GEC?My boss and I have been going back and forth on this one but, I would like to add two 200 A disconnects on the pedestal on the load side of the CT cabinet. But if I do this wouldn't I be required to pull a ground with my feeders, or is there a way around this?You're help is greatly appreciated.

Okay, you're in a common situation with a CT service for the first time, and it's good you're thinking it through carefully. Let's break down the issues and address your questions.

Understanding CT Metering and Grounding CT Cabinet as Service Equipment

The CT cabinet, where the current transformers are located, is almost always considered
service equipment. This is a critical point. It's the point where the utility's responsibility ends and your customer's begins.

Bonding and Grounding in the CT Cabinet

You're correct – the utility's documentation specifies that the service neutral and CT cabinet must be bonded to ground in the CT cabinet. This is standard practice for CT metering.

The CT Cabinet Ground IS the GEC

Yes,
the grounding electrode conductor (GEC) connects to this point of bonding in the CT cabinet. It is, for all practical purposes, the service grounding electrode connection point. You'll run your GEC from the CT cabinet to your grounding electrode (rods, water pipe, etc.) This makes sense because the neutral of the service is bonded to the earth there.

Addressing Your Specific Questions and Concerns
1. Adding 200A Disconnects on the Pedestal (Load Side of the CT Cabinet)

This is where things get a little tricky and code interpretation becomes very important. Your concern about requiring a ground with the feeders to these disconnects is valid and hinges on whether they are considered
service equipment or separately derived systems. Scenario 1: Disconnects as Service Equipment If the AHJ considers these disconnects as an extension of the service, then they are part of the service. Since the CT cabinet already has a neutral-to-case bond and GEC connection, you generally would NOT need to run a separate grounding conductor (equipment grounding conductor - EGC) with the feeders to these disconnects. In this case, the metal enclosures (disconnect enclosures and CT cabinet) would be considered effectively grounded through the grounded neutral conductor (service neutral). In this case the disconnects are part of the service so grounding would only happen in the CT cabinet. Scenario 2: Disconnects as Separately Derived Systems (SDS - unlikely, but possible) It is very unlikely that the AHJ would consider this a SDS. A separately derived system requires a step-down transformer or on-site generator.

Important Considerations and Recommendations Regarding 200A Disconnects Verify with the AHJ

Before proceeding, you MUST discuss this specific situation with your local Authority Having Jurisdiction (AHJ), which is the electrical inspector. Explain your plan to add the disconnects after the CT cabinet and ask them directly if they will consider those disconnects to be: Part of the service (covered by the CT cabinet's grounding/bonding) OR

Independently requiring equipment grounding conductors


Clear Communication with the Utility

Also, inform the utility of your plan to add the disconnects. While the CT cabinet is their domain, modifications downstream could have implications on their system monitoring or protection. Better to keep them in the loop.2.

Reusing Existing Feeders to the House

Neutral Sizing

Double-check the sizing of the existing neutral conductor to the house. The load calculations may have changed with the increased capacity.


Condition of Existing Conductors

Thoroughly inspect the existing conductors for any damage, deterioration, or overheating. Replace them if necessary.

Overcurrent Protection

Ensure that the overcurrent protection for the reused feeders (at the load side of the CT cabinet or in the new disconnects, depending on your setup) is appropriately sized for the conductors.

Additional Tips and Considerations


Documentation is Key

Take detailed photos and document everything: CT cabinet installation, grounding connections, conductor sizes, disconnect locations, etc. This will be invaluable for future reference and troubleshooting.

Torque Specifications

Follow all torque specifications for terminations in the CT cabinet, disconnects, and panels. Improper torque is a common cause of problems.


Labeling

Clearly label all panels, disconnects, and equipment with their respective functions and voltage.

Testing

After the installation is complete, perform thorough testing to verify proper operation and grounding. This should include voltage measurements, ground impedance testing, and a visual inspection of all connections.


Documentation

The utility should provide clear documentation for the CT's. If anything is unclear, ask.

In summary: Focus on getting clear direction from the AHJ regarding the disconnects before you proceed. That will dictate whether you need to run separate grounding conductors with the feeders to the disconnects or if you can rely on the service neutral as your effective ground-fault current path. And communicate clearly with the utility to ensure your plan aligns with their requirements. This is a significant upgrade, so taking the time to do it right will pay off in the long run. Flag for review