User: farmantenna, Location: mass
Asked on: Sunday, October 5, 2025 at 11:25 am EDT
Answered on: Sunday, October 5, 2025 at 11:26 am EDT
Question: I have 28 apt feeders from 3ph 120/208 service that have to get to 7 4- stacked meter modules (everything is in basement) and no wall above them so will need a wireway. It's crazy to think an inspector or anybody would allow all those conductors (84) to go in one wireway without a crippling ampacity adjustment? Art 376 no adjustment up to 30 conductors.My question is would you use just the # of conductors over 30 to determine which line in 310.15(c)(1) or once you're over 30 the ampacity reduction would start at 45%?30 conductors no adjustment34 conductors 40% or 80%?Luckily Massachusetts amends 310 table if diversity is likely.Opinions?
You're right to be concerned about conductor ampacity adjustments in this scenario. It's a significant issue, and you need to address it carefully for code compliance and safe operation.Here's a breakdown of how I understand the code applies and my thoughts on your options
Understanding 310.15(C)(1) & Wireways
Article 376 and Wireways
Yes, Article 376 (Metal Wireways) governs the installation and use of wireways. You are correct that 376.22 limits the number of current-carrying conductors in a wireway.
310.15(C)(1): Adjustment Factors
This section is crucial. It addresses the ampacity adjustment needed when multiple conductors are bundled together, as they will be in a wireway.
Your Question: Threshold for Adjustment This is the key point. The way I interpret 310.15(C)(1), and how it is generally understood, is that once you exceed 30 current-carrying conductors in a raceway or cable, the adjustment factor applies to ALL conductors. It's not an incremental thing where you only adjust for the conductors over 30. The entire group is subject to the reduction. So, with 34 conductors, you would apply the adjustment factor for 31-40 conductors. Referring to 310.15(C)(1), Table 310.15(C)(1) the adjustment factor is 80%.
Why This Matters (Heating)
The issue is heat. When you have many conductors carrying current close together, the heat they generate doesn't dissipate as effectively. This raises the conductor temperature, potentially exceeding its insulation rating and leading to failure (and fire). The ampacity adjustment factors are designed to compensate for this.
Massachusetts Amendment (Diversity)
You mention that Massachusetts has an amendment to Table 310.15(C)(1) that considers diversity. This is very important. Diversity refers to the fact that not all 28 apartment feeders will be drawing their maximum current simultaneously. Investigate the Amendment Thoroughly
Obtain the exact text of the Massachusetts amendment. Understand exactly what conditions must be met to apply the diversity factors. There will likely be requirements for load calculations, monitoring, or other means of demonstrating that the actual load is significantly less than the sum of the feeder capacities.
Documentation is Key
If you plan to use the diversity amendment, you must have thorough documentation to justify your application of the factors. This will be essential for the inspector. Load calculations and possibly a load study from similar buildings would be helpful.
Options and Recommendations
Given the situation, here's how I'd approach it:1. Consult the Massachusetts Electrical Code and your Local Inspector
The Massachusetts amendment is your best bet. Talk to the local electrical inspector before you start any work. Get their interpretation of the amendment and what documentation they will require. This is crucial.2.
Load Calculations are Essential
Perform very detailed load calculations for each apartment. Use the methodology in Article 220 of the NEC, including demand factors. Be conservative, but also realistic. The more thoroughly you can justify your load calculations, the better your chance of using the diversity amendment.3.
Consider Multiple Wireways
If you can't justify the diversity amendment, or if the inspector rejects it, the most straightforward (but possibly more expensive) solution is to use multiple wireways. Divide the conductors into smaller groups so that each wireway has 30 or fewer current-carrying conductors. You will need to maintain separation between the wireways.4.
Physical Spacing
If the inspector does not want to approve any derating less than code, and you don't want to install multiple wireways, consider physically spacing the cables out inside of the wireway and making sure there is ample ventilation to allow the heat to dissipate.5.
Larger Conductors
Another (also expensive) option is to increase the size of the conductors to compensate for the ampacity adjustment. This will be costly and may not be practical depending on the existing conduit sizes.6.
Busway
While likely overkill for just 28 apartments, consider a busway system. Busways are specifically designed for high-current distribution and may have different ampacity adjustment rules. However, they are typically much more expensive than wireways.
Example (Without Diversity)
Let's say you have #3 THHN copper conductors and need to supply 100A to each apartment (after all demand factors are applied) Without adjustment, #3 THHN is rated for 100A (Table 310.16). With 34 conductors in the wireway, you need to apply an 80% adjustment factor (310.15(C)(1)). Adjusted ampacity of #3 THHN: 100A 0.80 = 80A.In this scenario, a #3 THHN wire would not be sufficient. You would need to go to a larger conductor size (at least #1 THHN copper for 115A .8 = 92A) or you would need to run multiple wireways.
Important Considerations
Neutral Conductors
Be very careful about counting neutral conductors. In a 3-phase system, neutrals are generally not counted as current-carrying conductors unless they carry significant harmonic currents (see 310.15(C)(1) Note 5). However, you must account for neutrals if they carry the majority of the current load due to unbalanced loads.
Grounding Conductors
Equipment grounding conductors (EGCs) are generally not counted as current-carrying conductors for ampacity adjustment purposes.
Terminations
Don't forget to check the temperature rating of your terminations (breakers, meter sockets, etc.). You may need to use conductors with a higher temperature rating to match the termination rating (e.g., 90°C).
In summary, consult the Massachusetts amendment and your local inspector first. Explore load calculations to justify diversity. If that fails, use multiple wireways, larger conductors, or possibly a busway system.
This is a complex situation. Get expert advice and be prepared to provide thorough documentation. Good luck! Flag for review