Question: So I was looking at the chart for conduit wire fill shown in the first link. I noticed that a 2" LB67 can carry only three 1/0 conductors, but a 2" LL67 or LR67 can carry six 1/0 conductors. That seem counter-intuitive, especially comparing 2020 NEC 314.28 (A) (2) exception, with the second link with the conduit body dimensions.What am I missing? Everything being equal, I'd much rather run wires into an LB than an LL or LR.https://www.eaton.com/content/dam/eaton/products/conduit-cable-and-wire-management/crouse-hinds/other/industrial-fittings-wire-fill-chart.pdf

You've stumbled upon a common point of confusion, and you're right to question it! The discrepancy in wire fill capacity between an LB and LL/LR conduit body of the same trade size (like 2") comes down to a combination of physical space inside the fitting and National Electrical Code (NEC) requirements for pulling conductors. Let's break it down

Why the LB is More Restrictive:
Internal Geometry and Bends

The LB (LB67 in your example) has a much tighter internal bend than an LL or LR. The bend in an LB is sharp and abrupt, creating significant friction and strain on conductors during pulling. The NEC recognizes this and limits the number of conductors allowed to prevent damage to the insulation and ensure ease of pulling.


Limited Access for Pulling

The opening of an LB is smaller and often obstructed by the internal geometry. This makes it more difficult to get a good grip on the conductors and pull them through without damaging them.

Why LL/LR Can Accommodate More



Gentle Bends

LL and LR fittings have a much wider, more gradual bend compared to the LB. This reduces friction and pulling tension.


Larger Opening

The large opening on an LL and LR provides much more direct access for pulling conductors. It also allows for better visibility to confirm they're entering into the conduit properly.

Straight Pulls

When properly aligned, conductors enter and exit LL/LR bodies on a single plane. This means that the conductors are not bent during their transit.

NEC Implications
314.28(A)(2) Exception

You correctly pointed out the 314.28(A)(2) exception for conduit bodies. This exception is related to the size of the conduit body itself, not just the trade size of the conduit entering it. The exception allows for smaller conduit bodies if they are marked with their volume. This marking, however, does not automatically equate to a higher fill capacity. It simply allows you to calculate the fill based on volume rather than the conduit size, which may or may not result in a higher conductor allowance.

Key Takeaways



The sharp bend in an LB is the limiting factor,
not just the physical space inside. LL and LR fittings are designed for easier pulling with gentler bends. NEC requirements prioritize conductor protection and ease of installation. While you might prefer an LB for certain layouts, the NEC restrictions on wire fill are there for a reason: to prevent damage to conductors and ensure a safe and compliant installation.

Recommendations Follow the Manufacturer's Wire Fill Charts

Always refer to the manufacturer's wire fill charts (like the Eaton one you linked) or the NEC tables for accurate information.


Consider Pulling Tension

Even if a conduit body can physically accommodate the number of conductors, consider the pulling tension. Too much tension can damage the insulation and make future maintenance difficult. Use pulling lubricants and proper techniques.*

Choose the Right Fitting for the Job:
Select the conduit body that is appropriate for the layout, the number of conductors, and the bending requirements. If you're concerned about tight bends and a large number of conductors, an LL or LR might be a better choice than an LB.You are very observant to notice this difference! It's exactly this type of critical thinking that ensures safe and compliant electrical installations. Flag for review