User: Joethemechanic, Location: Hazleton Pa
Asked on: Sunday, October 5, 2025 at 5:40 pm EDT
Answered on: Sunday, October 5, 2025 at 5:55 pm EDT
Question: Something like thisCan the sum total amperage of the breakers exceed the amperage of the service?Using this panel for example, could you install six 25 amp 3 phase breakers for a total of 150 amps? And if so, what are the limitations and can the sum of the amperage exceed the rating of the service conductors also?
You've hit on a very important concept in electrical systems: the difference between breaker capacity and actual load. The answer is a qualified YES, but with significant caveats.
Here's a breakdown
Breaker Capacity vs. Actual Load
Breakers are protection devices. They are sized to protect the wiring they feed. They do not necessarily represent the actual continuous current that a device will draw.
Diversity and Load Calculations
Electrical systems are designed based on calculated loads, not the sum of all breaker ratings. The National Electrical Code (NEC) and local codes mandate specific methods for calculating loads, taking into account:
Demand Factors
Not every appliance or device will be drawing its maximum current simultaneously. Demand factors are used to estimate the likely maximum load on a circuit or service. For example, in a dwelling, you don't assume all receptacles in the kitchen will be running at their maximum simultaneously.
Diversity
Similar to demand factors. Different types of loads have different diversity. Lighting might have a high diversity, while heating or cooling might have a lower diversity (they run more continuously).
Continuous vs. Non-Continuous Loads
The NEC distinguishes between continuous loads (operating for 3 hours or more) and non-continuous loads. Continuous loads are often required to be derated, meaning the breaker and wiring must be sized for 125% of the continuous load.
Answering Your Specific Questions
"Using this panel for example, could you install six 25 amp 3 phase breakers for a total of 150 amps?" Yes, technically, you could install those breakers, provided the calculated load using NEC methods for each individual 3 phase device meets the requirements. But simply adding up the breaker ratings is meaningless. The key is: What are those 3-phase loads? Are they motors? Heaters? Lighting? The NEC has different rules for each type of load. What is the calculated load for each 3 phase device using NEC methods? Is the calculated load for each device 20 amps? 15 amps? Will each device or appliance actually draw 25 amps? "What are the limitations?"1. Calculated Load
The total calculated load on the panel (using NEC methods) must not exceed the service rating. This is the most important limitation.2.
Conductor Ampacity
The conductors feeding the panel (service conductors) must have an ampacity (current-carrying capacity) equal to or greater than the calculated load, and no less than the rating of the overcurrent device (main breaker).3.
Panelboard Rating
The panelboard itself has a maximum amperage rating. Make sure you do not exceed this value.4.
Available Physical Space
Obviously, you're limited by the number of breaker spaces available in the panel.
"Can the sum of the amperage exceed the rating of the service conductors also?" NO. The service conductors must be sized to carry the calculated load, but generally, not less than the rating of the panel or the main breaker in the panel. This is a fundamental principle of electrical safety. The service conductors are the wiring from the utility connection (meter) to your main electrical panel. Their ampacity (how much current they can safely carry) is determined by their size (gauge) and insulation type.
Example to Illustrate
Let's say you have a 100-amp service panel and you want to install six 20-amp, 120V branch circuits.
Breaker Capacity
The sum of the breaker capacity is 6 20 amps = 120 amps.
Actual Load
If each circuit powers general-purpose receptacles, you wouldn't expect them all to be loaded to 20 amps simultaneously. Demand factors (NEC Article 220) would allow you to calculate a lower calculated load.
Service Calculation
If, after applying the demand factors, the calculated load on the panel is 80 amps, you're within the capacity of the 100-amp service.
In Summary
Breaker ratings are for protection, not necessarily an indication of actual load. Electrical systems are designed based on calculated loads using the NEC and local codes. The sum of breaker ratings can often exceed the service rating because of demand factors and diversity. The calculated load must never exceed the service rating or the ampacity of the service conductors.
Always consult a qualified electrician for any electrical work. Incorrect calculations or installations can be dangerous.Important Note: This information is for educational purposes only and should not be considered a substitute for the advice of a licensed electrician. Electrical work can be dangerous and should only be performed by qualified professionals. Flag for review