Topic: NEC Continuous and Non-Continuous and System Size

User: kerrys914, Location: St. Louis

Asked on: Monday, October 6, 2025 at 3:19 pm EDT
Answered on: Monday, October 6, 2025 at 3:37 pm EDT

Question: Is the below correct?320amp (400amp max) Meter Center ApplicationLets say I have 350amps load on my 400amp MDP.200amp continuous loads150amp non-continuous loadsWill the 320amp meter center/socket be a correct application? My understanding as long as the continuous load is 320 or less and the combined loads (non + continuous) is 400amps or less, the 320amp meter will be fine.Cheers

You're close, but there are a couple of important nuances to consider when sizing a meter center. Let's break it down

Understanding the Code Requirements (NEC is the primary guide here):
125% Rule for Continuous Loads

Continuous loads (loads expected to operate for 3 hours or more) need to be calculated at 125% of their actual value.


Total Load Calculation

You add the calculated continuous load (125% of actual) to the non-continuous load to get the total calculated load.

Meter Center Ampacity

The meter center's ampacity needs to be
at least as high as the total calculated load.

Your Scenario Breakdown


Continuous Load Calculation

200 amps (continuous) 1.25 = 250 amps (calculated continuous load)2.

Total Calculated Load

250 amps (calculated continuous) + 150 amps (non-continuous) = 400 amps

Analysis

Your total calculated load is 400 amps. The 320 amp meter center is not adequate. You need a meter center rated for at least 400 amps.

Why a 320A Meter Center is Insufficient

The NEC requires that the meter center (and the service entrance conductors) be sized to handle the calculated load, which includes the 125% factor for continuous loads. A 320A meter center would be overloaded and potentially dangerous.

Key Takeaways



Don't Confuse Maximum vs. Calculated Load

A "400 amp max" designation on the MDP doesn't mean you can automatically use a 320 amp meter center if the
actual load on the MDP is less than 400 amps. You MUST perform the load calculation according to the NEC.

Continuous Loads are Critical

The 125% rule for continuous loads is essential in determining the correct size of service equipment.*

Consult a Qualified Electrician

Load calculations can be complex, especially for larger services or specialized equipment. Always consult with a licensed and experienced electrician to ensure that the service equipment is properly sized and installed in accordance with local codes and regulations.

In summary, you need a 400 amp meter center (or larger) for this application.
Using a 320 amp meter center would be a violation of the NEC and could create a fire hazard. Flag for review