Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Typical number of strands #10 AWG Copper

User: brycenesbitt, Location: United States

Asked on: Monday, October 6, 2025 at 4:00 pm EDT
Answered on: Monday, October 6, 2025 at 4:00 pm EDT

Question: Without asking Gemni, how many strands are typical for #10 cable?I was doing a build in a UL508A facility and all the #10 wire they had was very fine stranded, and was a royal PITA to get into the lugs cleanly.I brought some 19 strand wire and that was fine. Are there other strand counts available (I've never cared before ;-)

You're right, "typical" #10 isn't as straightforward as it used to be. Here's the breakdown: Solid #10

Obviously, this is
one strand. It's common in residential wiring (NEC), but less so in industrial control panels (UL508A) where vibration can be a concern.

7 Strand #10

This is a very common stranded version, sometimes called "standard stranded."

19 Strand #10

This is more flexible than 7 strand, and what you used. It's also a fairly common count.


Highly Flexible #10

This is where it gets tricky, and what you likely encountered. These cables can have strand counts in the hundreds (e.g., 105, 133, 259) of very fine strands. They are designed for applications with constant flexing or tight bend radii, such as robotics, cable carriers (drag chains), and machine tools.

Other Strand Counts

Yes, other counts
do exist, but are far less common. You might find them in specific industrial or automotive applications.

Why the headache?
The very fine strands in highly flexible cable splay out easily and are a pain to terminate in standard lugs. Using ferrules (crimp-on end sleeves) is essential with these fine-stranded cables. They keep the strands together and provide a solid connection.

UL508A Implications: UL508A requires components and wiring to be installed per their listing. Using the correct ferrules and termination techniques is crucial for meeting UL standards, especially with fine-stranded conductors. Also, make sure the lugs are sized appropriately for the wire gauge
and* stranding type, and torqued correctly. Flag for review

Previous Question Next Question