Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: If I have a 120/240 Panel 100 amp can I have 80 amps on each phase.

User: kjroller, Location: Dawson Mn

Asked on: Monday, October 6, 2025 at 4:58 pm EDT
Answered on: Monday, October 6, 2025 at 4:58 pm EDT

Question: My question is Just to clarify what I believe I already know but in a 120/240 panel you only want to load it to 80% continuously I understand so 80 amps on a 100-amp service and each phase can carry 80 amps. Is this correct and would the same statement be true for a 100-amp 3phase 480-volt panel you could have 80 amps on each of the 3 phases?

You are on the right track, but let's refine your understanding

Understanding the 80% Rule (Continuous Loads)

The 80% rule (or the 125% rule, looked at from the other side) is about protecting conductors and overcurrent devices (like breakers) from overheating when subjected to continuous loads. Continuous Load Definition

A load is considered "continuous" if it operates at its maximum current draw for

3 hours or more
.

Your Understanding - Corrected and Expanded

Here's the breakdown for both single-phase and three-phase panels

1. Single-Phase 120/240V, 100-Amp Service:

Your Understanding

You correctly identified that you shouldn't load the panel to more than 80% of its rating

with continuous loads
. Refinement

This means that the
total continuous load on the panel should not exceed 80 amps. Each leg (L1 and L2) can carry a combination of continuous and non-continuous loads.

Calculation

The calculation is slightly more complex than simply saying "80 amps per leg." You need to calculate the total continuous load on each leg (L1 and L2) and ensure that neither leg exceeds 80 amps of continuous load. Non-continuous loads are added to this calculation to see what the total load is.

Example

L1 has a 40-amp continuous load (e.g., water heater). L2 has a 30-amp continuous load (e.g., some lighting circuits). This is acceptable because neither leg exceeds 80 amps of continuous load. BUT Then, if L1 had 60 amps of continuous load and a 30-amp non-continuous load for a total of 90 amps on that leg, that is not acceptable.

Key Point

The 80% rule applies to the continuous portion of the load. Non-continuous loads can exceed the 80% limit.

2. Three-Phase 480V, 100-Amp Panel



Your Understanding

Your statement about the 80% rule and 80 amps per phase is generally correct,
if we are only considering continuous loads.

Refinement

The same 80% rule applies to each phase (A, B, and C) individually when considering continuous loads.

Calculation

The
total continuous load on each phase should not exceed 80 amps.

Example

Phase A has a 50-amp continuous load. Phase B has a 60-amp continuous load. Phase C has a 70-amp continuous load. This is acceptable.

Important Considerations for Both Single-Phase and Three-Phase



Demand Factors

Building codes (like the NEC in the US) allow for the use of "demand factors" in some cases. These factors allow you to reduce the calculated load for certain types of equipment (e.g., multiple appliances in a dwelling unit are not likely to all operate at full load simultaneously). Demand factors are complex and must be applied according to code. Do NOT apply these unless you have specific code knowledge and a valid reason.


Nameplate Ratings

Always use the nameplate ratings of equipment to determine their current draw.

Motor Loads

Motor loads are a special case. You often need to use 125% of the motor's full-load current (FLC) when sizing conductors and overcurrent protection.


Voltage Drop

Ensure that voltage drop is within acceptable limits. Long wire runs can cause voltage drop, which can affect equipment performance and safety.

Professional Consultation



Always consult with a qualified electrician or electrical engineer for any electrical work.
Electrical systems can be dangerous, and proper design and installation are critical for safety and code compliance. This information is for educational purposes only and should not be used as a substitute for professional advice.

In summary: Yes, you're generally correct about the 80% rule limiting the
continuous load on each phase, but understanding how the 80% rule is applied to continuous loads versus* total loads, and understanding that you must account for both L1 and L2 on the single-phase panel, is critical. Plus, you need to consider the other factors like demand factors, motor loads, and voltage drop. Flag for review

Previous Question Next Question