Question: Client says her bedroom circuit trips every 5 ish days.. I took a look in the panel and took the hot and neutral off the breaker. I did continuity test between all conductors and got nothing. I did an ohms test between hot and neutral and it was showing 178ohms of resistance.. I know a 500ft spool of #12 wire has 0.5 ohms of resistance so why did this hot/neutral have 178 ohms of resistance? Could there be a small pinch or knick in the wire somewhere within that Romex causing a very very slow trip since it’s on an arc fault breaker? The panel is roughly 100-120 feet from the bedroom, it’s in an assisted living facility
Okay, let's break down the situation and analyze the possible causes for the nuisance tripping and the resistance reading you're getting.
Understanding the Situation Intermittent Tripping
A circuit tripping every 5 days is a definite problem and needs investigation.
Arc Fault Breaker
Arc-fault circuit interrupters (AFCIs) are designed to detect dangerous arc-faults, but they can be prone to nuisance tripping. However, it's important to rule out actual arc faults first.
Isolation
You properly isolated the circuit by removing the hot and neutral wires from the breaker. This is the correct procedure for testing.
Continuity Testing
Good you tested for shorts between conductors. This confirms no immediate short.
Resistance Reading
178 ohms between hot and neutral on an isolated circuit is the key here and the most concerning.
Why 178 Ohms is Significant (and Not Expected) Expected Resistance
In a properly wired, unloaded circuit, you should see very high resistance (approaching infinity) between the hot and neutral when the circuit is isolated. A reading of 178 ohms indicates something is creating a path for current to flow.
Resistance of Wire
As you correctly pointed out, the resistance of the wire itself is negligible for a 100-120 foot run.
Possible Causes for the 178 Ohm Resistance
Here's a breakdown of the most likely culprits, in order of probability:1. Appliances/Devices Connected to the Circuit
This is the MOST LIKELY CAUSE. Even with the circuit breaker off, anything plugged into an outlet on that circuit can provide a path between hot and neutral. Wall warts, phone chargers, lamps, TVs, etc., all contain components that will register some level of resistance. Even if "off," they are still connected to the circuit.2.
Moisture/Contamination
This is especially likely in an assisted living facility.
Outlet Boxes
Water spills, cleaning solutions, or even condensation can get into outlet boxes and create a conductive path, especially if there's dust or debris present.
Within Devices
The same can happen inside lamps, radios, or other devices.3.
Compromised Insulation (Low Probability)
Knick or Pinch in Wire: This is very unlikely to be the sole cause of 178 ohms, but it could contribute. If there's a nick in the insulation that's exposed to a slightly damp environment, it could create a leakage path. Old/Deteriorated Wiring
In rare cases, especially with very old wiring, the insulation can degrade and become slightly conductive. This is less likely with Romex used in relatively recent construction.4.
Neutral-Ground Fault (Less Likely, but Possible)
While you checked for shorts, a high-resistance fault between neutral and ground could also indirectly show up as a resistance between hot and neutral. This is less likely if the wiring is relatively new and properly installed.
Troubleshooting Steps (in order)
Unplug Everything
This is the FIRST and MOST IMPORTANT STEP. Go to the bedroom and systematically unplug every single thing that's plugged into any outlet on that circuit, including lamps, clocks, phone chargers, TVs, etc. Then, go back to the panel and re-measure the resistance between hot and neutral. If the resistance goes up to a very high value (megohms or higher), you've found the problem. One of the devices you unplugged is leaking current. Plug them back in one by one, testing after each, to identify the culprit.2. Visual Inspection of Outlets
Carefully remove the cover plates of the outlets in the bedroom (AFTER ENSURING THE CIRCUIT IS OFF). Look for: Signs of moisture or corrosion. Loose connections (though these usually cause immediate tripping). Overheating (discoloration, melting). Evidence of pests (mice can chew on wires).3.
Check Light Fixtures
Do the same visual inspection of any light fixtures on the circuit.4.
Insulation Resistance Testing (Megger)
If you still haven't found the problem, you'll need to do more advanced testing. A megohmmeter (megger) applies a high voltage to the circuit and measures the insulation resistance. This can reveal even small insulation faults that a standard ohmmeter might miss. This is best left to a qualified electrician with experience using a megger. Important: You MUST disconnect all devices before using a megger to avoid damaging them.5.
Check Wire Connections
If the previous steps haven’t yielded results, inspect all wire connections within the affected circuit. Pay close attention to any junctions, splices, or points where the wires connect to outlets, switches, or fixtures.
Important Considerations
Safety First
Always work with circuits that are de-energized (breaker off and verified with a non-contact voltage tester). If you're not comfortable working with electrical wiring, hire a qualified electrician.
Document Everything
Keep a log of your troubleshooting steps and the results. This will help you (or another electrician) track down the problem.*
Assisted Living Environment
Be mindful of the residents and their belongings. Communicate clearly and be respectful.
In Summary
The 178 ohm resistance reading is the most important clue. Unplugging everything on the circuit is the crucial first step. If the resistance remains low after unplugging everything, further investigation (likely with a megger) is needed to find the fault in the wiring. Good luck! Flag for review