Question: First time I'm seeing IMC, just an FYI. Does it make sense they are showing two different insulations and also aluminum and copper for? Seem like this is a mistake,

You're right to be questioning the mix of insulations and conductors in the same context with IMC (Intermediate Metal Conduit). It sounds like you're looking at a table, specification, or drawing that's confusing the properties of the conduit with the properties of the conductors that might be run inside that conduit.Here's a breakdown of why this seems inconsistent and how to understand it: IMC (Intermediate Metal Conduit) is a raceway. Think of it as a protective pipe for wires. Its purpose is: Mechanical Protection: Shields conductors from physical damage. Grounding: When installed properly, it can serve as an equipment grounding conductor. Fire Resistance: Helps contain fires. Conductor Insulation (e.g., THHN, XHHW) is the insulation around the wires that carry the electricity. Its purpose is: Electrical Insulation: Prevents short circuits and shocks by isolating the current-carrying conductor. Specific Environmental Ratings: Rated for certain temperatures, wet/dry locations, oil resistance, etc. Conductor Material (Copper, Aluminum) is the actual metal carrying the electricity. Its purpose is: Conducting electricityWhy mixing these is confusing

The
conduit material and type (like IMC) is independent of the conductor insulation and material inside it. You choose:1.

The Conduit (IMC)

Based on the
environment where it's being installed (corrosion, physical damage risk, etc.) and based on local codes.2.

The Conductors (Wires)

Based on:
The electrical load (how much current needs to be carried). This determines the wire gauge (size). The environment inside the conduit and at the termination points. This determines the insulation type. (e.g., THHN is common for dry locations; XHHW is common for wet locations) Budget and wire length, dictates if you will use copper or aluminum (aluminum has more voltage drop)

Possible Scenarios Where You Might See These Mentioned Together (But Not Intermixed)


Ampacity Tables

NEC (National Electrical Code) ampacity tables will specify the maximum allowable current for different conductor sizes (gauges) AND will have correction factors based on the ambient temperature around the conduit and the number of conductors inside the conduit. This is where you might see various insulation types (THHN, THWN, etc.) listed alongside the conduit type (IMC, PVC, etc.) because the allowable current changes depending on the insulation's temperature rating.2.

Specification Documents

A specification for a project might say something like, "All branch circuit wiring shall be run in 3/4" IMC. Conductors shall be THHN/THWN-2, copper, sized per NEC Table 310.16." This specifies the conduit AND the acceptable conductors that can be used inside it, but they're distinct choices.3.

Fill Calculations

NEC Article 358 limits how much of the cross-sectional area of a conduit can be filled with conductors. You need to know the diameter of each conductor (which depends on the insulation type) and the inside diameter of the conduit (which depends on the conduit type) to perform this calculation.4.

Grounding Specifications

The grounding requirements for electrical systems often require specifying the type and size of grounding conductor required, and in some cases the grounding conductor might be run inside the conduit (but more often grounding is accomplished by using the conduit as the ground). Grounding specifications would also indicate that the conduit is rated for ground usage.

In Summary

IMC is a raceway (a protective tube). Insulation (THHN, XHHW, etc.) is a property of the wires inside the raceway. Conductor material (copper, aluminum) is a property of the wires inside the raceway.

Therefore, showing different insulations and conductor materials
directly associated with the IMC itself would be a mistake.
The IMC specification should focus on its* properties: material (steel, aluminum), size, coating, etc. The conductor insulation and material will be specified separately, based on the wiring requirements.To give you a more definitive answer, can you describe where you're seeing this information? (e.g., "It's in a table listing conduit types," or "It's on a drawing detail for a panel.") The more context you provide, the better I can help you understand it. Flag for review