Topic: 320a meter with disconnects

User: RdmanElect, Location: Poughkeepsie NY

Asked on: Tuesday, October 7, 2025 at 3:47 pm EDT
Answered on: Tuesday, October 7, 2025 at 3:47 pm EDT

Question: I'm drafting up a 320a meter with 2 disconnects for 2 Seperate 200a panels going into the same mechanical room.Is it a code violation to have them in Seperate enclosures as shown in the mike holt photo? Mind you it's coming from a stanchion 60 feet off the house.Does the 2 feeders need to be in the same panel or enclosure? I'm having trouble finding a 320 meter with 2 built in 200a breakers

Okay, let's break down the code issues and practical considerations for your 320A meter setup with two 200A panels.

Understanding the Key Code Issues

The primary concerns will be:1. Overcurrent Protection

Your installation must provide overcurrent protection for the feeders to each 200A panel. The overcurrent protection should be rated to protect the conductors. The service lateral from the stanchion MUST be correctly sized and protected for the load it's serving.2.

Grouping of Disconnects

The NEC requires grouping of disconnects in certain situations, particularly for services.3.

Service Entrance Conductors

The run from the stanchion to the disconnects is part of the service entrance conductors.4.

Accessibility

The disconnects must be readily accessible.

Analyzing the Separate Enclosures Scenario (Mike Holt Photo)


Referring to the Mike Holt photo (I'm assuming you're referencing a typical meter/disconnect arrangement), here's what's critical: Meter

The meter socket itself is usually provided by the utility. It's
not part of your equipment and is not what is being discussed.

Disconnects

The two 200A disconnects are in separate enclosures.

Code Violation? Probably NOT, with caveats.


Having separate enclosures for the two 200A disconnects is generally permitted, but only if you meet all of these conditions (which is a complex setup)



Service Entrance Conductors (230.40)

NEC 230.40 permits multiple service entrance conductor sets to supply one building under specific conditions. The most common applicable exception is:


(3) Capacity Requirements

If the capacity requirements exceed the maximum size of one service drop or service lateral. This is likely your scenario.



Grouping of Disconnects (230.72(A))

The disconnects must be grouped. The NEC requires service disconnects to be grouped and readily accessible at a readily accessible location nearest the point of entrance of the service conductors. This can be achieved in two different ways:


Adjacent

The two disconnects are located immediately adjacent to each other. This means side-by-side or directly above/below with minimal separation. The enclosures must be practically touching. This is what's usually pictured in Mike Holt material. If they are even a foot apart, it starts to raise concerns about compliance.

Remote Control (230.85)

Remote control ability is to be provided that allows disconnect of your service, typically for fire departments.


Proper Overcurrent Protection

As mentioned before, you must have overcurrent protection for each set of conductors feeding each 200A panel. Typically, this is achieved with a main breaker in each disconnect enclosure rated at 200A or less (based on conductor ampacity).

Correct Conductor Sizing

The service entrance conductors from the stanchion to the disconnects must be sized appropriately for the total load, taking into account demand factors. Just because you have a 320A meter base
doesn't mean you can run inadequate conductors. You must perform a load calculation per Article 220.

Approved Equipment

All equipment must be listed and labeled for its intended use.

Why Finding a 320A Meter with Two Built-In 200A Breakers is Difficult (and Usually Not the Right Approach)

Standardization

Utilities generally dictate the meter base they require. A single 320A meter base with two integral 200A breakers is not a common standard configuration, so manufacturers don't typically produce them.


Flexibility

Utilities prefer the ability to independently control the meter and disconnects. A single unit with built-in breakers limits this.

Cost

It would likely be a custom (and expensive) piece of equipment.

The Recommended Approach (and Likely What the Mike Holt Photo Shows)1.

Utility Coordination

First and foremost,

contact your local utility company. They will have specific requirements for the meter base, disconnects, and any other requirements for the service. They are the
authority having jurisdiction (AHJ) regarding the meter and service connection.2. 320A Meter Base

The utility will specify the required meter base.3.

Two Separate 200A Disconnects

Use two
separate 200A disconnect enclosures. These are key. Each disconnect should contain a 200A main breaker (or a breaker rated appropriately for the conductor ampacity). These are readily available from electrical supply houses.4.

Grouping

Mount the two disconnect enclosures
immediately adjacent to each other (side-by-side or directly above/below) as close as physically possible. This achieves the required grouping.5.

Conduit and Conductors

Run properly sized conductors from the meter base to each disconnect enclosure. Use conduit for physical protection and to meet code requirements. Make sure the conductors are rated for the application (THHN/THWN, etc.).6.

Feeders to the Panels

Run appropriately sized feeders from each 200A disconnect to its respective 200A panel in the mechanical room.

Advantages of This Approach


Code Compliance

Easier to comply with the NEC.

Standard Equipment

Uses readily available and cost-effective components.


Utility Acceptance

More likely to be approved by the utility.

Flexibility

Allows for easier maintenance and replacement.

Important Considerations


Load Calculation

Perform a thorough load calculation according to NEC Article 220 to determine the actual load requirements of the building. This will ensure that the service entrance conductors, meter base, and disconnects are adequately sized.

Demand Factors

You can use demand factors in your load calculation, but be sure to use them correctly and justify them to the AHJ if necessary.


Local Amendments

Be aware of any local amendments to the NEC that may affect your installation.

Inspection

Have the installation inspected by a qualified electrical inspector to ensure that it meets all applicable codes and regulations.

In Summary
While having separate enclosures for the two 200A disconnects is possible, it requires careful attention to detail and strict adherence to the NEC and local codes. The key is proper grouping, overcurrent protection, and correct conductor sizing. Contact your utility first* to determine their requirements, and then work with a qualified electrician to design and install the service. Flag for review