Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 277V>>120V, 1PH XFMR Bonding

User: Fishn sparky, Location: Washington State

Asked on: Wednesday, October 8, 2025 at 7:42 am EDT
Answered on: Wednesday, October 8, 2025 at 7:47 am EDT

Question: Good morning team,I have a 277V>>120V step down xfmr. The xfmr is mounted in a vented, 12"x12"x6" deep junction box. This xfmr is fed from a 277v/1PH/20A branch circuit. The secondary side is fused and feeds one general purpose receptacle. The xfmr housing does not have a connection for a system bonding jumper.The question, when I take a reading from line>>ground on the secondary side, I get 36V. I believe that this is due to the xfmr secondary not having a system bonding jumper. If the xfmr housing doesn't have a connection for the bonding jumper, my thought is the neutral terminal on the secondary side would need to have a connection to the EGC terminations of the primary side, junction box and secondary supply side bonding jumper.Please confirm my thinking is correct. I appreciate everyone's time!

Good morning! Yes, your thinking is correct. Let's break down why and the code considerations

Understanding the Issue
Ungrounded Secondary

Without a connection to ground (a system bonding jumper), the secondary side of the transformer is effectively floating. It's capacitively coupled to the primary side and surrounding environment, resulting in the voltage you're seeing (36V line-to-ground). This voltage isn't necessarily dangerous in terms of amperage, but it's a safety hazard because it can rise significantly under fault conditions and, as you pointed out, isn't reliably there.


Purpose of System Bonding Jumper (SBJ)

The system bonding jumper provides a low-impedance path for fault current to return to the source (the transformer's secondary neutral point). This allows the overcurrent protection device (your fuse on the secondary) to quickly trip and clear the fault, protecting people and equipment.

Your Proposed Solution and NEC Considerations


You are correct that connecting the secondary neutral to the primary EGC (equipment grounding conductor) system is the solution to ground the secondary. Here's how to do it, along with relevant code sections:1. Locate the Secondary Neutral

Identify the neutral terminal on the 120V secondary side of the transformer.2.

Establish the System Bonding Jumper

Connect a properly sized conductor from the secondary neutral terminal to the equipment grounding conductor (EGC) system.

Important

This connection must be made at the transformer location (inside the junction box). This becomes the point where the secondary is considered a separately derived system. Use an EGC with the proper current carrying capacity.

NEC 250.30
talks about grounding separately derived systems3. Connect to EGC System

Connect the SBJ to the nearest available point on the EGC system in the junction box. This would include: The grounding conductor from the 277V primary circuit. The metal junction box itself (if properly grounded). The EGC running with the 120V branch circuit supplying the receptacle.

Why this works
This creates a solid, low-impedance ground reference for the secondary side. It ensures that a fault on the secondary side will quickly trip the secondary fuse. It provides a predictable, low-voltage potential to ground on the secondary side under normal conditions (very close to 0V).

Important Considerations & Best Practices Conductor Sizing

The size of the system bonding jumper (SBJ) needs to be determined based on the size of the secondary conductors feeding the receptacle.

Refer to NEC 250.30(A)(1).
Generally, it will need to be at least the size of the ungrounded secondary conductor. You could go with a #12 copper conductor.
Tight Connections

Ensure all connections are clean, tight, and properly made using appropriate connectors (e.g., screw terminals, crimp connectors, split bolts).

Inspection

After making the connection, re-measure the voltage between the line and ground on the secondary side. It should now be very close to 60V (120V/2). Also, verify the resistance from the secondary neutral to the junction box is very low (ideally close to 0 ohms).


Permanently Grounded Transformer

Although your transformer doesn't have a dedicated ground lug, you can sometimes ground to the transformer case by using an "add-a-ground" lug, which clamps to the metal. This would add a redundant grounding path. This is not strictly required but is considered a best practice.

In summary, your proposed solution is correct and necessary to ensure the safe and proper operation of the transformer and the receptacle it feeds. Follow the NEC guidelines and best practices to ensure a solid, reliable ground connection.
Disclaimer: I am an AI Chatbot and not an electrical expert. Always consult with a licensed electrician for any electrical work. Flag for review

Previous Question Next Question