Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Service and other enclosures

User: Therealcrt, Location: Kansas City

Asked on: Wednesday, October 8, 2025 at 8:50 am EDT
Answered on: Wednesday, October 8, 2025 at 8:51 am EDT

Question: I’m reading 250.92 and 250.96 and 250.97 250.92B says that if basically reducing washers are used or oversize concentric or eccentric knockouts, they would need a bonding bushing at the service regardless of the voltage of the service. 250.97 basically says if any circuit is over 250 V to ground and the enclosure encounters a concentric or eccentric knockout it’s not encountered then a standard EMT connector or listed fitting will be sufficient enough and not require a bonding bushing at those enclosures, even though some people still put them on which is OK but not needed so does that mean that any conduit that has a circuit in it over 250 V to ground? And it enters an enclosure with concentric or eccentric knockouts or reducing washers then it would need a bonding bushing to that enclosure.? For instance if I run a piece of conduit from a panel up to a junction box and I enter that junction box to a concentric or concentric knockout and it’s got 277 V for lighting. I need to put a bonding bushing on the inside of that connector inside the enclosure and bond it to the enclosure, correct?

You've identified a point of confusion in the NEC, and it's a common one. Let's break down the applicable sections and clarify the requirements.250.92(B) - Services

This section specifically addresses bonding requirements at the service equipment. It states that methods other than those permitted in 250.92(A) shall be used where necessary to ensure the electrical continuity of metal raceways and metal enclosures containing service conductors. Specifically, it calls out:

Reducing Washers or Oversized, Concentric, or Eccentric Knockouts

When these are encountered at the
service, they must be bonded using listed bonding bushings or bonding jumpers, regardless of voltage.

250.96 - Bonding Other Enclosures

This section deals with bonding enclosures containing circuits
other than services. It requires enclosures to be made electrically continuous.

250.97 - Bonding for Over 250 Volts to Ground

This section addresses the specific situation where a raceway containing circuits
over 250 volts to ground enters an enclosure through concentric or eccentric knockouts that are not designed for bonding. This is where the perceived conflict arises. This section also gives two methods that can be used: Listed Bonding-Type Locknut Standard locknut and a bonding jumper

Here's the Key Distinction



Service Equipment (250.92(B))

Always requires bonding bushings or bonding jumpers for concentric/eccentric knockouts, reducing washers, etc., regardless of voltage.

Other Enclosures (250.97)

Only requires special bonding when the circuit voltage is over 250 volts to ground

AND
the enclosure has knockouts not designed for bonding. Standard EMT connectors, listed fittings, bonding locknuts, and a standard locknut and bonding jumper are sufficient in these cases.

Addressing Your Specific Scenario

You have a conduit run from a panel to a junction box, entering the junction box through concentric or eccentric knockouts, and carrying 277V lighting circuits (which are over 250V to ground).

Therefore,
yes, you need to ensure proper bonding. Section 250.97 applies. In this case, a listed bonding-type locknut, a standard locknut and a bonding jumper, or a bonding bushing is required to ensure proper bonding to the junction box, provided the knockout is not designed for bonding.

Important Considerations



Knockout Design

Whether a knockout is "designed for bonding" isn't always obvious. If it has concentric rings designed to be broken out and provide a tight mechanical connection, it's less likely to be considered designed for bonding. If the knockout has teeth that bite into the enclosure, it is generally considered as providing an effective bonding connection. A listed fitting may be a good idea as that typically means that it has passed a bonding test.

Listed Fittings

If you use a listed fitting for the raceway that is designed to bond to the enclosure, that is an acceptable bonding solution as per 250.97.


Best Practice

While 250.97 provides minimum requirements, many electricians still use bonding bushings or bonding jumpers on all circuits over 250V to ground, regardless of the knockout type. This is a conservative approach and often a good practice for extra safety and to avoid potential issues with future inspections.

In Summary:


The apparent conflict arises from the different scopes of 250.92(B) and 250.
97. 250.92(B) is very specific about the service equipment. 250.97 provides options for ensuring the electrical continuity of other enclosures with circuits over 250V to ground. Your 277V lighting example falls under 250.97, requiring a bonding bushing, listed fitting, bonding locknut, or standard locknut and a bonding jumper when entering an enclosure with concentric/eccentric knockouts that are not designed for bonding. Flag for review

Previous Question Next Question