User: blueheels2, Location: Raleigh, NC
Asked on: Wednesday, October 8, 2025 at 10:20 am EDT
Answered on: Wednesday, October 8, 2025 at 10:20 am EDT
Question: I’m upgrading a service from 200 to 320/400 amp.We are currently under the 2017 for single family dwelling so I’m not required to have exterior disconnects.Room is tight so I was going to do away with exterior disconnects, but inspector said in this jurisdiction they adhere to to the 5’ rule or 2 stud bay rule unprotected conductors. Which caused me to send him an email about my plan which he says is a cod violation so I will lay it out for you. Please tell me the code if it’s wrong.I was going to mount the 320 meter outside nipple over about 12” in 2.5” into an exterior jbox slash trough (using this instead of 3” LB) pulling both sets of feeders in this 2.5”.From the back of the exterior box I was going 16” into a 2’ x 2’ x 8” jbox and then I was going to leave there with 2- 2” going to the 200 amp main breaker panels.Inspector says I can’t (or he doesn’t think I can ) leave the 320!meter with both sets of wires in the same conduit.You guys see a problem with that?
Okay, let's break down your plan and the inspector's concern based on the 2017 NEC, and potential interpretations.
Your Proposed Plan (Summarized)
320A Meter
Outside, feeds to a 2.5" nipple.
2.
2.5" Nipple (12")
From meter base to exterior J-box/trough. Both sets of service entrance conductors (SEC) for the two 200A panels are pulled through this single nipple.3.
Exterior J-Box/Trough
Receives the conductors from the meter.4.
2.5" Nipple (16")
From exterior trough to interior 2'x2'x8" jbox.5.
Interior J-Box
Feeds two 200A main breaker panels via (2) 2" conduits.
Inspector's Concern
The inspector is concerned about having
both sets of service entrance conductors (the feeders for both 200A panels) in the same conduit (the 2.5" nipple) from the meter base to the exterior J-box. This is the core of the issue.
Analysis and Relevant NEC 2017 Code Sections
230.7 Number of Services. Generally, a building or structure is permitted to have only one service. However, there are exceptions. You need to ensure your situation falls under one of the permitted exceptions. This is typically where the "320A service feeding two 200A panels" design comes into play for dwellings. You're essentially splitting the load, but it's still considered one service. 230.40 Number of Service-Entrance Conductor Sets per Service. Exception No. 2
Where two to six service disconnecting means in separate enclosures are grouped at one location and supply separate loads from one service drop or service lateral, one set of service-entrance conductors shall be permitted to supply each individual service disconnect(s).
Exception No. 3
A single-family dwelling unit and its accessory structure(s) shall be permitted to have one set of service-entrance conductors run to each from a single service drop or lateral.
310.3(H) Paralleled Conductors in Raceways or Cables 310.10(H)(1) General. Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, neutral, or grounded circuit shall be permitted to be connected in parallel (electrically joined at both ends) only where installed subject to the requirements of 300.5 or 300.
50. 310.10(H)(2) Conductor and Installation Requirements. (1) The paralleled conductors shall be the same length. (2) The conductors shall have the same conductor material. (3) The conductors shall be the same insulation type. (4) The conductors shall be terminated in the same manner. (5) Where run in separate raceways or cables, the raceways or cables shall have the same physical characteristics. 310.15(B)(3) Adjustment Factors. [Ampacity Adjustment] This section deals with derating conductors when there are multiple current-carrying conductors in the same raceway or cable. You absolutely need to perform ampacity calculations to ensure your conductors are properly sized after applying any necessary derating factors. This is critical when you're putting multiple sets of service entrance conductors in the same conduit. 314.28 Sizing Pull Boxes, Junction Boxes, and Conduit Bodies. If you use a junction box, you will need to size it according to this section, based on the size and number of raceways entering and leaving the box, as well as the size of the conductors.
The Potential Problem: Improper Paralleling (Implicit in the Inspector's Concern)
The inspector's concern likely stems from an interpretation that your setup is effectively paralleling conductors, even though you're feeding two separate panels. By placing the entire 320A load into the 2.5" conduit, he may be viewing this as needing to meet parallel conductor requirements. Here's why:1. Load Sharing and Ampacity Derating
Even though the load should split between the two 200A panels, the reality is that, momentarily, one panel could draw more current than the other. Having all conductors sharing a single conduit increases the risk that those conductors could exceed their ampacity if derated. The inspector wants to ensure there's no overload potential.2.
Inductive Reactance and Impedance
Unequal inductive reactance and impedance can occur if the conductors from the meter to the panels are not balanced.
Analysis of Your Plan
Your proposed plan is generally legal so long as you follow all codes and guidelines. Here’s my personal thoughts1.
Service Entrance Conductors in Same Conduit
NEC doesn't explicitly prohibit multiple sets of service entrance conductors from sharing the same conduit from the meter base, but the inspector is likely concerned about the implications of doing so, primarily the need to meet paralleling requirements and the potential for overloading due to imbalanced loads.2.
Meeting Paralleling Requirements
If you do run both sets of SEC in a single conduit, the inspector will likely require strict adherence to parallel conductor rules. This means: Conductors must be sized according to 310.15(B)(3)(a). This means all conductors for both 200A panels inside the 2.5" conduit have to be counted for derating. This can significantly increase the conductor size. Conductors must be the same length, material, and have the same insulation. Terminations need to be identical. (Possibly) The inspector may require you to treat it as a true parallel situation and size the conductors based on the total service ampacity (320A), even if you're splitting it across two panels. This is unlikely if you keep them separate after the interior j-box.3.
J-Box Sizing
The 2'x2'x8" j-box seems generously sized, but double-check against 314.28 to ensure it meets the requirements for the conductor sizes and number of conduits.
How to Address the Inspector's Concerns & Possible Solutions
Detailed Load Calculations
Provide the inspector with detailed load calculations for each of the two 200A panels. This demonstrates that you've considered the load distribution and the potential for imbalance. It helps him understand the design is safe.2.
Conductor Ampacity Calculations
Show the inspector the ampacity calculations, including the derating for multiple current-carrying conductors in the 2.5" conduit. This will likely require significantly larger conductors than you might initially think.3.
Clarify Intent
Confirm that you are not paralleling conductors. You are simply splitting the service at an interior jbox.4.
Splitting at Meter
The simplest solution is to use separate conduits immediately from the meter base. You could use a meter base with two hubs or use a short nipple from the meter to an exterior jbox with two conduits leading from there to your two panels. This completely* avoids the paralleling concern because the conductors are not running together for any significant length.5.
Consider Parallel Conductors: If space is truly a premium, you could consider 2-2” Conduits from the meter. This would mean all conductors are being paralleled from meter.I am not an electrician, so seek professional help. I hope this was helpful in guiding you. Flag for review