Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ground resistance value for Fire Pup Controllers

User: federicop, Location: caracas, venezuela

Asked on: Wednesday, October 8, 2025 at 2:07 pm EDT
Answered on: Wednesday, October 8, 2025 at 2:17 pm EDT

Question: Is there a minimum ground resistance value for fire pump controllers using soft starters? I recently asked the supplier of a controller we are installing and he answered they don't have a value. I'm using the NFPA 70 value of 25 ohm minimum. Peer specialists have advised 5 ohm or less for equipment using electronic sensitive equipment. Thanks

You're asking a great question that highlights the difference between code-minimum and best practice, especially with sensitive electronic equipment like soft starters. Here's a breakdown

1. NFPA 70 (National Electrical Code) and 25 Ohms:
The Code Minimum

NFPA 70 (NEC) generally requires a ground resistance of

25 ohms or less
for a single rod electrode, and often requires supplemental electrodes to achieve that if necessary. This is primarily focused on personnel safety during ground faults. It's the minimum
acceptable level for electrical safety, not necessarily ideal for equipment performance.2. The Problem with 25 Ohms for Sensitive Electronics (Like Soft Starters)



Noise and Harmonics

Soft starters, and other electronic equipment, generate electrical noise and harmonics. A higher ground resistance (like 25 ohms) allows these unwanted currents to circulate, potentially causing:

Malfunctions

Spurious trips, erratic behavior, and communication problems.


Reduced Lifespan

Premature component failure in the soft starter and other connected equipment.

EMI (Electromagnetic Interference)

Disruption to nearby electronic devices.


Voltage Rise During Faults

A higher ground resistance means a higher voltage rise on the grounding system during a ground fault. This can damage sensitive components connected to the ground.

3. Why 5 Ohms or Less is Recommended for Sensitive Electronics



Reduced Noise

Lower ground resistance provides a lower impedance path for noise and harmonic currents to return to the source, minimizing their impact on the equipment.


Faster Fault Clearing

Lower resistance ensures faster operation of overcurrent protective devices (like circuit breakers) during a fault, reducing damage and improving safety.

Stable Reference Point

A lower ground resistance provides a more stable voltage reference point for the electronics, leading to more reliable operation.


Manufacturer Recommendations

Many manufacturers of electronic equipment (including some soft starter manufacturers, though it's not always explicitly stated) imply or recommend lower ground resistance through their installation instructions or troubleshooting guides.

4. Why the Supplier Said They "Don't Have a Value"



Code Compliance vs. Performance

The supplier is likely stating that their soft starter will
function within the code-required 25 ohms. They are focusing on meeting the minimum safety standard of NFPA 70.

Site-Specific Conditions

Optimal grounding depends heavily on soil conditions, the size of the electrical system, and the sensitivity of other equipment connected to the system. They can't provide a universal number.

Passing the Buck

Sometimes, suppliers avoid specifying a value because they don't want to be liable for grounding issues that are outside their control.

5. Recommendations and Best Practices



Aim for 5 Ohms or Less

You are correct to strive for 5 ohms or less, especially with electronic fire pump controllers and soft starters. This is considered best practice for reliable operation and protection of the equipment.

IEEE Standards

Consult IEEE Std 142 (Green Book) and IEEE Std 1100 (Emerald Book) for guidance on grounding sensitive electronic equipment. These standards provide more detailed information and recommendations than the NEC.


Grounding System Design

Ensure you have a well-designed grounding system, including:

Multiple Ground Rods

Connected together with a continuous conductor.


Grounding Ring (if practical)

A conductor encircling the building and buried in the earth.

Bonding

Properly bonding all metallic enclosures, conduits, and equipment together to create a low-impedance path.


Dedicated Grounding Conductor

Running a dedicated grounding conductor (green wire) back to the service entrance for all circuits supplying sensitive equipment.

Testing

Regularly test the ground resistance using a ground resistance tester.


Coordination with Electrical Engineer

Work with a qualified electrical engineer experienced in grounding to design and verify the grounding system. They can take into account the specific site conditions and equipment requirements.

Transient Voltage Surge Suppression (TVSS)

Installing TVSS devices at the service entrance and at the soft starter is highly recommended.

In summary:
While the supplier isn't wrong* in saying they don't have a specific grounding value, aiming for 5 ohms or less is a much better practice for the long-term reliability and performance of your fire pump controller and soft starter. Don't rely solely on the code minimum. Invest in a properly designed and installed grounding system. Flag for review

Previous Question Next Question