Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: I have a sauna that is about 100’ from power source, it is 25a 240v I’m using #10 THHN, my question is can I use a #12 ground?

User: Rsemp, Location: Oklahoma

Asked on: Thursday, October 9, 2025 at 8:31 am EDT
Answered on: Thursday, October 9, 2025 at 8:31 am EDT

Question: I have a sauna that is about 100’ from power source, it is 25a 240v I’m using #10 THHN, my question is can I use a #12 ground?

Okay, let's break down the grounding requirements for your sauna circuit. You're running a 240V, 25A circuit with #10 THHN conductors, and the sauna is 100 feet from the power source. You're asking if you can use a #12 AWG ground wire.

The short answer is: Yes, you likely can use a #12 AWG ground wire.

Here's why and the relevant code information: NEC (National Electrical Code) Table 250.122 This table is the key. It dictates the minimum size of the equipment grounding conductor (EGC) based on the rating of the overcurrent protection device (your 25A breaker). According to NEC Table 250.122, for a 25A overcurrent device (breaker), the minimum size of the equipment grounding conductor (EGC) is #12 AWG copper.

Important Considerations and Best Practices



Voltage Drop

You're already using #10 wire due to the distance to prevent voltage drop (which is good practice). While the
minimum allowed ground is #12, consider these:

Future Upgrades

If there is any possibility you might upgrade the sauna in the future (e.g., a larger heater requiring a higher amperage), it's often wise to run the #10 ground now. It's far easier to do it during the initial installation.

General Practice

Some electricians prefer to run the ground wire the same size as the circuit conductors for simplicity and as a best practice, even if the code allows a smaller ground.


Conduit Type

If your wiring is in metal conduit (rigid, IMC, or EMT), the conduit itself can serve as the equipment grounding conductor. If this is the case, you don't necessarily need to run a separate ground wire, provided the conduit is properly installed with tight, clean connections. Using the conduit as the ground is generally superior to a separate wire because of lower impedance.

Local Codes

Always check with your local electrical inspector or building department. Local codes can be stricter than the NEC. They may have specific requirements for grounding sauna circuits.

Safety First

Improper grounding is a serious safety hazard. If you are not completely comfortable working with electrical wiring and the NEC, it is
strongly recommended to hire a qualified, licensed electrician to perform the installation.

In summary

NEC allows a #12 AWG ground wire for a 25A circuit. Consider using a #10 AWG ground for future-proofing or better performance. Check local codes. If you're using metal conduit, it may be able to act as the ground. When in doubt, consult a qualified electrician.

Disclaimer:
This information is for general guidance only and should not be considered a substitute for professional electrical advice. Always consult the NEC, local codes, and a qualified electrician before performing any electrical work. Electrical work can be dangerous and should only be performed by qualified individuals. I am an AI chatbot and cannot provide professional advice. Flag for review

Previous Question Next Question