User: Gunnar, Location: Santa Rosa, CA
Asked on: Thursday, October 9, 2025 at 1:12 pm EDT
Answered on: Thursday, October 9, 2025 at 1:22 pm EDT
Question: Hi folks,I recently was at an older home where the electrical serivce had been moved from its original overhead location on the left side of the house to an underground service at the right side. In this case, a new service equipment with a single main disconnect was placed at the right side and fed to a new panel that replaced the original service equipment at the left side. A new ground rod was driven near the new service and bonded to the original ground rod near the replacement (sub) panel with a #6 conductor. The distance between the two rods got me to thinking (dangerous, I know).NEC 250.53 (A)(3) in general requires two rods placed a minimum of 6 feet apart and the Informational Note says that twice the distance of the longest rod is better (but not required). I cannot find a maximum limit in distance for the two rods and began wondering if there would be some kind of issue given the length of the #6 conductor and the potential resistance that would occur over that (estimated) 80+ foot distance? I realize that this should not normally carry any voltage/current, but in the (unlikely) event of a lightning strike, would that contribute to failure of the conductor? What if that distance were greater, like 200 feet?This is essentially a four-part question:1) Does anyone know of a maximum distance for the two rods (electrodes, whatever)?2) The IN talks about the increase in "paralleling efficiency". Would that efficiency drop if the rods were placed even farther apart? (I wouldn't think so, but...)2) Should that #6 conductor have been increased to #4 (or greater) to address potential distance/resistance/voltage drop?3) Am I overthinking this and should I just go read a good book?Thanks
You're asking excellent questions that touch upon some often-misunderstood aspects of grounding electrode systems! Let's break down your four-part inquiry
1) Does anyone know of a maximum distance for the two rods (electrodes, whatever)?
No, there is no maximum distance specified in the NEC between ground rods used for grounding electrodes. The NEC focuses on the minimum separation of 6 feet. The thinking is that you want them far enough apart to be in different areas of the soil and thus more likely to encounter different soil resistances, which increases the chance of a lower overall ground resistance.2) The IN talks about the increase in "paralleling efficiency". Would that efficiency drop if the rods were placed even farther apart? (I wouldn't think so, but...) Correct, efficiency likely wouldn't drop by increasing the distance. The "paralleling efficiency" refers to how well the two electrodes act together to lower the overall ground resistance. As you increase the distance between the rods, you're less likely to be within the "sphere of influence" of the other rod. Think of it like overlapping circles – if they don't overlap at all, each is acting independently, and combining their effect is more efficient. However, this isn't a linear relationship where more distance always equals more efficiency. Soil conditions are the primary factor. At a certain point, increasing distance provides diminishing returns.3) Should that #6 conductor have been increased to #4 (or greater) to address potential distance/resistance/voltage drop? No, increasing the conductor size to address distance/resistance/voltage drop is likely unnecessary and not the primary concern here. Here's why: Grounding Conductors vs. Circuit Conductors
Grounding conductors are not intended to carry continuous current under normal conditions. They only carry fault current during a short circuit or ground fault, or a rare lightning strike. So, voltage drop calculations, which are relevant for conductors carrying sustained loads, don't really apply here.
Lightning Considerations
While lightning is a valid concern, a #6 copper conductor is generally considered adequate for bonding ground rods. Lightning currents are huge and create massive voltage gradients in the soil. No realistically sized conductor will "prevent" damage from a direct or even nearby strike. The goal is to provide a low-impedance path to ground to help dissipate the energy and minimize the risk of equipment damage and electric shock.
NEC Table 250.66: The grounding electrode conductor is required to be sized per Table 250.66. Note 1 further explains that it does not need to be larger than #6 copper if connected to a rod, pipe, or plate electrode.4) Am I overthinking this and should I just go read a good book? You're not overthinking it. You're engaging in critical thinking about electrical safety, which is commendable! However, in this specific scenario, given the NEC requirements and the realities of grounding practices, your concerns are not likely to be significant in practical terms.
Addressing your Lightning Concern More Directly
Lightning is a complex phenomenon. Here's what you should consider:
The Grounding System is Primarily for Fault Current, Not Lightning
While a good grounding system helps with lightning protection, it's not a dedicated lightning protection system. Those systems involve air terminals (lightning rods), heavy conductors, and specific grounding methods.
Soil Resistance is Key
Soil resistance is a much bigger factor than the resistance of the #6 conductor. Dry, rocky soil will have a high resistance, limiting the effectiveness of any grounding system, regardless of conductor size.
Bonding is Essential
Make sure all metallic components (gas pipes, water pipes, metal building structures) are properly bonded to the grounding system. This helps equalize potential and minimize the risk of side flashes during a lightning strike.
In summary: You're right to be curious, but the #6 conductor between the ground rods is likely adequate in this situation. Focusing on proper bonding throughout the electrical system and considering the soil conditions will provide more benefit than simply upsizing that conductor. Flag for review