Question: I have a customer who bought a used 3 phase motor and the motor conductors aren’t labeled, nor connected to anything. Some seem to be somewhat paired up with others but nothing clearly obvious or for certain.It’s a 12 wire motor and the high voltage is like the high voltage delta diagram in the bottom left corner of the link below.https://control.com/uploads/articles/Poster_3Phase_Motor_Wiring.png
Okay, dealing with unmarked 12-lead motors can be tricky, but with a systematic approach, you can figure it out. Here's a breakdown of how to identify and connect the windings for high-voltage delta operation, along with important safety precautions
Safety First!
1. Disconnect Everything
Before you even think about touching those wires, ensure the motor is completely disconnected from any power source. Lock out/tag out procedures are essential.2.
Verify No Voltage
Double-check with a reliable voltage meter that there's no residual voltage present.3.
Insulated Tools
Use insulated tools for all work.4.
Ground
Make sure the motor frame is properly grounded.5.
Qualified Personnel
If you're not 100% comfortable with this process,
hire a qualified electrician. This is not a beginner project. Improper wiring can damage the motor, create a safety hazard, or both.
Understanding the 12-Lead High-Voltage Delta Configuration
The diagram you linked to illustrates the high-voltage delta connection. The key concept is that each phase of the three-phase power source is connected across two windings in series. This allows the motor to be connected to a higher voltage supply. The key is to understand which leads belong to which winding.
Identifying the Windings
This is the most critical and time-consuming part. You'll need an ohmmeter (multimeter set to measure resistance).1. Label Everything
Use numbered wire markers to label each of the 12 wires. This is absolutely essential to keep track of things. Label them 1 through 12.2.
Measure Resistance
Take resistance readings between every possible pair of wires (1 and 2, 1 and 3, 1 and 4... all the way to 11 and 12). Record every reading. A table or spreadsheet will be helpful.
Important
Look for pairs of wires that show a low and consistent resistance. This low resistance indicates that these two wires belong to the same winding. Typical resistance values for motor windings will be a few ohms or less, but this can vary based on motor size and construction. If a pair of wires are open (infinite resistance), they are not part of the same winding.3.
Pairing Strategy
Typically windings are paired together and close in proximity. Meaning, 1 may be paired with 2, 3 with 4 and so forth. However, this is not always the case. You may be paired to 12. The reason to test every wire to every other wire is to get an accurate assessment of each potential pairing.
4.
Document Your Findings
Create a table or list showing the wire pairs you've identified and their resistance values.5.
Confirmation and Troubleshooting You should end up with 6 pairs. Each pair of leads will represent one end and the opposite end of a coil. If any of the resistances are zero or higher than expected, there's probably a short or open circuit in the winding. This is not something you can fix without specialized motor repair equipment and skills.
Connecting for High-Voltage Delta
Once you've identified the winding pairs, follow this diagram closely.1. Reference the Diagram
Refer to the bottom left delta diagram in the link you provided.2.
Wire Connections
Make the following connections based on your identified winding pairs (replace W1, W2, etc., with your actual wire numbers):
T1
Connect leads that are one side of the coil from leads (1 & 6)
T2
Connect leads that are one side of the coil from leads (2 & 4)
T3
Connect leads that are one side of the coil from leads (3 & 5) Connect the other ends of the coils, pairs (7 & 12), (8 & 10), (9 & 11) together.3.
Double-Check
Before applying power, carefully double-check all connections against the diagram. Any mistake here could damage the motor.
Testing (Use Caution!)1. No Load
Before connecting the motor to its intended load, test it with no load.2.
Voltage and Current Monitoring
Use a multimeter to monitor the voltage and current on each phase as you start the motor. The voltage should be close to your supply voltage, and the current should be relatively low (the motor's nameplate will give you an idea of the expected no-load current).3.
Listen and Observe
Listen for any unusual noises (humming, grinding, etc.) and watch for excessive vibration. If anything seems wrong, immediately disconnect the power and re-check your wiring.4.
Rotation
If the motor runs smoothly but in the wrong direction, swap any two of the three incoming power leads to reverse the rotation.
Important Considerations
Motor Nameplate
The motor nameplate is your best friend. It will tell you the voltage, amperage, horsepower, and other critical information.
Service Factor
Check the motor's service factor. This indicates how much overload the motor can handle safely.
Insulation Resistance
If you have a megohmmeter (megger), check the insulation resistance between the windings and the motor frame. Low insulation resistance indicates moisture or contamination in the windings, which can lead to failure.
Thermal Overloads
Always use correctly sized thermal overload protection for the motor to prevent damage from overcurrent. This is crucial for any motor installation.
Disclaimer: Working with electrical equipment can be dangerous. I cannot provide electrical advice for your project as I don't know all of the parameters of the installation and don't have any control or understanding over your skill level. Always consult with a qualified electrician for any electrical work. Flag for review