Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 310.15(b)(1)(1) vs 310.15(b)(1)(2)

User: Ponchik, Location: CA

Asked on: Friday, October 10, 2025 at 1:09 am EDT
Answered on: Friday, October 10, 2025 at 1:09 am EDT

Question: Besides one is for 86F and one is 104F what is the difference between the two tables? 310.15(b)(1)(1) vs 310.15(b)(1)(2)?I have always used the 86F table. When is the 104F table used?TIA

Let's break down the difference between NEC tables 310.15(B)(1)(1) and 310.15(B)(1)(2) and clarify when to use each

Key Difference: Ambient Temperature & Application
310.15(B)(1)(1): Ambient Temperature Correction Factors Based on 30°C (86°F) - This is the more common and broadly applicable table. It's used for conductors installed in typical ambient temperature environments (around 30°C or 86°F). This table is for ambient temperatures up to 86°F. 310.15(B)(1)(2): Ambient Temperature Correction Factors Based on 40°C (104°F) - This table is used specifically for conductors installed in high ambient temperature environments (around 40°C or 104°F). This table is for ambient temperatures up to 104°F.

When to Use Each Table1. Determine Ambient Temperature

The first step is to determine the ambient temperature in the area where your conductors will be installed. This is the air temperature surrounding the conductors after the installation. This is not the temperature of the conductors themselves, it is the ambient.2.

Compare to Table Base Temperatures



If the ambient temperature is at or below 86°F (30°C)

Use the correction factors from

310.15(B)(1)(1)
. If the ambient temperature is above 86°F (30°C) but at or below 104°F (40°C)

Use the correction factors from

310.15(B)(1)(2)
.3. High Ambient Environments

Table 310.15(B)(1)(2) is typically used in these situations:

Conduit exposed to direct sunlight

Sunlight can significantly increase the temperature inside a conduit, especially on rooftops.


Areas with poor ventilation and high heat-generating equipment

Think factories, industrial settings, and some commercial kitchens.

Certain geographical locations

Hot climates with consistently high ambient temperatures (e.g., desert regions).

Why the Difference Matters


Conductor ampacity (current-carrying capacity) is derated (reduced) as ambient temperature increases. Higher temperatures increase the resistance of the conductor and lead to more heat generation. To prevent overheating and potential insulation damage (or even fire), you
must apply the correct ambient temperature correction factors. Using the wrong table (especially using the 86°F table when the ambient is much higher) can lead to an undersized conductor, which is a serious safety hazard.

Important Considerations
Ambient Temperature vs. Conductor Temperature

Remember, ambient temperature is the air temperature around the conductor. Conductor temperature is the temperature of the conductor itself while carrying current. These are different. Ampacity tables and correction factors address ambient temperature. Conductor temperature limits are often specified in the conductor's insulation rating (e.g., THHN is rated for 90°C).

Grouping of Conductors

Ambient temperature correction is separate from derating due to the number of current-carrying conductors in a raceway or cable (refer to 310.15(C)). You need to apply
both corrections if applicable.

Qualified Person

Determining the correct ambient temperature and applying ampacity derating correctly are crucial parts of electrical design. Consult with a qualified electrician or electrical engineer for complex installations or if you are unsure about any part of the process.

In summary, you've likely been using the 86°F table because you've been working on installations where the ambient temperature is typically at or below 86°F. The 104°F table is for environments where the ambient temperature is consistently higher and approaches or exceeds 86°F (but is at or below 104°F). Always determine the actual ambient temperature before selecting the appropriate correction factor table.
Flag for review

Previous Question Next Question