Topic: Reforming Capacitors on VFDs after Storage

User: Saturn_Europa, Location: Fishing Industry

Asked on: Friday, October 10, 2025 at 7:36 am EDT
Answered on: Friday, October 10, 2025 at 7:37 am EDT

Question: The plant I work at, had a 200 HP VFD Powerflex 750 make a loud bang then trip a 400 amp breaker. I replaced the VFD with one we had in storage. Not sure how long it has been on the shelf but at least 3 years. I searched through the manual and did not see anything about reforming the capacitors, so I decided to apply power (480v) and wait a few hours before applying a load. This is the method listed for the Automation Direct VFDs we normally use.I did some more searching and found this Allen Bradley service bulletin:Table 3 - Drive Storage Duration and Reforming Recommendations.Duration Reforming GuidelineUnder 2 years No reforming required.2 …3 years Apply rated voltage, per the normal method, for 30 minutes under no load.Over 3 years Using a DC power supply connected directly to the DC terminals of the product, ramp-up the voltage from 0…100% of DC bus voltage (as per Table 4) in increments of 50%, 75%, and 100% rated voltage, under no load, for 30 minutes at each increment. See Figure 5 on page 4 for an illustration of this methodDoes anyone actually use the last method? I dont have this type of equipment and would have to hire someone to reform the caps.This drive costs over $21k. Does not reforming the capacitors properly effect the longevity of the VFD? Or is it only a danger of capacitor failure on startup?

You're right to be concerned and to question the best course of action. Let's break down the situation and potential consequences

Understanding Capacitor Reforming:
Electrolytic Capacitors and Storage

Electrolytic capacitors (the kind used in VFDs) have a liquid electrolyte inside. Over time, especially when not energized, this electrolyte can dry out or degrade. This increases the Equivalent Series Resistance (ESR) of the capacitor.


Reforming Process

Reforming is the process of gradually re-establishing the dielectric layer within the capacitor. Applying voltage slowly allows the dielectric to reform without excessive heat or damage.

Why it Matters

If you apply full voltage to a degraded capacitor, it can overheat rapidly due to the high ESR. This can lead to:


Catastrophic Failure

The capacitor can explode or rupture, potentially damaging other components in the VFD. This is the "loud bang" you experienced in your original VFD failure (though the cause of that failure is unknown)

Reduced Lifespan

Even if the capacitor doesn't fail immediately, its lifespan is likely to be significantly shortened.


Performance Issues

Degraded capacitors can lead to voltage ripple on the DC bus, which can affect the VFD's performance and potentially damage the motor.

Analyzing Your Situation



Storage Time

Your drive has been in storage for at least 3 years, placing it firmly in the "Over 3 years" category according to the Allen-Bradley service bulletin.


Cost of the Drive

At $21k, the risk of damaging the drive is significant.

Your Attempted Method

Simply applying 480V for a few hours, as you do with the Automation Direct VFDs, is
not the recommended procedure for PowerFlex 750 drives stored for this length of time. You could be causing damage.

Should You Use the DC Ramp-Up Method?
Ideally, Yes

The DC ramp-up method is the safest and most thorough way to reform the capacitors according to Allen-Bradley. It minimizes the stress on the capacitors during the process.

Practically, Consider the Cost/Benefit

The cost of hiring someone to perform the DC ramp-up is a factor. Get a quote. It might be less than you think, and far less than replacing a $21k VFD.


Alternatives (With Caveats)

If hiring someone is truly not an option, consider a modified approach with the understanding that you are taking a calculated risk:

Very Slow AC Ramp-Up (With Monitoring)

Instead of full 480V, use a Variac (variable autotransformer) to slowly increase the AC voltage feeding the VFD. Start at a very low voltage (e.g., 25% of rated), let it sit for 30 minutes, then slowly increase in steps. Monitor the VFD's internal temperature (if possible) and the AC current draw. If the current spikes or the temperature rises rapidly, stop and let it cool down. You are looking for excessive inrush current which would indicate the capacitors are failing.


Limited Exposure

Only run the drive off the motor long enough to test it and make sure it runs the motor properly.

Important Considerations



Warranty

Applying power without properly reforming the capacitors could void the VFD's warranty (if it still has one). Contact Allen-Bradley to confirm.


Root Cause of Original Failure

What caused the original VFD to fail so spectacularly? Was it a line surge, motor issue, or component failure? Addressing the root cause is crucial to prevent another failure.*

Preventive Maintenance

Implement a preventive maintenance program that includes capacitor reforming for stored VFDs to avoid this issue in the future.

Recommendation

1.

Contact Allen-Bradley

Discuss the situation with an Allen-Bradley service technician. They can provide more specific advice based on the VFD's serial number and history. They may also be able to recommend a local service provider who can perform the DC ramp-up.2.

Get a Quote

Obtain a quote for professional capacitor reforming.3.

Weigh the Risks

Based on the cost of reforming, the cost of the VFD, and the potential consequences of failure, make an informed decision.4.

If proceeding on your own

Very slow voltage ramp up and monitoring of the drive. Limit exposure of the drive to the motor until you are sure it is working.

In summary, while the DC ramp-up method might seem inconvenient, it's the recommended approach for a high-value VFD that has been in storage for an extended period. Ignoring this recommendation could lead to a costly and potentially dangerous failure.