User: journeyman0217, Location: Tennessee
Asked on: Friday, October 10, 2025 at 9:36 am EDT
Answered on: Friday, October 10, 2025 at 9:37 am EDT
Question: I was reading some past threads and I'm still not clear on how to size wire for a 400 amp sub panel. 500 kcmil is good for 380amps at 75 degrees. Can I use the next standard size breaker, in this case 400 amp, to protect these conductors as long as the connected load is less than 380 amps? And if the connected load is greater than 380 amps does the next size up rule still apply?
Okay, let's break down wire sizing for a 400 amp subpanel and address your specific questions regarding the 500 kcmil wire and the "next size up" rule.
Understanding the Basics Ampacity
This is the maximum current, in amperes, that a conductor can carry continuously under specific conditions of use without exceeding its temperature rating. Ampacity is affected by wire size, insulation type, ambient temperature, and the number of current-carrying conductors in a raceway or cable.
Overcurrent Protection (Breaker/Fuse)
The overcurrent protection device is there to protect the conductor from overheating and potential fire hazard due to excessive current flow, regardless of the load. It is not primarily there to protect the load (although it does offer some protection).
Continuous Load
A load is considered continuous if it operates for 3 hours or more at a time. NEC requires circuits feeding continuous loads to be rated for at least 125% of the continuous load.
Addressing Your Specific Questions1. "500 kcmil is good for 380 amps at 75 degrees. Can I use the next standard size breaker, in this case 400 amp, to protect these conductors as long as the connected load is less than 380 amps?" No, you cannot typically use a 400 amp breaker in this scenario under the general rules of the NEC. While your load might be less than 380 amps, the fundamental principle is that the breaker must protect the conductor. NEC Section 240.4(B) addresses the next size up rule. However, that rule comes into play only after you've determined that the conductor's ampacity (380 amps in your example) doesn't exactly match a standard breaker size. Section 240.4(B) allows you to "round up" to the next standard breaker size if your conductor ampacity falls between two standard sizes. However, the exceptions 240.4(B)(1) and 240.4(B)(2) usually won't apply. Those apply to specific applications like motor circuits, and your case is a subpanel feed. Therefore you would need to use an overcurrent protection device no more than 380amps, so something like a 350amp breaker.2. "And if the connected load is greater than 380 amps does the next size up rule still apply?" Absolutely not. If your connected load is greater than the ampacity of your conductor (380 amps in your example), and you use a breaker larger than 380 amps, you are violating the fundamental principle of overcurrent protection. You are allowing the conductor to potentially carry more current than it is rated for. This is a dangerous situation and a code violation. You would need to increase the conductor size to match the load.
Key Considerations and Code Requirements NEC 310.16 Ampacities
This table is the starting point for determining conductor ampacity. You must use the correct column based on the temperature rating of your terminations (usually 75°C for most equipment). Remember to adjust for ambient temperature and the number of current-carrying conductors in a raceway or cable using the correction factors provided in the tables.
Termination Temperature
Most electrical equipment is rated for either 60°C or 75°C terminations. You must use the ampacity column corresponding to the lowest rated termination on the circuit (either at the breaker or at the panel). Using the 90°C column without 90°C rated terminations is a violation of NEC 110.14(C).
Ambient Temperature Correction
If the ambient temperature is higher than the temperature listed at the top of the ampacity table (typically 30°C or 86°F), you must apply a correction factor to reduce the conductor's ampacity.
Number of Conductors in a Raceway or Cable
If you have more than three current-carrying conductors in a raceway or cable, you must apply an adjustment factor to reduce the conductor's ampacity. This is to account for the increased heat generated by multiple conductors in close proximity.
125% Rule for Continuous Loads
If you have a continuous load (operates for 3 hours or more), you must size the conductors and overcurrent protection device to at least 125% of the continuous load. For example, if you have a 300 amp continuous load, you would need conductors rated for at least 300 x 1.25 = 375 amps and a breaker sized accordingly.
Voltage Drop
While not a safety issue, excessive voltage drop can cause equipment malfunction and inefficiency. NEC recommends limiting voltage drop to 3% for feeders and 5% overall (feeder + branch circuit). For long runs, you may need to increase conductor size to minimize voltage drop.
Local Codes and AHJ
Always check with your local electrical inspector (AHJ - Authority Having Jurisdiction) for any specific requirements or interpretations of the NEC.
Example Scenario
Let's say you have a 400 amp subpanel with the following: Load
350 amps (non-continuous)
Terminations
Rated for 75°C
Conductors
THHN copper, 3 in a conduit*
Ambient Temperature
30°C1.
Determine the minimum conductor ampacity
350 amps2.
Consult NEC Table 310.16 (75°C column)
You would need at least 500kcmil conductors rated for 380 amps.3.
Overcurrent Protection
You would need to use a 350 amp breaker to protect the conductors.
In summary, you cannot typically use the next size up rule to use a 400amp breaker on 500kcmil conductors carrying a load of 380 amps or less. Breakers and conductors need to be sized to what the conductor ampacity is. Flag for review