Question: Friends,I have a PF525 VFD 1HP 480V drive. At the last minute they changed the motor to a break-motor.I have 480V in the VFD cabinet obviously, but I have no control voltage. no 120 or 24V at all. And no space to add a XFMR./PSU.I need to operate a brake contactor for the EM brake from the PF525. The PF525 onboard 24V+ is only good for like 100ma or so.We could use either the Opto-outputs (50ma max) or the R1 relay output. But I would need a 2-pole contacvtor with a coil consumpsion less then 100ma..Any ideas on how to get out of this corner i have been painted into.
Okay, this is a tricky situation, but we can brainstorm some solutions to control your brake motor with limited resources. Here are a few ideas, ranging from the most likely to work to the more creative (and potentially riskier)
1. Relay Logic Enhancement (Most Likely Solution):
The Problem
You need to control a brake contactor that draws more than the PF525's outputs can handle.
The Solution
Use a small interposing relay (or relays) to amplify the signal.
How it works
1. Use the PF525's Opto-output (50mA max) or Relay output (R1) to energize the coil of a very small, low-current 24VDC or 24VAC relay. Find one with a coil current draw significantly less than 50mA (for opto) or whatever the R1 relay allows. Look for a relay designed for signal-level switching, not power switching. Something you might find on a PCB.2. Use the contacts of that small interposing relay to switch a 480VAC circuit, which will operate the coil of your brake contactor.
Component Selection
Interposing Relay
Find a small DIN rail mountable relay with a coil voltage of 24VDC or 24VAC, and a contact rating sufficient to handle the inrush current of the brake contactor coil. Crucially, the coil current draw needs to be within the limits of your PF525 output. Look for solid-state relays as they are very low current draw.
Brake Contactor
You mentioned needing a 2-pole contactor. Carefully check the inrush and holding current requirements of the brake contactor's coil. The voltage must be 480VAC. Search for mini-contactors, as they are physically smaller and tend to have lower coil current requirements. The 2-pole requirement might limit your choices; a standard 3-pole contactor might be necessary, with one unused pole.
Wiring
1. Wire the PF525 Opto-output or R1 relay output to the coil of the interposing relay. Configure the PF525's parameters to activate the output when the motor should not be braking (i.e., when the motor is running). This is usually when the drive is enabled or at speed. You'll likely want to configure the drive output to activate before the drive starts outputting voltage and deactivate after the drive stops outputting voltage to the motor to ensure the brake releases and engages properly.2. Run 480VAC to a normally open (NO) contact of the interposing relay.
3. Wire the other side of that NO contact to the brake contactor's coil.4. Wire the other side of the brake contactor's coil back to the other 480VAC phase.
Important Considerations
Safety
This method involves working with 480VAC. Ensure all wiring is done by qualified personnel, in accordance with local electrical codes, and with proper safety precautions (lockout/tagout).
Proper Enclosure
Mount the interposing relay and any associated wiring in a suitable enclosure to protect it from the environment and prevent accidental contact. Even though it's low voltage, it's controlling 480V.
Drive Programming
The timing of the output activation/deactivation is critical for proper brake operation. Experiment with the drive's configurable delays to optimize the brake release and engagement sequence.
Reliability
Interposing relays add a point of failure. Choose a high-quality relay from a reputable manufacturer.
2. Solid-State Relay (SSR) - A Simpler Variation of #1
How it works
Use a low-current DC signal from the PF525's opto-output to switch a solid-state relay (SSR) that can handle the 480VAC needed for the brake contactor.
Component Selection
SSR
Select an SSR with a DC control voltage (matching the PF525's opto-output voltage, likely 24VDC), an AC output voltage rating of 480VAC or higher, and a current rating sufficient to handle the inrush current of the brake contactor coil (at least 2-3x the steady-state current). Critically, choose one with a low input current (within the PF525's opto-output limit).
Brake Contactor
As above, select a 480VAC brake contactor with the lowest possible coil current draw, ideally with a two-pole configuration.
Wiring
1. Connect the PF525's opto-output to the DC control input of the SSR.
2. Connect the 480VAC power to the input side of the SSR.3. Connect the output of the SSR to the brake contactor coil.
4. Connect the other side of the brake contactor coil back to the other 480VAC phase.
Advantages
Simpler wiring than using multiple electromechanical relays.
Disadvantages
SSRs can generate heat, especially when switching inductive loads (like a contactor coil). Ensure adequate heatsinking is provided if necessary.
3. Miniature Contactor with Low Current Coil (Check Carefully)
How it works
Find a very small contactor with a 480VAC coil that draws less than 50mA (for opto) or whatever the R1 relay allows. This is a long shot, as most 480VAC contactors have significantly higher coil current.
Component Selection
Miniature Contactor
This is the key. Extensive searching will be required. Look at contactors used in lighting control panels or very small motor starters. Consider contacting contactor manufacturers directly and explaining your requirements. Be prepared for a negative answer. You might have better luck finding a 24VDC or 120VAC mini-contactor and using one of the earlier solutions to power it.
Wiring
If you find a suitable contactor, wire the PF525's opto-output or R1 relay output directly to the contactor coil.
Advantages
Simplest wiring if you can find the right component.
Disadvantages
Finding a suitable contactor is extremely unlikely.
4. "Borrow" Power (Use with Extreme Caution and Qualification)
Warning
This is the riskiest option. It requires careful planning, deep understanding of electrical codes, and may not be permissible in all situations.
Consult a qualified electrician and engineer before attempting this. The Idea
If there's any other piece of equipment in the cabinet or very nearby that already has a 120VAC or 24VDC control power supply, carefully evaluate if you can tap into it to power a small interposing relay.
Conditions for Considering This
The existing power supply must have sufficient spare capacity (after considering the current draw of everything it already powers) to handle the additional load of the relay coil. Overloading the existing supply can lead to voltage drops, malfunctions, and potentially dangerous situations. The existing power supply must be properly protected with overcurrent protection (fuses or circuit breakers) of the appropriate rating. You may need to add additional fusing. The wiring must be done in accordance with all applicable electrical codes. You must have the permission of the equipment owner and/or manufacturer to modify the wiring.
How it would work
1. Identify a suitable source of 120VAC or 24VDC.
2. Calculate the available current capacity.3. Select an interposing relay with a coil voltage matching the available power and a coil current draw that is well within the available capacity.
4. Wire the relay coil to the available power supply (with appropriate fusing).5. Use the relay contacts to switch the 480VAC to the brake contactor coil (as in Solution #1).
Why it's risky
You're modifying an existing electrical system, which can have unintended consequences. If done incorrectly, it could create safety hazards, violate warranties, or damage equipment. It may also violate UL or other safety listings.
In Summary
Start with
Solution #1 (Relay Logic Enhancement) or Solution #2 (SSR). They are the most likely to be safe, reliable, and within the capabilities of your PF525 drive. Thoroughly research the available components and ensure your wiring is done correctly.Approach Solution #4 (Borrowing Power) only as a last resort, and only with the guidance of a qualified professional.Avoid relying on Solution #3 (miniature contactor with low current coil) unless you have already found a suitable part and can verify its specifications.Remember safety first. Good luck! Flag for review