Question: I have a question on a practice exam and have not been able to grasp it.The disconnecting means for a 50 HP, three-phase, 460 V induction motor shall have a minimum ampere rating of ?1/ 60amps2/ 100 amps3/ 125 ampsSo im in the 2023 nec I go to table 430.250 find my FLC of 65 amps65amps X 1.15=74.75for some reason be it a brain crap or what I cant seem to the answer they want of 100 ampstable 430.52 does my no good. I feel like im just missing something silly and will kick myself in the arse for it. The induction part appears to my to be the thing im messing up.thanks for any help or assistance

You're on the right track! Here's where you're getting mixed up: You're calculating the motor branch circuit short-circuit and ground-fault protection (fuse or circuit breaker) size, not the disconnect switch rating. The 1.15 you're multiplying by is used to determine the size of the overcurrent protection (short-circuit and ground-fault protection).

The Disconnect Switch
Disconnect switch rating

The disconnect switch only has to be rated at least 115% of the motors Full load Current (FLC).

Here's the breakdown and the answer


FLC

As you correctly identified, from Table 430.250, a 50 HP, three-phase, 460 V induction motor has an FLC of 65 amps.
2.


Disconnect Rating (NEC 430.110(A))

The disconnecting means must have an ampacity of at least 115% of the motor's FLC.3.

Calculation

65 amps 1.15 = 74.75 amps4.

The minimum size
of the disconnect needs to be at least 74.75 amps.
5. Standard Breaker/Switch Sizes

Breaker and switch sizes aren't made in every single amp value. You have to choose the
next standard size up. While 75A would technically work, the NEC often expects you to use standard sizes for practical reasons. The next standard size above 74.75A is 100A.

Therefore, the answer is 2/ 100 amps
Key Takeaway Disconnect Switch Size vs. Overcurrent Protection

The disconnect switch size is different from the motor branch circuit overcurrent protection (fuse or circuit breaker). Don't confuse the calculations.


Standard Sizes:
Remember to choose the next standard size up when the calculation results in a non-standard size.I hope this helps! Let me know if you have any more questions. Flag for review