Question: Never came across this many, and this size, conduits landing in a xfrmr. Is it even possible(Obviously I assume)? Do they make 5" FMC? Thanks
You're right to question that! It's quite a sight to see that many large conduits landing in a transformer, and yes, it's possible, though not always ideal and requires careful planning. Let's break down the potential issues and how it might be done.
Is it Possible? Yes, with conditions. Transformer Size and Enclosure
The most critical factor is the physical size of the transformer enclosure and its available landing space. Transformers are built with enclosures designed to accommodate terminations, but there's a limit. You need enough room to make the connections safely and comply with bending radii requirements.
Termination Space
The enclosure must be large enough to accommodate the number and size of conductors coming from all those conduits. Overcrowding can lead to overheating, difficulty in maintenance, and code violations.
Code Compliance (NEC or Local)
The National Electrical Code (NEC) and any local codes will have specific requirements for conductor fill in enclosures, bending radii of conductors, and accessibility for maintenance. This installation must comply with these.
Conduit Fill
Each conduit has a maximum conductor fill percentage. You need to calculate if the conductors for your circuit can fit safely in that conduit.
Heat Dissipation
A large number of conduits could potentially restrict airflow around the transformer, affecting heat dissipation.
Addressing Your Specific Questions
Do they make 5" FMC? No. FMC (Flexible Metal Conduit) maxes out at 4", and is generally not used in this kind of installation. You would more likely use liquid-tight flexible metal conduit (LFMC), EMT (Electrical Metallic Tubing), or Rigid Metal Conduit (RMC) for these large sizes.
Likely Scenarios and Solutions for This Many Large Conduits
Multiple Transformers
The most likely scenario is that this is not a single transformer but rather a bank of transformers. Perhaps three single-phase transformers wired to create a three-phase system. This would allow for more physical space to accommodate the terminations.2.
Dedicated Termination Cabinet or Pull Box
An alternative, especially if space within the transformer enclosure is limited, is to use a separate, large junction or pull box adjacent to the transformer. The conduits would terminate in the box, and then shorter, larger-gauge conductors would connect to the transformer terminals.3.
Bus Duct or Bus Bar System
Instead of individual conductors in conduits, a bus duct or bus bar system might be used for the main feeder connections. This is common for high-current applications, as it can handle more current in a smaller space than individual conductors. Bus duct would still need a transition to the transformer, but it might reduce the number of conduits.4.
Parallel Conductors
The large number of conduits could indicate that parallel conductors are being used for each phase. This is done when a single conductor cannot handle the required current. If parallel conductors are used, they MUST be sized, installed, and terminated per NEC guidelines.
Things to Consider and Investigate
Purpose of Each Conduit
You need to understand the purpose of each conduit. Is it feeding power to the transformer, or is it for secondary connections feeding loads? Knowing the load requirements will help determine the conductor sizes and conduit fill.
Conductor Sizes and Types
Determine the size and type of conductors being used in each conduit (e.g., THHN, XHHW). This is crucial for calculating ampacity and conduit fill.
Amperage of the Transformer and Loads
Knowing the transformer's KVA or amperage rating is essential, as well as the loads being served by the transformer.
Existing Documentation
Look for any existing electrical drawings, specifications, or load calculations for the installation. This documentation can provide valuable information about the design and intended purpose.
Important Safety Considerations
De-energize and Lockout/Tagout
Never work on energized equipment. Always de-energize the transformer and follow proper lockout/tagout procedures.
Qualified Electrician
This type of installation requires a qualified and experienced electrician familiar with high-voltage systems and the NEC.
Arc Flash Hazard: Large transformers can pose a significant arc flash hazard. Be sure to wear appropriate PPE (Personal Protective Equipment) and follow safe work practices.In summary, while it is* possible to have that many conduits landing on or near a transformer, it's critical to ensure code compliance, adequate space, proper termination techniques, and safe work practices. Detailed calculations and planning are essential. Investigate the factors mentioned above to determine if the installation is safe and code-compliant. Consult a qualified electrical engineer if you have any doubts. Flag for review