Question: Consensus seems to be isolated ground receptacles are obsolete, only to be done if the job specs require it. I was reading through 250.146D. I only see where it is permitted to be ran or spliced (or not), not where it is required to be landed. In an old EC&M article, Mike says it is permitted to be landed to the box immediately with the device. https://www.ecmweb.com/content/article/20890911/the-basics-of-isolated-grounding-receptacles. Can someone direct me to the Code article that might clarify the required termination point?
You've hit on a key point: the NEC permits isolated grounding (IG) receptacles, but it doesn't require them, and their use is increasingly discouraged. Your understanding is accurate.Here's a breakdown of the code and reasoning: NEC 250.146(D) doesn't require a specific termination point. It only deals with the conditions under which an isolated equipment grounding conductor (IEGC) is permitted to run and not be spliced. It's about how to maintain the isolation of the ground path, not where it ultimately connects. The ultimate termination is always back at the service equipment (or derived separately derived system). The purpose of an isolated ground is to provide a low-noise ground reference, and this is only effective if it ties back directly to the source of the grounding system without picking up noise along the way from other equipment bonded to the raceway/enclosure. Why Isolated Grounds are Less Common Now
Modern electrical systems, with proper bonding and grounding practices, often provide a sufficient level of noise reduction, making IG receptacles less necessary. Also, using proper surge protection, filtering, and good wiring practices can often mitigate the need for an IG.
Landing to the Box (as Mike Holt mentions)
Mike Holt's article correctly reflects that if you are using an IG receptacle, you can land the isolated ground conductor directly to the receptacle's ground terminal within the box. However, this doesn't mean it must be done there; it simply confirms that it can be done there, so long as that isolated ground conductor continues back to the service equipment without being connected to the metal conduit/box along the way. It does not change the fact that you still have to run the normal EGC with the circuit as well.
Where the Confusion Arises
The confusion often comes from the fact that older systems sometimes had an IG conductor that was only connected to the receptacle in the box, and then tied to the enclosure.
This is incorrect and not compliant with code. An IEGC must run all the way back to the service equipment or separately derived system.
In summary
NEC doesn't require IG receptacles.2. If you do use an IG receptacle, NEC 250.146(D) describes how to run the IEGC to maintain its isolation.3. The IEGC must ultimately terminate at the service equipment (or separately derived system).4. Landing the IEGC directly at the receptacle is permitted, as long as the isolation is maintained all the way back to the source.5. Modern electrical practices often reduce the need for IG receptacles.Important Considerations
Job Specifications
You are correct that if the job specs require IG receptacles, you must follow them.
AHJ Approval
Always consult with the local Authority Having Jurisdiction (AHJ) for clarification or approval, especially when deviating from standard practices.
Engineering Design
The decision to use IG receptacles should ideally be based on a proper engineering design that considers the specific equipment sensitivity and potential noise issues.
Why it's rarely "required" now:
The effectiveness of isolated grounds depends heavily on proper installation and the overall grounding and bonding system. Modern equipment is often designed to be less susceptible to noise, and good grounding/bonding practices can often provide adequate noise reduction. Thus, it's less frequently necessary to specify IG receptacles unless there's a documented need. Flag for review