User: paullmullen, Location: Wisconsin
Asked on: Saturday, October 11, 2025 at 8:39 pm EDT
Answered on: Saturday, October 11, 2025 at 8:39 pm EDT
Question: I'm licensed in Wisconsin, but helping out my daughter in California. I see routing of NM through the attic without staples or other support; it just drapes over the bottom chord of the trusses on 24" spacing. (See picture.). Is that OK? It was originally done in a development of condos/town homes probably all built at the same time.
Okay, let's break down the rules for NM cable support in attics, specifically in California (since that's where the work is being done). While your Wisconsin license is valuable, California's electrical code (based on the NEC with potential local amendments) governs this situation.
The Short Answer: No, that is NOT generally acceptable in California.Here's why, based on the National Electrical Code (NEC), which California adopts with some possible amendments
NEC 334.30 Securing and Supporting
NM cable must be secured and supported in a manner that protects it from physical damage. Simply draping it over truss chords does not provide adequate support or protection.
Specific Attic Requirements (NEC 334.23)
This section contains very specific rules on how NM cable can be run across the face of joists, rafters, or studs in accessible attics:
(A) Where Run Across the Top of Floor Joists
Where such run is made across the top of floor joists, or within 7 ft of the floor or floor joists across the face of rafters or studs, the cable shall be protected by guard strips that are at least as high as the cable.
(B) Cable Installed Parallel to Framing Members
Where such cable is run parallel to the sides of rafters, studs, or floor joists, neither guard strips nor running boards shall be required, and the installation shall comply with 334.30.
In Summary
The rules cited above mean that when running cables across framing members in accessible attics, guard strips are required to provide physical protection unless the attic is not accessible by means of permanent stairs or ladders and there is no flooring for a minimum of 6 feet. Also, where the cable runs parallel to the framing members it must be secured to those members in compliance with 334.30.
Here's a breakdown for your specific situation (draping over trusses)
Accessibility
The first question is how accessible is the attic? Does it have a permanent ladder or stairway? Even if it's only accessible by a hatch, it's usually considered "accessible" for the purposes of the code if there's a reasonable expectation of someone entering it for maintenance, storage, etc.2.
Physical Damage
The biggest issue is the lack of support. Draped NM cable is easily damaged. Consider these scenarios: Someone crawling through the attic could snag the cable. Stored items could be placed on top of the cable, crushing it. Rodents can chew on unsupported cables. Gravity can cause the cable to sag excessively over time.
What Needs to Be Done
Proper Support
The NM cable must be secured to the truss chords or other framing members with appropriate cable staples, cable ties listed and identified for securing and supporting cables, or straps. The NEC outlines how often the cables must be supported.
Guard Strips (Likely)
Unless the attic is completely inaccessible, guard strips are very likely required when running across the framing members to protect it.
Consider Conduit/Protection
If the cable run is particularly exposed or vulnerable, consider running it through conduit (like ENT - Electrical Nonmetallic Tubing).
Important Considerations for California
Local Amendments
California sometimes has amendments to the NEC. You need to check the California Electrical Code (CEC) for any specific modifications to these rules. You can often find this information on the California Building Standards Commission website.
Inspection
When you do any electrical work, it's essential to have it inspected by a qualified California electrical inspector.
Recommendations for Your Daughter
Consult a Local Electrician
The best course of action is to have a licensed and experienced California electrician evaluate the situation and make the necessary corrections. They will be familiar with the CEC and local practices.2.
Don't DIY (Unless...)
Unless you are also licensed to do electrical work in California, you should not attempt to fix this yourself. Many jurisdictions have restrictions on what kind of electrical work homeowners can do.3.
Get a Permit
Pulling a permit for this type of work is advisable. This will ensure that the work is inspected and meets code.
In summary, the situation you described with the NM cable draped over the trusses is likely a code violation in California. Proper support and, potentially, guard strips are needed to ensure a safe and compliant installation. Flag for review