Topic: Conduit Bodies Supports 314.23 (E) Ex

User: Derek9, Location: Alaska

Asked on: Sunday, October 12, 2025 at 11:22 pm EDT
Answered on: Sunday, October 12, 2025 at 11:32 pm EDT

Question: In regards to 314.23 (E) Ex, it states that IF your conduit body is larger than the raceway trade size, then it needs to be supported. To say it in Mike Holts words via his book, “IMC, RMC, PVC, RTRC, and EMT can support a conduit body if the trade size of the conduit body isn’t larger than the raceway.” Therefore, with that objective fact being stated, my question is if a larger conduit body such as an LB (2 1/2”) were used with a 2” RMC raceway, then how do you practically and mechanically support an LB? Upsizing large LB’s is fairly common to make wire pulling easier, however, I’ve never seen an LB itself be supported.

You've hit upon a practical problem that many electricians face! The code is clear, but the execution can be tricky. Here's a breakdown of how to practically and mechanically support a larger conduit body (like a 2 1/2" LB on a 2" RMC raceway) according to the NEC and common industry practices

Understanding the Problem:
Weight

Larger conduit bodies, especially cast metal ones like those used with RMC, can be quite heavy.


Leverage

The conduit running into and out of the LB creates leverage, especially if the conduit runs are long. Without support, the weight and leverage can strain the conduit, the LB itself, and the connections.

Code Compliance

314.23(E) is there to ensure that the weight and strain are properly handled, preventing damage and potential safety hazards.

Practical Methods for Supporting a Larger Conduit Body

Here are the most common methods:1.

Independent Support System

This is generally the best and most reliable method. It involves installing a support system dedicated to the LB itself.

Method



Straps/Clamps

Use pipe straps or clamps specifically designed for the diameter of the LB. These straps can be:

Directly Attached to the LB

Some LB designs have built-in mounting feet or flanges to which straps can be bolted. Check the manufacturer's specifications.


Wrap-Around Straps

Use heavy-duty wrap-around straps that fully encircle the LB body.

Support Structure

The straps are then attached to a secure support structure. This could be:


Unistrut

A very common choice. Attach the straps to Unistrut channels that are mounted to the wall, ceiling, or equipment frame.

Angle Iron

Similar to Unistrut, offering a rigid support.


Existing Structure (With Care)

In some cases, you might be able to attach to an existing building structure (steel beam, concrete wall), but always ensure the structure is capable of handling the weight and that you're using appropriate anchors/fasteners. Consult a structural engineer if there's any doubt.

Key Considerations



Material Compatibility

Use straps and supports made of materials compatible with the conduit body material (e.g., galvanized steel for galvanized RMC LBs).

Load Rating

Ensure the straps, anchors, and support structure have a load rating sufficient to support the weight of the LB and any conductors within it.


Placement

Position the support as close to the LB body as possible to minimize leverage.

Spacing

For long runs of conduit coming into and out of the LB, you may need additional supports for the conduit itself, closer to the LB, to prevent excessive strain.2.

Threaded Rod Hangers

This method is often used when the LB is suspended from a ceiling or overhead structure.

Method



Drill and Tap

Some LBs can be drilled and tapped to accept threaded rod (consult the manufacturer first).

Threaded Rod

Insert threaded rod into the tapped holes.


Hanger

Use a conduit hanger designed for threaded rod to suspend the LB from the overhead structure.

Considerations



LB Integrity

Drilling and tapping the LB must be done carefully and according to the manufacturer's recommendations to avoid weakening the body. If you can't get manufacturer guidance, it's best to avoid this method.

Load Rating

Ensure the threaded rod, hanger, and overhead support can handle the weight.


Leveling

Use a level to ensure the LB is hung straight.3.

Combination of Methods

You may need to combine methods for optimal support. For example, use straps to support the LB horizontally and a threaded rod hanger to provide vertical support.

Important Considerations for All Methods



Manufacturer Instructions

Always check the conduit body manufacturer's specifications for recommended support methods and load ratings. If they specify a particular method or prohibit others, follow their guidance.

Accessibility

Ensure the support method allows for easy access to the LB for future maintenance or wire pulling.


Corrosion

Protect all support hardware from corrosion, especially in damp or corrosive environments. Use galvanized or stainless steel hardware.

Professional Judgment

Use your experience and judgment to determine the most appropriate support method for the specific installation. If you're unsure, consult with a more experienced electrician or a qualified engineer.


EMT and Conduit Bodies

If you are using an EMT system then you might consider replacing the cast conduit body with a stamped steel one. The stamped steel bodies are generally listed to be supported by the emt.

What to Avoid



Solely relying on the conduit for support

This is the most common mistake. While the conduit can contribute to support, it's usually not sufficient for a larger LB, and it violates 314.23(E).


Using undersized or inadequate hardware

Don't use flimsy straps, undersized anchors, or hardware that's not rated for the load.*

Damaging the LB

Avoid drilling or modifying the LB in a way that could weaken its structure or compromise its integrity, unless explicitly approved by the manufacturer.

Example Scenario (2 1/2" LB on 2" RMC)

Let's say you're running 2" RMC conduit along a wall and need to install a 2 1/2" LB.1.

Best Approach

Use two heavy-duty galvanized pipe straps, sized to fit the 2 1/2" LB.2.

Attach to Unistrut

Mount a section of Unistrut horizontally to the wall, using appropriate anchors for the wall type (concrete anchors, toggle bolts for drywall, etc.).3.

Secure Straps to Unistrut

Attach the pipe straps to the Unistrut using bolts, washers, and locknuts. Position one strap near the top of the LB and one near the bottom to provide good support.4.

Additional Conduit Supports

If the RMC runs are long, install additional conduit supports within a few feet of the LB on both sides to minimize strain on the LB and its connections.

In Summary:


Supporting a larger conduit body requires a dedicated support system that's independent of the conduit itself. Prioritize robust, properly sized hardware, consult manufacturer specifications, and use your experience to ensure a safe and code-compliant installation. Remember that a properly supported LB will not only meet code but also contribute to a longer-lasting and more reliable electrical system. Flag for review