Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 800 Amp 35kA Distribution Block

User: NeilWicks, Location: USE

Asked on: Monday, October 13, 2025 at 6:53 am EDT
Answered on: Monday, October 13, 2025 at 7:31 am EDT

Question: Context:I need an 800 (or 760) Amp Distribution Block for a panel to be rated at 35kAThe panel will be fed from an 800 Amp Circuit Breaker in the MDB about 10 feet away with 2 x 500Total load in the panel will be 560 Amp with the largest load being 77 AmpNeed a little spare capacity above the 560 Amp of at least 100 Amp for some future additionsProblem:Can not find a suitable Distribution Block.All the Distribution Blocks I can find are only rated above their nominal 5 or 10kA when used in conjunction with 600 Amp Type J Fuses or a specified 600 Amp Circuit Breaker or similar, but nothing greater than 600 AmpQuestion:Any recommendations for a solution ?And would a configuration as shown in the image work ?And if it would work, would it still work without linking the two Distribution Blocks ?

Okay, let's break down this problem and find a solution for your 800A distribution block in a 35kA rated panel. The constraint of finding a distribution block specifically rated at 800A and 35kAIC is indeed a challenge, as you've discovered.

Understanding the Problem



Ampacity vs. SCCR

It's crucial to distinguish between the
ampacity (current carrying capacity) and the Short Circuit Current Rating (SCCR). Ampacity is how much current the device can continuously handle without overheating. SCCR is how much fault current it can safely withstand during a short circuit event. You need both to be adequate for your application.

Series Ratings

Manufacturers often achieve higher SCCRs by using components in series that coordinate to limit fault current. This is why you see distribution blocks rated higher when used with specific fuses or circuit breakers.

Distribution Block Limitations

Most distribution blocks on the market are designed for smaller applications and are not rated at the fault current required to handle the requirements you've listed.

Possible Solutions and Considerations


Dedicated Feeder Breaker and Distribution Panel



Best Practice

The most robust and code-compliant solution is often to use a distribution panel with a main breaker rated for the full 800A and the required 35kAIC. Then, use branch circuit breakers within that panel to feed your individual loads.

Why this is good

This provides a clear point of overcurrent protection and a panel specifically designed to handle the fault current.


Cost

This is likely to be more expensive than just a distribution block.

Space

It will take up more space than a distribution block.2.

Fused Distribution Block with a Properly Rated Fuse



Check Manufacturer's Documentation

Go back to the distribution block manufacturers' websites and carefully examine their specifications and application guides. Look for models that, when used with a specific class and size fuse (e.g., Class L fuses), achieve the required 35kAIC.

Fuse Sizing

The fuse must be sized appropriately to protect the distribution block and the downstream conductors. You need to coordinate the fuse to carry your 560A + 100A = 660A load, while still providing short-circuit protection. An 800 amp fuse is fine provided it does not exceed the ampacity of the conductors or the distribution block.


Example

A large Class L fuse block feeding a distribution block is a common industrial setup.

Important

Document EVERYTHING. The fuse must be properly documented as part of the overall system SCCR rating.3.

Using Multiple Distribution Blocks in Parallel (Your Image Scenario)



Potentially Problematic - Needs Expert Review

This could work, but it's crucial to understand the implications and potential problems. It's not a recommended "do-it-yourself" approach.

Key Concerns



Current Sharing

Will the two distribution blocks actually share the current equally? Even slight differences in resistance can cause one block to carry more current than the other, potentially overloading it.

Fault Current Sharing

During a fault, will the current divide equally? Unequal sharing can lead to one block exceeding its SCCR.


Listing and Approval

This configuration is highly unlikely to be UL listed or otherwise approved unless explicitly designed and tested by the manufacturer in this configuration. It will likely violate the electrical code.

If you pursue this



Engineering Analysis

You absolutely need a qualified electrical engineer to perform a thorough analysis, including calculations and simulations, to ensure proper current sharing and SCCR.

Manufacturer Consultation

Contact the distribution block manufacturer and ask them directly if this configuration is acceptable and what limitations apply. Get it in writing.


High-Quality Connections

Use properly torqued, high-quality connections with anti-oxidation compound to minimize resistance differences.

Without linking the two distribution blocks

This will NOT work. As the conductors are being split between the two distribution blocks, then if a fault occurs on one of the circuits fed by one of the distribution blocks, the other distribution block is now exposed to the same fault.


This would require both distribution blocks to be rated for the full 35kAIC independently
4. Using a Larger, Higher-Rated Distribution Block (May not exist at 800A, but check)



Search Extensively

Continue your search for a single distribution block rated for 800A and 35kAIC. Contact manufacturers directly (e.g., Eaton, ABB, Schneider Electric, nVent Hoffman) and explain your requirements. They may have a product that isn't readily available through standard distributors.

Recommendation

Start with Option 1, the dedicated distribution panel. It's the safest and most likely to meet code requirements. If that's not feasible due to cost or space constraints, thoroughly investigate Option 2 (fused distribution block). Option 3 (parallel distribution blocks) should only be considered with expert engineering analysis and manufacturer approval, and is generally discouraged.

In summary

Prioritize safety and code compliance. Don't assume a configuration is safe; verify it with calculations, manufacturer data, and potentially an electrical engineer. Document everything meticulously.

Regarding the Image:


The configuration in the image could work if you can prove (through engineering analysis and manufacturer approval) that the current and fault current will be shared equally, and that each block will remain within its SCCR limits. However, without those assurances, it's a risky and potentially non-compliant solution. As mentioned, without linking the two distribution blocks, this would not work at all.Good luck! This is a complex situation, and getting it right is essential for safety. Flag for review

Previous Question Next Question