User: pipe_bender, Location: Boston
Asked on: Monday, October 13, 2025 at 1:38 pm EDT
Answered on: Monday, October 13, 2025 at 1:38 pm EDT
Question: Hey gang looking at some engineered prints and is it OK to use Red / Black / Blue = Phase A / Phase B / Phase C for a 600/347 system if there is already a 208 that uses Black / Red / Blue = Phase A / Phase B / Phase C?There is a 480V system that has standard BOY.There would be voltage marking stickers on the pipes.Thanks everyone.
Using Red/Black/Blue for both a 600/347V system AND a 208V system, when both exist in the same facility is generally not recommended and can create confusion and safety hazards, even with voltage marking stickers. Here's a breakdown of why and what you should do instead
Why it's a Bad Idea:
Confusion & Errors
Different voltages with the same color coding increase the chance of accidental connections, misidentification, and potential equipment damage or personnel injury. Even with stickers, the possibility of human error during maintenance, troubleshooting, or new installations is too high.
Code Compliance Issues
While the NEC (National Electrical Code) in the US doesn't explicitly mandate specific colors across voltage levels, it highly recommends consistent practices and adherence to industry standards. Using the same colors for different voltages directly contradicts the intent of clear and standardized identification to prevent accidents. Inspectors may flag this as a violation based on the general requirements for safe electrical installations.
Safety Hazard
Technicians, electricians, and maintenance personnel are trained to associate certain colors with specific voltages. Deviating from common practice can lead to someone mistakenly thinking they are working on a 208V circuit when it's actually a 600/347V circuit. This can be deadly.
What You Should Do Instead
Consistent Color Coding for Each Voltage
600/347V
Use a DIFFERENT set of colors than the 208V system. Some options include:
Brown, Orange, Yellow
This is a common alternative for higher voltage systems and won't conflict with your existing 208V and 480V colors.
Purple, Gray, White
Less common but also distinct from the other voltages. This is a good solution.2.
Absolutely Mandatory Marking & Labeling
Voltage Labels
Use HIGHLY VISIBLE voltage marking stickers on EVERY conduit, junction box, and piece of equipment associated with the 600/347V system. These stickers MUST be durable, weather-resistant, and clearly indicate the voltage level (600/347V).
Phase Tape/Markers
In addition to the voltage labels, use phase tape or markers at connection points and within equipment to clearly identify A, B, and C phases.3.
Documentation & Training
Updated Drawings
Ensure all electrical drawings and schematics are updated to reflect the color coding scheme. Make it very clear on the drawings what the color coding is for each voltage level.
Training
Provide comprehensive training to all personnel who will be working on or near the electrical systems. The training should cover the color coding scheme, the hazards of working with different voltage levels, and the proper procedures for identifying and isolating circuits.4.
Consider Retrofitting the 208V system
Depending on the age and complexity of the 208V system, consider if it's feasible to change it to a different color code scheme. If you decide to keep the black/red/blue, then under no circumstances should you use it for the 600V system.
Example
208V
Black/Red/Blue (Phase A/B/C)
480V
Brown/Orange/Yellow (Phase A/B/C)
600/347V
Purple/Gray/White (Phase A/B/C)
Key Takeaway:
While voltage marking stickers help, they are NOT a substitute for clear and distinct color coding. Choose a different color scheme for your 600/347V system to minimize the risk of errors and ensure a safe working environment. The added cost is negligible compared to the potential cost of an accident. Flag for review