User: teeg123, Location: Maine
Asked on: Monday, October 13, 2025 at 2:21 pm EDT
Answered on: Monday, October 13, 2025 at 2:22 pm EDT
Question: here is the questionYou need a branch-circuit conductor for a 40 A non-continuous load in EMT with 8 current-carrying conductors. Conductors are THHN copper (90 °C). Ambient temperature is 40 °C. What is the minimum conductor size required after applying adjustment and correction factors?I highlighted in blue what I feel is the important information to answer this question.A-4 AWGB-6 AWG (correct answer)C-8AWGD-10AWG (my answer)I work through it like this correct me when I go wrong.1st 40 Amps of non-continuous = 40 Amps2nd I do temp correction 40Amps*1.15(which is in the 90 degrees for less than 50 degrees) =46Amps3rd I do the bundle adjustment 46Amps*70%=32.2Amps which in the 90-degree column in table 310.16 shows me #10 AWG after I round up.so, where am I going wrong and as always thanks in advance for the assistance.
You're very close! Here's where you're going wrong and the correct steps
Understanding the Problem
You have a 40A non-continuous load. You have 8 current-carrying conductors in EMT. Conductors are THHN copper (90°C rated). Ambient temperature is 40°C. You need to find the minimum conductor size after derating.
Step-by-Step Solution1. Base Ampacity
Start with the required ampacity for the load: 40A.2.
Temperature Correction
Your ambient temperature is 40°C. Look up the correction factor in Table 310.15(B)(1) for 90°C rated conductors. For 40°C, the correction factor is
0.91 (not 1.15 - that's for downward correction, not upward). You need to find the adjusted ampacity required before the bundling adjustment, so you are working backward. We need to compensate for the temperature correction. Adjusted ampacity before temperature correction: 40 A / 0.91 = 43.96 A (round up to 44A)3. Bundling Adjustment
You have 8 current-carrying conductors. Table 310.15(C)(1) gives adjustment factors for the number of conductors in a raceway. For 7-9 conductors, the adjustment factor is 70% (or 0.70). Again, we need to find the adjusted ampacity required before the bundling adjustment, so we are working backward. Adjusted ampacity before bundling correction: 44 A / 0.70 = 62.86 A (round up to 63A)4.
Determine Minimum Conductor Size
You now need a conductor that can handle at least 63A at its 90°C rating (before any adjustments). Look at Table 310.16 for THHN copper conductors in the 90°C column: #6 AWG is rated for 75A at 90°C. #8 AWG is rated for 55A at 90°C.5.
Choose the Correct Size
Since you need at least 63A, #8 AWG is not large enough.
#6 AWG is the correct answer.Why your method was wrong
Incorrect Temperature Correction
You multiplied by 1.15, which would decrease the ampacity. You need to divide by the correction factor to find the required ampacity before correction.
Order of Operations
It's important to understand you are trying to find a conductor size that, after being adjusted, can still carry 40A. You are essentially undoing the derating factors.
Confusion of Applying Factors
You need to divide to adjust ampacity before correction for bundling and temperature. By reversing the process in this way, the final size will have enough after the adjustment factors are applied.
Key Takeaways: Always double-check the tables and ensure you're using the correct correction/adjustment factors. When working with derating factors, you need to calculate the required ampacity of the conductor before applying the derating. Pay close attention to whether you need to increase or decrease ampacity to compensate for adjustments. Flag for review