Question: For derating conductors base on Table 310.15(B)(1). if I use 90 degree rated conductor but will terminate on 75 degree breaker. do I use the 90degree column or the 75 degree column?
You use the 75°C column for ampacity adjustments and derating.Here's the breakdown: Termination Temperature Rating
The termination temperature rating (e.g., 75°C on the breaker) is the limiting factor. This means the conductor temperature at the termination point cannot exceed that rating under normal operating conditions.
Table 310.15(B)(1) and Derating
When you apply derating factors for ambient temperature or the number of current-carrying conductors, you start with the conductor's allowable ampacity from Table 310.16.
Practical Application
Even though you have a 90°C rated conductor, because your breaker is rated for 75°C terminations, you must use the 75°C column from Table 310.16 to determine the starting ampacity for derating calculations. The conductor itself might handle the higher temperature, but the breaker can't. You must protect the weakest link in the chain, which is the 75°C termination.
In summary
Find the base ampacity
Look up the conductor size in Table 310.16 using the
75°C column.2. Apply Derating Factors
Multiply the ampacity from step 1 by the derating factors from Table 310.15(B)(1) for ambient temperature and the number of current-carrying conductors.
Important Considerations
Equipment Listing
Always refer to the equipment listing and instructions. Sometimes, equipment may be specifically listed for use with 90°C conductors, even with 75°C terminations. This is rare, but it's crucial to check the documentation.
Code Requirements
The NEC (National Electrical Code) in Article 110.14(C) is very clear on termination temperature limitations.
Safety: Following these rules ensures that connections don't overheat, leading to insulation degradation, fire hazards, and equipment failure.Always consult the latest edition of the NEC and a qualified electrician for specific installations. Flag for review