Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Code question

User: ST25spark, Location: Midwest

Asked on: Monday, October 13, 2025 at 6:51 pm EDT
Answered on: Monday, October 13, 2025 at 6:55 pm EDT

Question: Hi.It is a compromised ground....What section of NEC violation is this to site.I won't influence anyone with what sections I think on this.This is on a MLO single phase panel. 3 wires with no separate grounding conductor....https://imgur.com/a/Pyk7T79

Okay, I've examined the image you provided. Based solely on the image and the information you've given ("compromised ground," MLO single-phase panel, 3-wires with no separate grounding conductor), here are potential NEC violations to consider and why they might be relevant

Potential NEC Violations and Rationale:
250.4(A)(1) System Grounding

This section generally requires AC electrical systems to be grounded. If the
entire system is not properly grounded, it creates a shock hazard and compromises overcurrent device operation. The image suggests the system isn't grounded.

250.4(A)(5) Effective Ground-Fault Current Path

If there is not an effective ground fault path (required by NEC), that can keep a fault current from tripping the overcurrent device and clearing the fault.

250.24(A) Grounding Service-Supplied AC Systems

Since it is MLO, there
should be a grounding electrode conductor (GEC) connected to ground at the service equipment. It appears that it is not.

250.32 Grounding Requirements for Separate Buildings or Structures

If this MLO panel is in a separate building and supplied by a feeder, it must have a grounding electrode system as described in 250.32. This is especially important if there's no equipment grounding conductor (EGC) run with the feeder.

250.130 Equipment Grounding Conductors

This section allows the use of the grounded conductor to ground equipment under certain situations, but generally not from a subpanel.


408.40 Grounding of Panelboards

All panelboards MUST be connected to an equipment grounding conductor. If the 3 wires includes ONLY 2 hots and one neutral, that would not be an EGC.

Important Considerations (Limitations of Assessment)



Context is Critical

Without knowing the
full installation details, it's impossible to say definitively what violations exist. Where is this panel in relation to the service? What type of wiring is feeding the panel?

Local Amendments

Keep in mind local jurisdictions may have amended the NEC.

In summary, based on the limited information provided, it appears that there are NEC violations regarding the effective ground fault path and bonding of the grounding conductors within the panelboard.
A licensed electrician needs to evaluate the situation to determine the proper course of action to correct it. Flag for review

Previous Question Next Question