Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Cable tray used as EGC for parallel single conductors

User: Isaiah, Location: Baton Rouge

Asked on: Tuesday, October 14, 2025 at 7:20 am EDT
Answered on: Tuesday, October 14, 2025 at 7:20 am EDT

Question: My understanding per NEC: A single EGC, sized per 250.122 can be used when all parallel circuit conductors are run together in one cable tray. And, if bonded correctly, the cable tray itself can be used as the EGC. So why do clients insist on running an additional #4/0 in a cable tray? Is this strictly to ensure sufficient fault path for the parallel circuits?Enviado desde mi iPhone utilizando Tapatalk

You've got a good grasp of the NEC requirements. Here's a breakdown of why clients might insist on the additional 4/0 EGC, even when it seems redundant, and the factors influencing that decision

Understanding the Code Minimum vs. Client Preferences
NEC as a Minimum

The NEC sets the
minimum safety standards. It's entirely permissible to exceed these standards. Many clients, for various reasons, choose to do so.

Liability and Risk Aversion

Clients often have a lower risk tolerance than what the NEC mandates. A large fault current event can cause significant damage, downtime, and potential liability. They may want additional safety margin to minimize these risks.

Reasons for Oversized or Redundant EGCs in Cable Trays


Ensuring Fault Current Capacity



Worst-Case Scenarios

Clients may be concerned about scenarios where the cable tray's bonding is compromised (corrosion, loose connections). The additional EGC ensures a reliable fault current path, even if the tray's conductivity is degraded.


Future Expansion/Modifications

The electrical system might be designed with future expansion in mind. The additional EGC could provide capacity for increased load or changes in fault current levels.

Voltage Drop Concerns during Faults

A larger EGC reduces impedance and voltage drop during a fault, potentially allowing protective devices to operate faster and more reliably.2.

Perceived Reliability & Redundancy



Backup System

The supplemental EGC provides redundancy if the cable tray's integrity is ever in question.

Peace of Mind

Some clients simply feel more comfortable with the added safety margin, regardless of the code compliance of a single EGC or the cable tray.3.

Company Standards and Specifications



Internal Policies

Many large companies have internal electrical design standards that are stricter than the NEC. These standards might mandate a supplemental EGC in cable trays, regardless of the NEC's allowance.

Insurance Requirements

Insurance companies might have requirements for electrical system design that go beyond the NEC.4.

Coordination Studies and Selective Coordination



Improved Coordination

Larger EGCs can improve the coordination of overcurrent protective devices (OCPDs). Lower impedance allows for better discrimination between faults and overloads, minimizing nuisance tripping.5.

Harmonic Mitigation



Non-Linear Loads

In systems with significant non-linear loads (e.g., variable frequency drives, computers), harmonic currents can flow in the grounding system. A larger EGC can help reduce voltage distortion and overheating caused by these currents.6.

Grounding Electrode Conductor (GEC) Connection



Facility Grounding

Depending on the design, the supplemental EGC might be used as a primary GEC connection point, providing a direct path to the grounding electrode system.7.

Misinterpretation of the Code or Past Practices



Historical Reasons

In some cases, the requirement for a large supplemental EGC might be a holdover from older practices or a misinterpretation of past code versions. Engineers might continue to specify it out of habit or a lack of awareness of current code allowances.


Confusion with Other Requirements

Sometimes, the client might be confusing EGC requirements with other situations, such as service-entrance conductors where grounding electrode conductor (GEC) sizing is based on service size.8.

Corrosion concerns



Harsh environment
: If the cable tray is located in a harsh environment with exposure to corrosive substances, there might be concerns about the long-term integrity of the cable tray's metal components and the effectiveness of its grounding capabilities.9. Ease of Maintenance

Running an additional 4/0 EGC might be seen as providing easier access for future testing and maintenance of the grounding system.

In Summary

While the NEC allows for a single EGC or the cable tray itself (when properly bonded) to serve as the EGC for parallel circuits, clients often specify additional EGCs for: Increased reliability and redundancy Improved fault current capacity Compliance with internal company standards Concerns about cable tray bonding integrity Improved coordination of OCPDs Potential harmonic mitigation Peace of mind

Recommendation



Communication is Key

The best approach is to have an open discussion with the client about the NEC requirements and the reasons behind their preference for the additional EGC.

Documentation

Document the rationale for the additional EGC in the project specifications and drawings.


Cost-Benefit Analysis:
If the client is open to it, perform a cost-benefit analysis comparing the cost of the additional EGC with the potential benefits (e.g., reduced downtime, improved safety margin). This can help them make an informed decision.Ultimately, the client has the final say in the design, as long as it meets the minimum NEC requirements. Your role is to provide them with the information they need to make a safe, reliable, and cost-effective decision. Flag for review

Previous Question Next Question