User: Alwayslearningelec, Location: NJ
Asked on: Tuesday, October 14, 2025 at 9:58 am EDT
Answered on: Tuesday, October 14, 2025 at 9:59 am EDT
Question: A little unclear here. They are replacing motor, removing disconnect switch(adding splice box) and adding VFD. We are to reconnect existing circuit and run new wiring from VFD to motor.1. It says 6P. Is that really 6 pole circuit? I don't have panel schedule.2. Motor is 15 HP @208v. I come up with about 60A circuit. Disconnect is 100A.Would wire size need to be sized to the panel breaker or the 100A disconnect?How do they come up with 100A disconnect? Based on what?Thanks.View attachment 2580053View attachment 2580052
Okay, let's break down this scenario and address your questions
Understanding the Setup
Motor Replacement & VFD
The existing motor is being replaced and a Variable Frequency Drive (VFD) is being added. This means the power flow is changing: Power comes from the panel to a splice box (disconnect removed). From the splice box, new wiring goes to the VFD. New wiring then runs from the VFD to the new motor.
6P Circuit
The "6P" likely refers to a 6-pole circuit breaker in the panel. This is common for multi-phase (typically 3-phase) circuits, with each phase having two poles (one for the phase and one for neutral).
Existing Conditions
You know the motor is 15HP, 208V, and the existing disconnect was 100A. You're trying to determine the correct wiring and protection for the new setup.
Answering Your Questions1. "It says 6P. Is that really 6 pole circuit? I don't have panel schedule." Likely 3-Phase with Neutral & Ground
While technically a 6-pole breaker could exist for other configurations, the most probable scenario here is a 3-phase circuit with neutral and ground conductors included. Each phase conductor (A, B, C) and the neutral require two poles each (one 'hot', one 'neutral') for switching. The ground would just pass thru on a busbar or separate single pole.
Without a Panel Schedule
You'll need to confirm this physically at the panel. Look for the 6-pole breaker and identify how many wires are connected to it (excluding ground). 3-phase will have 3 current carrying phase conductors AND a neutral.2.
"Motor is 15 HP @ 208V. I come up with about 60A circuit. Disconnect is 100A. Would wire size need to be sized to the panel breaker or the 100A disconnect? How do they come up with 100A disconnect? Based on what?"
This is the core of the question. Let's break it down: Motor FLA (Full Load Amps) Calculation
You're right to calculate the motor's FLA. Use NEC Table 430.250 to find the FLA for a 15HP, 208V, 3-phase motor. It's about
46.2 Amps. Your 60A figure seems high if that's what you're basing it on. It's good to be cautious, but in this case, the table is your guide. VFD Input Current
The VFD's input current will be slightly higher than the motor's FLA due to VFD losses. The VFD manufacturer's datasheet is
crucial. It will specify the required input current rating (or input kVA). If you don't have it, assume at least 125% of the motor FLA, which would be: 46.2A 1.25 = 57.75A. Let's round that up to 60A for safety in the following calcs. Overcurrent Protection (Breaker) Sizing
NEC 430.52. This is where things get a bit complex, but in a good way. The VFD is considered an electronic overload relay: the breaker is allowed to be sized higher than the load, but it's there for short-circuit protection. As a general rule, you can go up to 250% of the motor FLA, but check the VFD documentation: often it will require a lower percentage than 250%, often 175% or less.In this case, let's say the VFD calls for 175% or less.
46.2 1.75 = 80.85A. So you can likely use an 80A breaker if it's standard size, or round up to 90A if your standard breaker size is 90A.
Conductor Sizing (from Splice Box to VFD)
NEC 430.22. Conductors must be sized no smaller than 125% of the VFD Input Current:60A 1.25 = 75A. Using NEC Table 310.16 (for allowable ampacities), you'll need at least a #4 AWG copper conductor rated for 75A at the appropriate temperature rating (likely 75°C or 90°C). This will depend on the terminals and equipment it's being connected to.
Conductor Sizing (from VFD to Motor)
VFD manufacturers often specify the conductor size. Check the VFD's manual. In the absence of manufacturer specifications, you can use the motor FLA of 46.2A, but make sure the VFD's overload protection is set correctly for the motor FLA. Use NEC Table 310.16. A #8 AWG copper conductor rated for 55A (at 75°C) is typically sufficient here, or you may need #6 depending on the ambient temperature and other factors.
Disconnect Sizing
Why was it 100A? Without knowing the original design, it's hard to say definitively. Here are some possibilities: Generous Sizing
The installer might have oversized it for future expansion or based on a higher FLA estimate.
Specific Motor Characteristics
The original motor might have had characteristics (like high starting current) that required a larger disconnect.
NEC 430.110
Disconnects must be rated for at least 115% of the motor's full-load current (FLA). In this case, 46.21.15 = 53.13 amps. So a 60A disconnect would be the minimum size.
Key Point: Coordination
You want to coordinate the breaker size, conductor size, and VFD ratings to ensure proper protection without nuisance tripping.
Here's a summary table
| Parameter | Value | NEC Reference(s) | Notes
Motor FLA | 46.2 Amps | Table 430.250 | From the table for a 15HP, 208V, 3-phase motor ------------------------------ | --------------------------------------- | ---------------- | ------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
Overcurrent Protection (Breaker) | 80 or 90 Amps (check VFD document) | 430.52 | Up to 175% of FLA or less. But CHECK the VFD manufacturer's documentation for the correct max breaker. Can be lower. VFD Input Current | ~60 Amps (Estimate) | VFD Datasheet | Check the VFD's documentation for the exact input current. This is an estimate based on assuming VFD will draw 125% of motor FLA
Conductor Size (VFD to Motor) | #8 or #6 AWG Copper (75°C or 90°C rating) | 310.16 | Based on the motor's FLA. Verify with the VFD manufacturer's recommendations. Also, consider voltage drop || Disconnect Rating | 60A Minimum (Check Local Codes) | 430.110 | Must be at least 115% of the motor's FLA. |Conductor Size (Splice Box to VFD) | #4 AWG Copper (75°C or 90°C rating) | 430.22, 310.16 | Based on 125% of the VFD's input current, and the ampacity of the wire.
Important Considerations
VFD Manual
Always consult the VFD manufacturer's manual. It will provide specific requirements for input power, conductor sizing, grounding, and overload protection. The values in that document override general code guidelines if they are stricter.
Grounding
Proper grounding is critical for VFD installations. Follow the VFD manufacturer's instructions and NEC Article 250.
Harmonics
VFDs can generate harmonics. Consider the impact on the electrical system and whether harmonic mitigation is needed.
Ambient Temperature
Wire ampacity is affected by ambient temperature. Adjust conductor sizes accordingly.
Voltage Drop
Evaluate the voltage drop in the conductors, especially for long runs. Use a voltage drop calculator.*
Local Codes
Always comply with local electrical codes and regulations.
Steps to Take
Obtain VFD Documentation
Get the VFD manufacturer's manual.2.
Verify Panel Information
Confirm the breaker configuration in the panel (6P).3.
Calculate and Select
Calculate the required conductor sizes and breaker rating based on the VFD documentation and NEC.4.
Inspect Existing Wiring
Check the condition of the existing wiring from the panel to the splice box. If it's damaged or inadequate, replace it.5.
Install Properly
Install all components according to the manufacturer's instructions and NEC.6.
Verify Settings
Ensure the VFD parameters are correctly set for the motor.7.
Test: Test the system after installation.This information should help you get started. Be sure to consult with a qualified electrician and electrical engineer if you have any doubts or questions. Good luck! Flag for review