Topic: White wire on equipment ground bus UL 508

User: xguard, Location: Baton Rouge, LA

Asked on: Tuesday, October 14, 2025 at 10:08 am EDT
Answered on: Tuesday, October 14, 2025 at 10:08 am EDT

Question: We had a control panel installed. It's UL 508 Listed by a control panel shop. I asked a question about a white wire being landed on the equipment grounding bus. It wasn't obvious to me what it was for initially. They said it's for a surge arrestor that was kind of hidden. There's also a black wire landed that should probably be taped green.The arrestor is a LA 303 by Delta. I don't have the wiring diagram but found this on the website. (I should note this arrestor is not being used in service equipment.)This is the response I received from the panel shop via the contractor “Yes, the white wire acts as a ground because if there is a surge, it shunts to ground relieving the surge. That does not violate NEC, as the panels are inspected for wiring codes before shipment.”Am I crazy or is this wrong? It looks like they landed it on the grounding bus because there weren't enough spots on the neutral bus. Thoughts? Not trying to be nit picky with them just jumped out at me. Thanks.

You are absolutely right to be concerned. The panel shop's explanation and wiring practice are highly questionable and likely violate the NEC. Let's break down why

Why This is Problematic:

1. NEC 200.2: General - Identification of grounded conductors. A grounded conductor shall be identified and distinguishable from all other conductors. This identification shall be accomplished by one of the following means: (1) Insulation. A grounded conductor shall be identified by one of the following: (a) A continuous white or gray outer finish. (b) Three continuous white stripes along its entire length on other than green insulation. (2) Tracer. A tracer of any color other than white or green.2. NEC 200.7 Use of Insulation. A conductor with white or gray insulation, or with three continuous white stripes, shall be used only for the grounded conductor. Exception No. 1: An insulated grounded conductor of size 6 AWG or smaller shall be permitted to be used as an ungrounded conductor if permanently reidentified at each location where the conductor is visible by marking tape, painting, or other effective means. This means a white or gray wire MUST be used for the neutral conductor unless re-identified at each termination point. Using it directly for grounding (without re-identification) violates this core principle.3.

Improper Use of Neutral (White Wire) for Grounding

While technically the surge arrestor is shunting to ground
eventually, the white wire is NOT a grounding conductor. It's a neutral conductor. Using it as a surrogate ground creates a potential path for neutral current to flow on the grounding system under normal operating conditions if there were ever a neutral to ground fault. This is extremely dangerous.4.

Black Wire Not Marked Green

A grounding conductor MUST be easily distinguishable. While you
can tape a black wire green, this isn't ideal. It's much better to use green insulated wire from the outset. The NEC emphasizes clear and permanent identification.5.

Potential Issues with Surge Arrestor Function

While the Delta LA303 is designed to shunt surges to ground, its effectiveness relies on a proper, low-impedance grounding path. If the "ground" connection is made via the neutral bus, it might not provide the fast, clean path needed for effective surge protection, especially if the main neutral-ground bond back at the service entrance is weak or compromised.6.

UL 508 and the NEC

The UL 508 Listing implies that the control panel was built and wired in accordance with the National Electrical Code (NEC) as well as other applicable standards. This would include the proper use of grounding and neutral conductors.

Here's what you should do


Document Everything

Take pictures of the wiring configuration immediately. Include clear photos of the white wire on the grounding bus, the black wire, and the model number of the surge arrestor.2.

Contact the Panel Shop Directly (Not Through the Contractor)

Explain to the panel shop that you have concerns about the wiring practices and that you believe they are in violation of the NEC. Refer to the NEC sections mentioned above (200.2 and 200.7). Be polite but firm. Ask them to explain the justification for their wiring method in detail and reference the specific NEC articles they believe allow it.
3.


Demand Correction

Tell them that you expect them to correct the wiring to comply with the NEC. This should include:
Moving the white wire from the grounding bus to the neutral bus. Ensuring that the surge arrestor has a dedicated grounding conductor connected to the equipment grounding bus (and, ideally, using a green insulated wire for this purpose). Properly identifying the grounding conductor (green insulation preferred, or at least adequately taped with green tape).4.

Involve an Independent Electrical Inspector (If Necessary)

If the panel shop refuses to correct the wiring, or if you are not satisfied with their explanation, consider contacting a qualified and independent electrical inspector. They can assess the installation and determine if it meets code. Their feedback is invaluable.5.

Consult with an Electrical Engineer (If Necessary)

If the situation becomes complex or if you have further doubts about the surge protection design, consulting with a licensed electrical engineer is a good idea. They can review the entire system and provide expert recommendations.

In summary: The panel shop's explanation is not valid. You're right to be concerned. It sounds like they took a shortcut, and it needs to be corrected to ensure safety and compliance. Flag for review