Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Box Fill

User: Therealcrt, Location: Kansas City

Asked on: Tuesday, October 14, 2025 at 12:19 pm EDT
Answered on: Tuesday, October 14, 2025 at 12:19 pm EDT

Question: I will have two sets of 500 KCMill AL with 2/0 AL ground stabiloy MC Cable entering into the back of a junction Box. Out of the bottom of the junction box I’ll have 2 3” EMT conduits piped down about 10 feet into the top of my panel. With the same wire configuration, except THHN. What would be the correct size Junction box I need to make those connections length, width, and depth right now I came up with a 24 x 24 x 6“ junction box

Okay, let's break down the junction box sizing requirements based on the National Electrical Code (NEC). You're dealing with large conductors and multiple conduit entries, so we need to carefully consider volume, conductor bending space, and conduit spacing.

Here's the analysis



1. Conductor Bending Space (Most Critical)



NEC 314.28(A)(1) - Minimum Size

This is the primary rule governing the box size for conductors of size #6 AWG and larger. The code specifies that the minimum dimension of the box (in any direction) must be at least 8 times the trade size of the
largest raceway entering that wall of the box, for straight pulls.You have two 3" conduits entering the bottom. 8 x 3 = 24. This means you need a minimum of 24" for a straight pull from the top of the JB down to the bottom conduits.

You also have two sets of 500 kcmil entering the box from the back.
While the conductors may be flexible, the rules still apply regarding conductor bending space. Therefore, we can assume that the 24" length satisfies the minimum requirement.2. Conductor Fill (Volume)



NEC 314.16(A)

This section governs the volume of the box and the number of conductors allowed. While less critical in your scenario with very large conductors, it's still worth checking.


Conductor Count

For each set of 500 kcmil, you have one conductor. You have four sets of 500 kcmil, so that is a total of 4 current-carrying conductors.

Grounds

Each set of 2/0 requires 1 conductor. Thus, 2 conductors must be added to our total.


Total Conductors

6 conductors

Table 314.16(A) does not include 500 kcmil. Table 314.16(B) includes volume allowances



Each 500 kcmil conductor must have 225.0 inches^3 of free space.
Conductors total volume required

225 x 6 = 1350 inches^3


24 x 24 x 6 = 3456 inches^3, so the conductor fill requirements are met.
3. Conduit Spacing (Knockout Spacing)



NEC 314.27(A)

This is important to ensure you can properly install the locknuts and bushings on your conduits. Check the manufacturer's specifications for your junction box to confirm the knockout spacing is sufficient for two 3" conduits. The knockouts for the two 3" conduits may not fit on the bottom of a 24x24 box.


Typically, a standard 24" x 24" box will have adequate knockout spacing for two 3" conduits, but VERIFY.
4. Derating



NEC 310.15(C)(1)

With more than three current-carrying conductors in a raceway or cable, you'll need to apply derating factors to the ampacity of the conductors. This is more relevant to the panel calculations and conductor selection but should be considered overall.

Conclusion and Recommendation

Based on the NEC requirements, your initial estimate of a 24" x 24" x 6" junction box is likely sufficient, assuming the following are TRUE:


The 24" dimension allows for adequate bending space per NEC 314.28(A)(1).
The box volume is sufficient for the conductors, connections, and any devices inside (NEC 314.16). The knockout spacing on the box allows for proper installation of two 3" conduits (NEC 314.27(A)).I strongly recommend you do the following BEFORE purchasing


Double-Check Knockout Spacing



This is the most important point.
Verify the knockout spacing on your specific 24" x 24" x 6" junction box can accommodate two 3" conduits side-by-side on the bottom. Review the manufacturer's specifications for the junction box. If it can't accommodate the conduits, you'll need a larger box.2. Consider a Deeper Box

While 6" might be enough depth, consider a deeper box (e.g., 8" or 10") for ease of installation and better conductor management. It gives you more room to work and make connections.3.

Consult with a Qualified Electrician

It's always best to consult with a licensed electrician to review your specific installation details and ensure compliance with all applicable codes and regulations. They can provide expert guidance and help you avoid costly mistakes.

Important Considerations



Material

Ensure the junction box is suitable for the environment (indoor, outdoor, corrosive, etc.).


Listing

The junction box must be listed by a recognized testing laboratory (e.g., UL).*

Support:
The junction box must be properly supported (NEC 314.23).By carefully considering these factors and verifying your calculations, you can select the correct size junction box for your application and ensure a safe and compliant installation. Good luck! Flag for review

Previous Question Next Question