Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: AIC Rating

User: Rknrbn, Location: WI

Asked on: Tuesday, October 14, 2025 at 4:17 pm EDT
Answered on: Tuesday, October 14, 2025 at 4:24 pm EDT

Question: I'm building a 800 amp single phase service with a 38000 AIC rating. I have an existing 400 amp fused disconnect with proper AIC rating. I am upgrading and adding a 200 amp fused disconnect with the proper AIC that feeds a 10000 AIC rated main lug panel 150' away. I will also have a 200 amp main breaker panel with a 38000 AIC rating with a subpanel adjacent to that, with a 10000 AIC rating. So the 400 amp disconnect, the 200 amp disconnect, and the 200 amp main breaker panel are the 3 main disconnects equaling in 800 amps. Is this all correct and AIC ratings?

Okay, let's break down your 800A single-phase service upgrade and analyze the AIC ratings. It's crucial to get this right for safety and code compliance.

Summary of Your Setup



Service

800A single-phase, 38,000 AIC available fault current.


Existing 400A Fused Disconnect

Suitable AIC rating (stated as having it).

New 200A Fused Disconnect

Suitable AIC rating (stated as having it).


200A Fused Disconnect Feeds

10,000 AIC rated Main Lug Only (MLO) panel, 150' away.

New 200A Main Breaker Panel

38,000 AIC rating.


Subpanel

Adjacent to the 200A Main Breaker Panel, 10,000 AIC rating.

Analysis


Service Entrance and Disconnects

You have three main disconnects that sum up to 800A (400A + 200A + 200A = 800A). This is a common approach for larger services.

Crucially Important

Each disconnect must be rated to interrupt the available fault current at the service entrance (38,000 AIC). You stated that the 400A and new 200A fused disconnects have the proper AIC rating, and that the new 200A main breaker panel has the proper AIC rating. Assuming this is absolutely correct, then you are ok for the main disconnects. The choice of using fused disconnects and a main breaker panel is acceptable. The critical thing is the AIC rating.2.

200A Fused Disconnect and the 10,000 AIC MLO Panel

This is where we need to be very careful. You're feeding a 10,000 AIC rated panel from a 200A fused disconnect that does have a 38,000 AIC rating.

This setup is acceptable if the fuses in the disconnect are CURRENT LIMITING FUSES.
Current Limiting Fuses

Current-limiting fuses, when they interrupt a fault, do so very quickly and drastically reduce the magnitude of the fault current that "lets through" to the downstream equipment. If you use current-limiting fuses with a tested series rating with the 10,000 AIC panel, this is acceptable. You will have to verify the series rating of the fuse and panel combination to ensure it meets or exceeds the available fault current.


If the fuses are not current-limiting

The 10,000 AIC rating of the panel is insufficient. It must be able to withstand the full 38,000 AIC available fault current. In this case, you would need to replace the 10,000 AIC panel with one rated for at least 38,000 AIC, or use a different overcurrent protection strategy.3.

200A Main Breaker Panel and the 10,000 AIC Subpanel

Similar to the previous point, you need to ensure that the main breaker panel protects the subpanel. Since the main breaker is rated for 38000 AIC, it must be series rated for a 38000 AIC rating.

Series Rating

Check the series rating of the main breaker panel and subpanel combination. Many manufacturers have tested combinations that allow you to use a lower AIC rated subpanel downstream of a higher AIC rated main breaker panel. The series rating of the two panels combined will allow for a lower AIC rating. Verify that the series rating of the main breaker and the subpanel combination is AT LEAST the available fault current of 38000 AIC.

Without Series Rating

If there is no listed series rating for the combination, the subpanel
must have an AIC rating equal to or greater than the available fault current (38,000 AIC).

Important Considerations and Recommendations



Documentation

Gather and keep all documentation related to the AIC ratings of your equipment. This includes manufacturer's specifications, UL listings, and any series rating information.

Local Codes and AHJ (Authority Having Jurisdiction)

Always check with your local electrical inspector or AHJ. They have the final say on code compliance and may have specific requirements for service upgrades.


Qualified Electrician

This is a complex service upgrade. It must be performed by a licensed and qualified electrician experienced with large service installations and AIC calculations.

Fault Current Calculation

Have a qualified electrician or engineer perform a proper fault current calculation at various points in your system. This will confirm the actual available fault current and ensure your equipment is adequately rated. The 38,000 AIC figure is a starting point, but the fault current can vary slightly depending on factors like transformer impedance and conductor lengths.


Labeling

Clearly label all panels and disconnects with their AIC ratings and any series rating information.

Current Limiting Fuses

It is highly recommended to use current limiting fuses for the 200A fused disconnect to properly protect the MLO panel.

In Summary

Your design can be code-compliant
if you carefully consider the current-limiting characteristics of the fuses in the 200A fused disconnect, and* the series rating of the 200A Main Breaker panel and the subpanel. It's absolutely critical to have a qualified electrician perform the installation and verify all AIC ratings.You MUST make sure that all equipment is rated properly. If in doubt, go with a higher AIC rating.

Disclaimer:
This information is for general guidance only. Always consult with a licensed and qualified electrician for your specific project. Electrical work can be dangerous, and incorrect installations can lead to fire, injury, or death. Flag for review

Previous Question Next Question