User: Ponchik, Location: CA
Asked on: Tuesday, October 14, 2025 at 4:56 pm EDT
Answered on: Tuesday, October 14, 2025 at 4:57 pm EDT
Question: Note 9 of Ch.9 states to treat the cable as one conductor.When doing conduit fill calculation say for (2) 12-2 NM cables, the two cables are considered as (2) individual conductors and use the 31% column or treated as 4 conductors and use the 40% column?TIA
You're right to be careful with this. The note you're referencing (likely Note 9 to Table 1 of Chapter 9) is important. However, its application is specific.
Here's the breakdown
Note 9 to Table 1, Chapter 9, NEC
“A cable containing two or more conductors shall be treated as a single conductor for calculating percentage conduit fill area. For cables that are oval in shape, the cross-sectional area shall be calculated using the actual major and minor diameters.”
Applying Note 9
This note only applies to the percentage fill calculation itself. It tells you how to determine the area occupied by the cable within the conduit. You treat the entire cable assembly (sheath and all conductors inside) as a single, oval-shaped conductor.
Conductor Count for Conduit Fill
This is where it gets tricky. While Note 9 tells you to treat the cable as a single conductor for area calculations, you need to use the actual number of conductors inside the cable when selecting the percentage fill column in Table 1 of Chapter 9.
In your Example (2) 12-2 NM Cables
Total Conductors
Each 12-2 NM cable has two current-carrying conductors (hot and neutral). Ground conductors are not counted for fill calculations. Thus, two 12-2 NM cables contain 4 current-carrying conductors.2.
Fill Column Selection
Because you have four current-carrying conductors, you would use the 40% fill column in Table 1, Chapter 9.
Here's the full process for two 12-2 NM cables in conduit
Determine Number of Conductors
In this case, 4 current-carrying conductors (two from each 12-2 NM cable).2.
Choose Fill Percentage
Table 1, Chapter 9 dictates the fill percentage. With 4 conductors, use the 40% fill column.3.
Calculate Area of Each Cable
This is where Note 9 comes into play. Treat each cable as a single, oval conductor. Measure (or find in Appendix C) the major and minor diameters of the 12-2 NM cable. Calculate the area of the oval using the formula: `Area = π (major diameter / 2) (minor diameter / 2)`4.
Total Area of Cables
Multiply the area of one cable by the number of cables (2 in this case) to get the total area occupied by the cables.5.
Required Conduit Area
Divide the total area of the cables by the allowable fill percentage (40% or 0.40) to determine the minimum required area of the conduit. `Required Conduit Area = Total Cable Area / 0.40`6.
Select Conduit Size
Look up the internal area of different conduit sizes in Table 4, Chapter 9. Choose the conduit size with an internal area greater than or equal to the required conduit area you calculated in step 5.
In Summary
Note 9 is for calculating the AREA each cable takes up.
The total number of current-carrying conductors determine the ALLOWABLE FILL PERCENTAGE.
Important Considerations
Appendix C
The dimensions of common cables are usually listed in Appendix C of the NEC. This saves you the trouble of physically measuring the cable.
Derating
Remember to consider conductor ampacity derating rules if you have more than three current-carrying conductors in the conduit (310.15(C)(1)).
Grounding Conductors: Equipment grounding conductors are not counted as current carrying conductors for conduit fill calculations (Note 5 to Table 1 of Chapter 9), but are counted for conductor ampacity adjustment factors (310.15(C)(1)).Always consult the latest edition of the NEC for the most accurate and up-to-date information. The NEC is the final authority on these matters. When in doubt, consult with a qualified electrical inspector. Flag for review