User: YouConduit!, Location: Midwest
Asked on: Tuesday, October 14, 2025 at 5:21 pm EDT
Answered on: Tuesday, October 14, 2025 at 5:23 pm EDT
Question: Trying to determine if the branch-circuit OCPD can be used as the disconnecting means for two different motors. The OCPDs will be in a 480V/3ph panelboard and will be lockable. Both motors are within 50 feet and can be seen from the panelboard.Motor 1: 1/3 HP, NEMA 1 FVNR starterMotor 2: 20 HP, VFD(VFD and starter are both right next to the panelboard in question)I'm getting hung up on the 430.102(B) and 430.109, but it seems redundant to add a disconnect switch 20 feet away from the panelboard.**2023 NEC**
Okay, let's break down the NEC requirements for disconnecting means for motors, focusing on your specific scenario. You're right to focus on 430.102(B) and 430.109, as they are key.
Understanding the Requirements 430.102(B) Location
This section states that the disconnecting means shall be located within sight from the motor location and the driven machinery location.
430.109 Type
This section specifies the types of disconnecting means that are permitted for different motor horsepower ratings.
Analysis of Your Situation Motor 1 (1/3 HP, NEMA 1 FVNR Starter)
430.109(C)(1)
For motors rated 1 horsepower or less that are normally left running and are so constructed that they cannot be damaged by overload or failure to start, the branch-circuit protective device shall be permitted to serve as the disconnecting means if the switch or circuit breaker is also readily accessible.
Application to Your Case
Since your motor is 1/3 HP, this exception could apply. But there's a caveat: "so constructed that they cannot be damaged by overload or failure to start." This is a little vague. In most industrial settings, and to err on the side of caution, it's best to assume the motor could be damaged by overload.
430.109(A)(1)
For motor rated 2 horsepower or less and 300 volts or less, the disconnecting means shall be a listed switch rated for the application or a listed molded case circuit breaker.
Application to Your Case
This option would apply if the molded case circuit breaker is listed.
Motor 2 (20 HP, VFD)
430.102(B)
Within sight requirement is met in your case (50 ft and visible).
430.109(A)(6)
For motors over 100 horsepower, the disconnecting means shall be a listed motor-circuit switch rated in horsepower.
430.109(A)(5)
For motors over 2 horsepower to and including 100 horsepower, the disconnecting means shall be a listed motor-circuit switch rated in horsepower or a listed molded case circuit breaker.
Important Considerations for VFDs
Disconnect Rating
The disconnect must be rated for motor circuit applications, not just general-use switches. This typically means a horsepower rating.
Input vs. Output
The disconnect should be on the line side of the VFD (the input). Disconnecting the output of the VFD while it's running can damage the VFD.
Lockout/Tagout (LOTO)
VFDs often have internal capacitors that can hold a charge even after power is removed. Follow the VFD manufacturer's instructions for safely discharging the capacitors before working on the motor or VFD.
Can the Branch-Circuit OCPD Be the Disconnecting Means? Motor 1 (1/3 HP)
Potentially. If the OCPD is readily accessible (NEC definition matters here - generally means not behind locked doors or requiring a ladder), and you can definitively say the motor is constructed to not be damaged, then maybe. However, it's generally better practice to install a separate disconnect.
Motor 2 (20 HP, VFD)
Very unlikely. The OCPD cannot be the disconnecting means. You
must have a separate, horsepower-rated disconnect switch for the 20 HP motor. This switch must be within sight of the motor (or lockable per exception).
Justification for a Separate Disconnect (Motor 2) Safety
Provides a clear and easily accessible means to de-energize the motor and VFD during maintenance or emergencies.
Code Compliance
NEC 430.109(A)(5) requires it.
Solutions and Recommendations1. Motor 2 (20 HP, VFD): Install a horsepower-rated disconnect switch. Mount it near the VFD (within sight of the motor, as you mentioned it is). Choose a disconnect switch specifically rated for motor circuits. Look for a horsepower rating equal to or greater than the motor's HP. Ensure the disconnect switch is lockable in the open position for LOTO. Consult the VFD manufacturer's documentation for any specific disconnect requirements.2. Motor 1 (1/3 HP): Install a horsepower-rated disconnect switch. Install it near the motor and starter. Choose a disconnect switch specifically rated for motor circuits. Look for a horsepower rating equal to or greater than the motor's HP. Ensure the disconnect switch is lockable in the open position for LOTO.
In summary: While it might seem redundant, a separate disconnect for the 20 HP motor is a definite requirement for code compliance and safety. It provides a clear, local point of isolation for maintenance, troubleshooting, and emergencies. It's best practice to install a separate disconnect for Motor 1 as well. Flag for review